Weather Simulation for Dimming expansion module
Re: Weather Simulation for Dimming expansion module
Unsure currently... measure the voltage on that channel
compared to the others. It really should be off. your offset is 600 seconds, so within 10 minutes of the set time both channels should be off and neither are set to be moon. There is not much chance the code is wrong here, way too many people using it- no one has ever reported this type of error. Seriously, just check the output voltage between the common ground on the dimming module and channel 1 and 2 wires. They should be the same. If they are and one lights off and the others on- well.... thats something you need to figure out. If they are different (do this well after sunset) then I will have to really look at your code. I assume you have the code posted here and not an old version... if not. Start there first and grab most recent code.
Hi,
first of all a silly mistake of mine. the channel 1 is what is still lighting up & not the 2. Now i measure the voltage and it is zero on channel 0 and 0.7 on channel 1. the channel which is set for moon is at 3.3.
i switched of the power and again turn them on again now both 0 and 1 is lighting at same intensity. Don't know whats wrong i am doing.
I am confused as well.
Can you tell us the answers to these questions-
Does channel 2 rise and set correctly?
Does channel 1 "rise" with ch2?
- I.E. does it gain intensity during the day and peak around noon then getting dimmer throughout the day until it "sets" with this odd 0.7V low intensity light.
Does channel 1 EVER go dark?
Do the moon lights work correctly?
Have you double checked to ensure that you have these things plugged into the correct output channels on the dimming module, I know when I wired this up I had them all backwards the first time...
Reason I ask is its really hard to see how there is a code issue here. IF channel 2 rises and sets correctly then the calculation for rise and set are working. There is almost nothing else to trouble shoot- the only difference between the calculations for Ch1 and Ch2 light intensity and sunset is due to the CHoffset array. So- if your CHoffset array is correct (and it looks like it is) then I don't honestly know what to say. I can look at your code but unless you have introduced an error (and this is very hard to see by just looking) its hard to say how it would be code based. Everyone else using this would have the same issue- but no one does.
That said, I will look but please answer the questions as it will help narrow down, and seriously- double check that your wired up correctly. I had my ch 1 plugged into ch 6 out etc etc for a few days. The manual has a diagram of how the output wire channels are numbered with respect to the PWM channel-
Looked at code you posted-
Only thing I see thats odd is that you have a new line splitting your declaration of the Choffset array- in most cases you can split C type code into as many lines or as few as you like (but I am not absolutely certain if there is an exception for cases like this with an array designation)- so with that in mind..... I would make that the line look like this. It avoids any possible confusion or inadvertent inclusion of hidden control characters etc on a copy and paste as well as brings your code to the same lay out std as what everyone else is using.
int Choffset[]={0,0,0,0,600,-600,0,0,0,0,0,0,0,0,0,0};
Other than that, I again am left with the idea that this is not code based- in that if you have in fact a faithful copy of whats posted here and that everyone else is using, this is not an error that exists there. I will wait until you have a chance to answer the above post questions and correct this line (just to be safe, leave no spaces in the array designation and be sure your using numbers and not a capital letter "o" which again, does not appear to be the case here.
Might help if he post current code since he changed the things you originally mentioned. Maybe something he changed is incorrect.
I agree- Possibility exists that something is odd and was introduced/deleted.
I am sorry this is being such a pain for you, but its not terribly complicated, if you can look through the questions and see if in fact you can get a zero voltage output on that channel under any condition that would help a lot. Its just very very odd-
Don't give up, what I just thought of is that I could easily edit your code to shut off that channel... and if its still on then you have an issue with the driver not coming down to zero output with a zero PWM input signal. This seems to me to be the most likely cause at this point - because no one else has experienced this issue. Let me know what you want to do. Shutting off the channel is TRIVIAL...
in fact... just edit this line to look like the next..
This will eliminate channel 1 from EVER having any intensity output on the PWM channel output. If it still lights up...
There is a problem with your hardware and how its dealing with the PWM input signal and scaling that to output current based upon the input voltage.
I would do this FIRST- It answers the question. If you have any light on ch1 with this in the code you need to leave it this way and play with your driver until it is dark under these conditions then remove that small if loop and at that point you should be good to go... if instead you get a dark channel 1- with only this mod, then we need to figure out what the heck is going on in the version of the code your operating from. Or indeed, if you are experiencing some unusual circumstance that is revealing a otherwise hidden issue.
It would be very nice to see you try this, it will directly put to rest any concerns here about what happening and further will provide a nice trouble shooting record should anyone else experience this.
for (byte a=0;a<6;a++){//using all prior mods to light intensity (Insolation-->Cloud-->Storm) lets make some light
analogWrite(PWMports[a],TrueIntensity[a]);//dont change this to 8 to refelct array for channels.. we only have 6 here!
if (a==1){
analogWrite(PMWports[a],0);
I am having trouble installing this on my new PWM expansion module. From what I understand this is installed on the PWM module, not on the main unit. I have taken the PWM module out of its case and there is nowhere to insert the USB cable that came with the main unit. The only way for me to connect it to my computer is with the mini USB cable that came with the PWM expansion module. When I do this, I get an error in Windows 7 that the USB Device not recognized. When I go to load the code, only COM1 shows up. I try it anyway with Reef Angel controller w/ optiboot selected, and I get the following error:
System wide configuration file is "C:\Program Files\Reef Angel Controller\hardware/tools/avr/etc/avrdude.conf"
Using Port : \\.\COM1
Using Programmer : arduino
Overriding Baud Rate : 115200
avrdude: Send: 0 [30] [20]
avrdude: Recv:
avrdude done. Thank you.
Please help!
avrdude: Recv:
Please help!
Sorry...
There was a change in hardware where the new dimming modules are not going to allow this anymore.
They are not smart modules any longer.
So I can't use this code? I want to have clouds/lightning effects. What would be the best way to do this now?
The dimming module is being reworked to allow for better and easier compatibility and in the process, it was found best to use a dedicated chip for the dimming signal instead of a mcu like the previous hardware was using.
This code would have to be ported to be used in the head unit itself.
Based upon what Roberto just said-
Porting to the head unit is not probably overly difficult. The code has no special "code" that would only work on the Dimming module, it is however relatively large and would be unlikely to fit on anything other than the RA+. I had spent a little time trying to create an object library that would bring this code into the distribution. I admit to being slightly over matched in my coding skills as I have no OO C++ experience and limited OO Perl experience... so I got it split into what seemed to be rational segments, and then decided I was unsure what/how exactly to take this split up code and do something with it so that it could get packaged into the libraries.
At this point, given my availability and ability I would be happy to work with a more experienced person to see this through but am uncertain I can do this on my own without dedicating way too much time to a C++ learning curve when the only place I use this language is for RA.
If someone is willing to help (and I honestly do not think its going to take much) finish this, we should talk.
If this occurs, it will simply be part of the distribution and could be enabled by adding a few lines of code and includes.
Lnevo? Any time or interest?
Ok, so I'm trying to port this into my code, and when compiling, its giving me this error:
Globals\Globals.cpp.o: In function `MoonPhase()':
C:\Users\DaveElise\Documents\Arduino\libraries\Globals/Globals.cpp:116: multiple definition of `MoonPhase()'
Small_Reef.cpp.o:C:\Users\DAVEEL~1\AppData\Local\Temp\build4725006818650472374.tmp/Small_Reef.cpp:746: first defined here
Here is my code:
Here is my code:
#include <avr/wdt.h>
//includes for SWFLTEK functions
#include <stdlib.h>
#include <math.h>
//***********************************ARRAYS YOU MUST MODIFY TO MAKE YOUR TANK SET UP WORK*****************************
//YOU MUST READ EVERY WORD IN THIS SECTION IN ORDER TO APPROPRIATELY CONFIGURE THIS PROGERAM- READ EVERY LINE BELOW///
byte ChMax[]={200,220,200,220,225,0,0,0};//Incremental value (Max-flicker) above flicker you want as max intensity (!!!!!!! Light Set Point is ChMax PLUS Flicker !!!!!!)
byte flicker[]={31,31,31,31,40,0,0,0};//need to input actual values here for flicker point on all channels in PWM expansion box
boolean Wchannel[]={1,0,1,0,0,0,0,0}; //use 1 to designate white channel (i.e. off during storm and used for lightning). Array corresponds to PWM channel 0-5 in order
//Array to give direction to dimming. e.g. DimOrder[]={0,0,1,1,0,0} (cloud chase effects, just group channels you want to dim together during a cloud or storm
//as either a 0 or a 1, i.e. all left side channels are 0 all right are 1 or all front are 0 all back are 1 or whatever
//(which is zero or 1 will change who dims first). set them all to 0 if your tank has no left/right or front/back lights.
byte DimOrder[]={0,0,1,1,1,0,0,0};
//set all channel positions that you would like to use for the lightning strike effect to 1 (0-5 are PWM channels 6,7 are Main PWM outs)- and channels with a 0 are not used in strike
byte StrikeChannel[]={1,1,1,1,1,0,0,0};
byte MoonCh[]={0,0,0,0,1,0,0,0};//place a 1 in the array position of all lighting channels you would like to use a moon lighting (this does not preclude their use in other phases (day, storm etc)
//**********************************DONE CHANGING THINGS HERE BUT YOU MUST CHANGE ChOffset array IN CalcSUN function******
//defines for SWFLTEK functions
// arc-seconds per radian
#define _sec_rad 206264.806247096370813
// axial tilt of earth at epoch, in radians
#define _tilt 0.409092804222329
// tropical year in seconds... rounding error accumulates to 26 seconds by the year 2136
#define _tropical_year 31556925
// 'zenith' of rising (setting) sun in radians (360 - 2 * 90.833 degrees)
#define _zenith 3.11250383272322
//*******************GLOBAL VARIABLE DECLERATIONS FOR MHOCKIN Weather package*************************************
//Unless your planning on editing the program DO NOT CHANGE ANYTHING HERE
long latitude, longitude;
byte TrueIntensity[8];//array used to place hold final write values for PWM intensity setting
long elapsedTime;//used multiple places as elapsed since midnight
long newDay;
unsigned long rise;//time in seconds from the year 2000 (GMT) for sunrise
unsigned long set;//time in seconds from the year 2000 (GMT) for sunrise
long ChRiseSet[16];//times of rise and set for all 8 channels based upon offsets from calc rise and set values
float ChSlope[16];//slopes for 1/2 day calculations based upon time from offset to midday for channel 1-8
long CloudMaster[20];// Set up array to hold start and end times for clouds for the day-
long midDay;// exactly 1/2 way between rise and set, i.e. solar noon for latitudes <60 close enough for us...
byte PWMports[] ={
3,5,6,9,10,11};
byte ChannelValue[8];// Array to store output of insolaiton which may be modified and stored in TrueIntensity which is used to write to the PWM channels
unsigned long StrikeStart;//timer to keep track of strike sequence
int StrikeMaster[20];//Array to hold random strike pattern generated by weather array is sized to MAX needed given strike patter generator (8 strikes=16 positions)
byte StrikeNumber;//place to hold total number of strikes this sequence
boolean StrikeNow;//starts lightning strike sequence in loop state change made in weather/storm loop
byte StrikeCount;//Used to properly sequence strike sequence for delay between strikes
byte cmdnum=255;
byte datanum=255;
byte dow=0;//day of week
byte strikePattern, strikeTime;//used in Lightning() for timing of particular instance of strike
boolean Cloud;// are we in a cloud interval on days that have clouds
boolean CloudToday;//set in CalcSun if randomization yields a day with clouds.
boolean IsStorm;// are we in a storm
byte CloudsTotal;// how many clouds today
long lastmillis;// variable to track millis to enable cloud and insolation loop restriction by time
boolean StormAdvance;//storm timer for light effect advance
boolean InsolationAdvance;//when true we recalculate light intensity during clear sky (every 3 seconds seems more than often enough)
byte counter;//used to track millis advance for insolation,cloud trigger
//END HEADER/Global Variable declaration//
ReefAngel.FeedingModePorts = Port4Bit | Port5Bit | Port6Bit;
ReefAngel.WaterChangePorts = Port1Bit | Port3Bit | Port4Bit | Port5Bit | Port6Bit;
ReefAngel.OverheatShutoffPorts = Port3Bit | Port7Bit;
ReefAngel.Relay.On( Port2 );
ReefAngel.Relay.On( Port4 );
ReefAngel.Relay.On( Port5 );
Serial.begin(57600);
Wire.begin(8);
//Wire.onReceive(receiveEvent);
//Wire.onRequest(requestEvent);
pinMode(3,OUTPUT);
pinMode(5,OUTPUT);
pinMode(6,OUTPUT);
pinMode(9,OUTPUT);
pinMode(10,OUTPUT);
pinMode(11,OUTPUT);
wdt_enable(WDTO_1S);
unsigned long seed=0, count=32;
while (--count){
seed = (seed<<1) | (analogRead(5)&1);
randomSeed(seed);//start random generator at a different point each time (not perfect but whatever its gonna be pretty damn random)
setSyncProvider(RTC.get); // the function to get the time from the RTC
setSyncInterval(SECS_PER_HOUR); // Changed to sync every hour.
dow=0;//set Day Of Week (dow) to a 0 value which is impossible (day()=1-7)... so we trigger calcSun on restart
StrikeNow=false;//no lightning strike yet
CloudToday=false;//set to no clouds so CalcSun can set correctly if should be true
Cloud=false;//set cloud to false
IsStorm=false;//set storm to false
lastmillis=millis();//start our millis timer now
counter=0;//used in weather for triggering a storm, triggering lightning in a storm.
StrikeCount=0;//Number of lightning strikes in the sequence.. set to zero until initialized in sequence
//Standard PWM Functions Receive/Process
wdt_reset();
if (howMany==5){
cmd1=Wire.read();
cmd2=Wire.read();
cmd3=Wire.read();
cmd4=Wire.read();
cmd5=Wire.read();
if (cmd1=='$' && cmd2=='$' && cmd3=='$'){
cmdnum=cmd4;
datanum=cmd5;
//Serial.println(cmd4,DEC);
//Serial.println(cmd5,DEC);
else{
for (int a=0;a<howMany;a++){
Wire.read();
void ProcessCMD(byte cmd, byte data){
wdt_reset();
//End Standard Functions
//Start of sunrise, sunset and cloud calculations- runs on reset and once a day thereafter.
void CalSun(){
//Serial.println("CalSun Run Now");
//*********************YOU NEED TO CHANGE THESE VALUES Read instructions in their ENTIRETY and CAREFULLY change to values for your tank and geographical region***************************
//channels 0-5 are PWM expansion board lights 6,7 are ReefAngel Controller PWM outputs
//offsets for rise/set all values in seconds offset from calculated rise or set value (-) am offset=longer day****** (-)pm offset=shorter day)
//array order is ch0 am offset, pm offset, ch1 am offset, pm offset etc..
//THESE values are the number of seconds that a particular channel will be offset from the rise/set time, i.e. negative to rise earlier/set earlier
int Choffset[]={
-600,0,-1800,6000,0,600,-1200,6600,-2200,6600,0,0,0,0,0,0};
// NOW SET YOUR LATIDTUDE AND LONGITUDE COORDINATES as Degrees, Minutes, Seconds of Lat and Lon
//If Your NORTH of the equator your LONGITUDE must START with a NEGATIVE number (the rest are positive) e.g. All of North America, Europe, Russia etc are negative
//If Your EAST of the Prime Meridian your LATITUDE must START with a NEGATIVE number (the rest are positive), e.g. Most of Europe, All of China, India, Austraila, Russia etc are negative
latitude=dmsToSeconds(40,44,00);//United States of America- Salt Lake City, local time is -7 hours GMT
longitude=dmsToSeconds(-111,47,00);
//**********************ok now were done changing things IF YOU CHANGED the Top part of the GLOBAL variable decleration AND this... your FULLY configured and ready to load********************************************
if (dow==0){//if the controller has resarted we need to find midnight
long hours, minutes;//store current elapsed local hours as total seconds from midnight
time_t t=now();//store current clock time to parse
hours=hour(t);
hours=(hours*3600);//current hour number 0-23 as seconds
minutes=minute(t);
minutes=(minutes*60);//minutes of current hour as seconds
newDay=now();
newDay-=(hours+minutes);//Convert current local unix epoch time to local unix epoch time of midnight
else if (dow!=0){//if we did not restart but the day is new then it is midnight and were good to go..
newDay=now();
//#define SECS_YR_2000 (946684800) the time at the start of y2k (need to subtract from unix epoch time to bring to Y2K origin
newDay-=946684800;//convert GMT unix Epoch to seconds elasped since 2000 for GMT midnight of today
rise=newDay;//set value to send to SunRise as midnight GMT in seconds from Y2K
set=newDay;//
//Calculate rise time and set time using Epherma Library functions (see end of code)
SunRise(&rise);//call to Epherma function
SunSet(&set);//Call to Epherma functionunsigned long newDay;
/*Serial.print("rise and set= ");
Serial.println(rise);
Serial.println(set);
Serial.print("newDay as seconds since 2000 to todays midnight= ");
Serial.println(newDay);*/
rise=(rise-newDay);// set to elapsed seconds of day
set=(set-newDay);
/*Serial.print("rise and set as elapsed seconds of day= ");
Serial.println(set);*/
newDay+=946684800;//Convert newDay back to unix epoch GMT midnight today (used in loop to determine how far we are into the day)
/*Serial.print("newDay as seconds since since 1970 to todays midnight= ");
Serial.print("elapsed is");
long elapsed=now()-newDay;
Serial.println(elapsed);*/
//Calculate rise and set times for all channels in equivlants to elapsed seconds from midnight today
//populate array for chRise and Set as well as chSlope for 0.5pi/ half day lenght for each channel from midday (asymmetric days are allowed)
float deltaY=1.570796327;//1/2 * pi as integer by scaling* 10^9 to fill UL
midDay=(((set-rise)/2)+rise);
long HalfDayLength=((set-rise)/2);
for (byte b=0;b<16;b++){//working as of April 5 2012 serial tested
if (b%2==0){
ChRiseSet[b]=rise+(Choffset[b]);
ChSlope[b]=(deltaY/(float)(HalfDayLength-(Choffset[b])));
else if (b%2==1){
ChRiseSet[b]=set+(Choffset[b]);
ChSlope[b]=(deltaY/(float)(HalfDayLength+(Choffset[b])));
//***************** to CHANGE THE chance of Clouds actually occuring on a given day************************
byte CloudChance=100;//% Chance of a Cloud every day
//****************************now were done- did you use a value from 0-100 without a decimal?****************
byte RainMaker=random(1,101);
if (RainMaker<=CloudChance){
CloudToday=true;//used to trigger weather function, can also be used to send flag to controller
else if (RainMaker>CloudChance){
CloudToday=false;//see above comment on CloudToday
return;
long dayLength=0;
for (byte a=1;a<16;a=(a+2)){//determine maximum day length given light on tank that is not moon light, this will yield night clouds and storms (and a storm after dark is severe... always
if (a==0){
if (((set+Choffset[a])-rise)>(set-rise)){
dayLength=((set+Choffset[a])-rise);
else dayLength=(set-rise);
else if (a!=0){
if (dayLength<((set+Choffset[a])-rise)){
// number of clouds possible for the day, max and min
byte CloudsMax=10;//DONT INCREASE BEYOND 10 or it will DIE, or increase array size to handle it (among other things)
byte CloudsMin=4;//use 2 as a minimum
CloudsTotal=random(CloudsMin,(CloudsMax+1));
// Average day is 50,000 secs so if 4 clouds and 10% that gets you 5,000 seconds of clouds (about 1800 seconds length for each of the 4 clouds in independent segments (if 4 is # clouds)
byte OvercastMin=((CloudsTotal*10)/5);//Min cloud length will be about 1000 seconds (15 mins)- 1 hour min of clouds if you have 4, 2 hours if you have 8
byte OvercastMax=((CloudsTotal*10)/2);//max cloud length will be about 2500 seconds (45 mins)- 6 hours max of clouds if you have 8, 3 hours max if you have 4
float Overcast=random(OvercastMin,OvercastMax);
Overcast=(Overcast/100);
// split the total lenght of time for clouds into equal segments and then to randomly chop or add time to the
//segments such that cloud length is variable. Then distribute into random parts of the day and fill array with start,duration pairs for clouds
int CloudLength;
CloudLength=((dayLength*Overcast)/CloudsTotal);//average cloud length
long SunSegment=((dayLength-(dayLength*Overcast))/(CloudsTotal+1));//average sun length between clouds
float CloudFraction=0;
float SunFraction=0;
//start by zero filling CloudMaster array
for (byte a=0; a<20; a++){
CloudMaster[a]=0;
byte b=0;//used to get pairs of fraction for SunFraction in for loop
byte c=0;//used to get pairs of fraction for CloudFraction in for loop
//now randomize cloud length and sunsegment length as pairs to get different looking days-
for (byte a=0; a<(CloudsTotal*2); a++){
if (a%2==0){
if (b==0){
if (a==0){
SunFraction=random(20,181);//vary each pair of SunSegments from 20%-180% of possible length such that every pair =2*SunSegment in length
SunFraction=(SunFraction/100);
CloudMaster[a]=(SunFraction*SunSegment);
else if (a<((CloudsTotal*2)-2)){
b++;
else if (a==((CloudsTotal*2)-2)){
SunFraction=(2-((float)CloudMaster[0]/(float)SunSegment));
else if (b==1){
SunFraction=(2-SunFraction);//were on the second part of a pair
b=0;//reset so next time we start a new fraction
else if (a%2==1){//if were in odd positions we need to determine cloud lengths in random pairs such that each pair =2*CloudLength in length
if (c==0){
CloudFraction=random(20,181);//vary each pair of SunSegments from 20%-180% of possible length such that every pair =2*SunSegment in length
CloudFraction=(CloudFraction/100);
CloudMaster[a]=(CloudFraction*CloudLength);
c++;
else if (c==1){
CloudFraction=(2-CloudFraction);
c=0;//reset so next loop finds a new fraction
/*Serial.println("here is cloud master in is entirety prior to forming start and end pairs");
for (byte a=0;a<20;a++){
Serial.println(CloudMaster[a]);
//reframe array to generate cloud start, cloud end, cloud start, cloud end
if (a==0){// if were starting our first cloud we need to add to rise value to first sun segment
CloudMaster[a]=rise+CloudMaster[a];
else {
CloudMaster[a]=(CloudMaster[a-1]+CloudMaster[a]);//just add prior values together e.g. (second position is cloud end so to find end add rise corrected start time with duration)
// subsequent start would be end of 1st cloud + next sunsegment fraction
/*Serial.println("here is cloud master in is entirety as start and end pairs");
if (a%2==0){
Serial.print("Start time=");
else {
Serial.print("End time=");
}//END SunCalc FUNCTION
void Insolation()
InsolationAdvance=false;//reset this flag now that we have entered function
//define Pi as delta Y for slope since cos 0.5-1.5 Pi goes 0-1-0 in 0.5 pI increments slope of 1/2 day (0-1 intensity) delta Y is 1/2 Pi
float Pi=3.1415926;//scale to 10^8
float PiHalf=1.5707963;//scale to 10^8
float secSoFar;//variable to account for seconds elapsed for each channel 1/2 day period from rise-->midDay and midDay-->set
/* using -cos(pi/2+elapsedTime/slope) calculate fractional intensity of each channel throughout the day
use flicker points to adjust minimum intensity to stable light. Turn off lights after set or before rise etc.
by splitting into half days centered on midday (1/2 ofset-rise) we center exactly the cos function for every channel so color blends are maintained
throughout intensity ramp... more or less ... change intensity every 120 seconds throughout the day*/
if (elapsedTime<=midDay){
byte c=0;//loop counter
for (byte b=0;b<16;b=(b+2)){
if (elapsedTime>=ChRiseSet[b]){
secSoFar=(elapsedTime-ChRiseSet[b]);//just account for length of every channel 1/2 day and switch at midDay
ChannelValue[c]=flicker[c]+ChMax[c]*(-cos(PiHalf+(ChSlope[b]*secSoFar)));
else if (elapsedTime<ChRiseSet[b]){
if (MoonCh[c]==1){
byte MoonToday=MoonPhase()*0.5;//SCALE FACTOR to DIM moon setting for use with HIGH power LED as moon light
if (MoonToday==0) ChannelValue[c]=0;
else if (MoonToday<flicker[c]) ChannelValue[c]=flicker[c];
else ChannelValue[c]=MoonToday;
else if (MoonCh[c]==0){
ChannelValue[c]=0;//its dark and this is not a moon phase channel
c++;//index by one so we count 0-7 as b goes 0-14 by twos
else if (elapsedTime>midDay){
for (byte b=1;b<16;b=b+2){
if (elapsedTime<=ChRiseSet[b]){
secSoFar=(elapsedTime-midDay);
ChannelValue[c]=flicker[c]+ChMax[c]*(-cos(Pi+(ChSlope[b]*secSoFar)));
else if (elapsedTime>ChRiseSet[b]){
if (MoonCh[c]==1){
c++;//index to count 0-7 as b counts 1-15 by twos.
}//END function
//WEATHER FUNCTION BEGIN
void Weather ()
static byte loopCount;
static float CloudCover; // variable to store value in random walk - declared static to accumulate Cloud effect
static float PriorCloudCover; //used to "delay" one side of the tank from the other in cloud passing effects
static long StormStart;
static long StormEnd;
static long CloudEnd;
static boolean wtrigger;//use to track the first run of functions to calculate random times that become fixed, see change from cloud to storm for useage
static byte Counter;//used to trigger storms from cloud you can change its if loop comparison to decrease or increase storm rate see below in cloud==true if loop
static byte Severity;
static byte StormCount;// used to limit X storms per cloud and to choose which cloud can have a storm
static int StepSize;
static int LastStepSize;
//check to see if were having a scheduled cloud
if (Cloud==false){
//Write Insolation values to TrueIntensity so the loop will pick them up and the cloud/storm will get the right data (since intensity changes during the day)
for (byte a=0; a<8; a++){//this must be above the next loop
TrueIntensity[a]=ChannelValue[a];//this is where intensity is set for the PWM channel analog write in the loop... don't mess with this.
for (byte a=0; a<(CloudsTotal*2); a=(a+2)){//if its time for a cloud, run it
if ((elapsedTime>=CloudMaster[a]) && (elapsedTime<=CloudMaster[(a+1)])) {
CloudEnd=CloudMaster[(a+1)];//to avoid this loop running true during the compute cycles at the end of the cloud and before elapsedTime advances a second, actual cloud does not
//Serial.print("We started a cloud and its end is=");
//Serial.println(CloudEnd);
CloudCover=CloudStart(CloudMaster[a]);//CloudStart modifies TrueIntensity to get us to 50% intensity at the start of the cloud effect and also sets cloud=true to bypass this
Counter=0;
StormCount=random(0,3);//the number of storms MAX that may occur in this cloud (remember Random is range= -1 on high end)
loopCount=1;
LastStepSize=0;//zero out cloud random walk variables
StepSize=0;//zero out cloud ranodm walk variables
return;//exit having started a cloud in CLoudStart routine called above
else if ((Cloud==true) && (IsStorm==false)){
if (StormAdvance==false){//use millis tracker to run this loop every 2 seconds
return;
StormAdvance=false;//reset to false when true so we run this once, until time advance is true again
if (elapsedTime>=CloudEnd){
ClearSky(CloudCover, CloudEnd);
return;
/*Use fractional intensity to set minimum value for any channel. Dimming is proportional to actual intensity output
and constrained by flicker point. Random walk uses static variable "CloudCover" constrained to 0-100 to represent fractional intensity (i.e. (1-(CloudCover/100))*Insolation SetPoint
is how the current cloud intensity is set, i.e. cloud cover of 90 gives 10% insolation setpoint unless below flicker in which case = flicker*/
if (loopCount==1){
PriorCloudCover=CloudCover; //e.g. PriorCloudCover=CloudCover with no float math to screw things up
LastStepSize=StepSize;
StepSize=(random(5,21));// in Percent% (0-100) This is how much light intensity will change over the loop count interval (this actual time is dependent upon the call frequency of StromAdvance as set in the loop)
if ((random(0,2)!=1)) StepSize=-(StepSize);
if ((CloudCover+StepSize)>=100){//cannot shut off lights more than 100% so limit here
StepSize=(100-CloudCover);//
Counter++;
else if ((CloudCover+StepSize)<=0){//cannot be brighter than 100% so since were in a cloud dont "limit" it but reflect it back down
if (Counter>=50) Counter-=random(-1,2);//since we got bright... lets further delay and randomize storm occurence
CloudCover=CloudCover+StepSize;
if ((Counter>=60) && ((CloudEnd-elapsedTime)>=300)) {//if Counter (indexes when cloud cover reaches 100) has accumulated and we still have time lets make a storm
//to change the frequency of storms increase or decrease the number comparison for counter in the if statement above (larger #== less storms).
//if you change counter comparison here change it in the next loop as well
if (StormCount>=1){//if we can have storms in this cloud (random- statisticly 1/3 clouds = no storm, 1/3 = 1 possible storm, 1/3 = 2 possible storms)
byte RandomStorm;
RandomStorm=random(0,11);//this randomizes for longer clouds without storm, avg cloud is much longer prior to storm occuring- thus short clouds will not generally have a storm
if (RandomStorm>=4){
StormCount-=1;//count down by 1 the number of storms in this cloud- this will not roll the byte since the loop requires it to be at least 1 to ever subtract here.
Counter=0;//reset this variable since Storm loop uses it as well.
int LongestStorm;//used to pass max possible time to storm if loop from cloud loop within weather function
LongestStorm=(CloudEnd-elapsedTime);
Severity=StartStorm(LongestStorm, IsStorm, StormEnd);
loopCount=1;//reset counting loop for the storm
else if ((Counter>=60) && ((CloudEnd-elapsedTime)<300)){
Counter=0;//just reset the counter (does not really matter in this case but its clean)
for (int a=0;a<8;a++){
if (ChannelValue[a]==0) TrueIntensity[a]=0;// if were in an evening storm dont reset intensity (it would go to flicker point and possibly flicker)
else if (DimOrder[a]==0){
TrueIntensity[a]=(flicker[a]+(((float)(ChannelValue[a]-flicker[a]))*(1-((CloudCover-(StepSize-(StepSize/4)*loopCount))/100))));
else if (DimOrder[a]==1){
TrueIntensity[a]=(flicker[a]+(((float)(ChannelValue[a]-flicker[a]))*(1-((PriorCloudCover-(LastStepSize-(LastStepSize/4)*loopCount))/100))));
loopCount++;
if (loopCount>4) loopCount=1;
//enable a flag sent from controller to triger a storm, i.e. IsStorm=true
// set channel intensities for all but white with random walk continuing from above using static variable so should be seamless
else if (((Cloud==true) && (IsStorm==true)) || ((Cloud==false) && (IsStorm==true))){
//current else statement covers possibility of triggering storm from controller (i.e. not coming out of a cloud) but remember you need to flag wtrigger as TRUE when you do this
if (StormAdvance==false){//Every 1 second duing a storm change intensity, clouds are movin fast baby
return;
StormAdvance=false;//reset so we run again in 1 second.
if (elapsedTime>=StormEnd){ //if were done with the storm we need to stop this loop, but were probably still cloudy so dont mess with that here
IsStorm=false;
Counter=0;
return;
if (loopCount==1){
Counter++;
if (Counter>=2) Counter-=random(0,2);//since we got bright... lets further delay and randomize strike occurence
if (Counter>(Severity+2)) Counter=0;//allow if to accumulate on ocassion to train strike sequences 2-3 in a row but then dump it
if ((Counter>=(Severity+random(-1,4))) && (StrikeNow==false)) {//this is where a storm is triggered. Counter indexes when cloud cover reaches 100 on the random walk
//to change the frequency of lightning strikes increase or decrease the number comparison for counter in the if statement above (larger #== less storms).
byte RandomStriker;
RandomStriker=random(1,11);
if (RandomStriker>4){
StrikeNumber=(random(2,11)); //random high =x-1 so max strike =12 each strike requires a duration and a delay thus StrikeMaster is 18 positions
//ensure the array is zeroed out past the last position required for this strike pattern so each pattern is only as long as generated
//Array is in pairs, position in arry of (0,1) (2,3) etc as strike (delay,duration)
if (a>=(StrikeNumber*2)){
StrikeMaster[a]=0;
if (a%2==0){
if (a==0){
StrikeMaster[a]=random(300,1601);//no need for random here but I am leaving it since I wrote it that way. This must be independent from a=2,4,6 etc...
else {
StrikeMaster[a]=(StrikeMaster[(a-2)]+random(200,1401));//position 0,2,4,6,8.. is strike delay
else if(a%2!=0){
StrikeMaster[a]=random(50,110);//position 1,3,5,7,9... is strike duration (I tried real lightning strike durations and its too short this is adjusted for visual effect
StrikeNow=true; //Trigger to start strike sequence in loop
StrikeStart=millis();//set timer to "zero" now- sequence will start in loop after this function
StrikeCount=0;
Counter=0;
if (Severity>5){
for (int a=0;a<8;a++) {
else if (Wchannel[a]==1){//if were in a storm but not a severe storm constrain whites to 50% of Insolation intensity
TrueIntensity[a]=(flicker[a]+((((float)(ChannelValue[a]-flicker[a])/4))*(1-((CloudCover-(StepSize-(StepSize/3)*loopCount))/100))));
TrueIntensity[a]=(flicker[a]+((((float)(ChannelValue[a]-flicker[a])/4))*(1-((PriorCloudCover-(LastStepSize-(LastStepSize/3)*loopCount))/100))));
else if (Wchannel[a]==0){//if were blue, we chase as for a cloud
TrueIntensity[a]=(flicker[a]+(((float)((ChannelValue[a]-flicker[a])))*(1-((CloudCover-(StepSize-(StepSize/3)*loopCount))/100))));
TrueIntensity[a]=(flicker[a]+((((float)(ChannelValue[a]-flicker[a])))*(1-((PriorCloudCover-(LastStepSize-(LastStepSize/3)*loopCount))/100))));
else if (Severity<=5){// severe storms occur throughout the day, but EVERY storm after sunset is severe...
else if (Wchannel[a]==1){//if were white we need to be off in a storm
TrueIntensity[a]=0;
else if (ChannelValue[a]==0){//if this light channel is dark... e.g. after sunset for this channel- it produces no cloud effect
TrueIntensity[a]=0;
else if (Wchannel[a]==0){//if were not shut off in a strom and not after our daylight period (this channel) then we produce storm light sequences.
if (DimOrder[a]==0){//if we dim first... do it
else if (DimOrder[a]==1){//else we dim second
}//end of CWHchannel==0 being true
}//end of for loop in severity <5 == true loop
}//end severity compairson loop no more else statements
loopCount++;
if (loopCount>3) loopCount=1;
}//end of storm if loop
}//End Weather function
//CloudStart drops light intensity to 50% of whatever daylight setting is to start the cloud at 50
int CloudStart(long StartTime){
byte elapsed;
elapsed=(elapsedTime-StartTime);//counts up since we start this at elapsedTime=StartTime and StartTime is fixed
TrueIntensity[a]=(flicker[a]+(((float)((ChannelValue[a]-flicker[a])))*(1-(elapsed*2.5)/100)));
if (elapsed>=20);
Cloud=true;//start the cloud
return 50;//set CloudCover to 50
}//end CloudStart function
//StartStorm sets up duration and severity of storm. Its currently limited to 90-600 sec in length- it will rarely be lower than 3 minutes
byte StartStorm(int MaxLength, boolean& trigger, long& EndTime){
byte LightningIntensity;
int StormDuration;
MaxLength-=120;//remove 2 mins from longest storm so that we end up with 2 minutes of cloud after the storm before the sky clears to daylight
if (MaxLength>720){
MaxLength=720;//modify local variable
StormDuration=random((MaxLength/3),(MaxLength+1));
EndTime=(elapsedTime+StormDuration);//Set by reference StormEnd static variable in weather
else {
StormDuration=random((MaxLength/2),(MaxLength+1));
if (elapsedTime<midDay){
LightningIntensity=random(3,11);//morning storms are generally less severe
else if (elapsedTime>midDay){//afternoon storms are more likely to be severe (every 10-15 sec or less) to about once in a minute or maybe less
if (elapsedTime>(set-rise)){//Storms after sunset are always severe... it just looks too cool!
LightningIntensity=3;
else {
LightningIntensity=random(3,8);
trigger=true;
return (LightningIntensity);
//End Storm Start Function
//Similar to Cloud start but in reverse... now ramp intensity from wherever we were at the end of the cloud to the value set by Insolation
void ClearSky(int CloudPercent, long TerminationTime)
byte elapsed=(elapsedTime-TerminationTime);//Counts up from the scheduled end of the cloud in seconds
float slope=(CloudPercent/30);//Just calculate how much to increment every second to go from CloudCover to clear sky (CloudCover of zero)
float LightAdvance;
LightAdvance=(CloudPercent-(slope*elapsed));//were reducing CloudCover from start to zero over 10 seconds.
TrueIntensity[a]=(flicker[a]+(((float)(ChannelValue[a]-flicker[a]))*(1-(LightAdvance/100))));
if (elapsed>=30){//at this point lights are back to full Insolation setting so cancel the cloud and start waiting for the next one
Cloud=false;//stop the cloud we are now outside of a true condition in the if loop so it will now stay false and lights are back on
IsStorm=false;//just to be redundant this is not called from a storm...
}//End Clear Sky function
byte MoonPhase()
int m,d,y;
int yy,mm;
long K1,K2,K3,J,V;
byte PWMvalue;
m = month();
d = day();
y = year();
yy = y-((12-m)/10);
mm = m+9;
if (mm>=12) mm -= 12;
K1 = 365.25*(yy+4712);
K2 = 30.6*mm+.5;
K3 = int(int((yy/100)+49)*.75)-38;
J = K1+K2+d+59-K3;
V = (J-2451550.1)/0.29530588853;
V -= int(V/100)*100;
V = abs(V-50);
PWMvalue = 4*abs(50-V); // 5.12=100% 4=~80%
//pinMode(lowATOPin,OUTPUT);
//return (PWMvalue*100)/255; //output is 0-100
return PWMvalue;//output is 0-255
//********************** DO NOT MESS WITH THIS UNLESS YOU KNOW WHAT YOUR DOING****************************
//THE CODE BELOW THIS copied directly from the SWFLTEK Epherma library constructed by Michael Rice.
//this code is being used freely with attribution to Micahel Rice in accord with his request
// A big thank you for these library functions. Its great!
//convert degrees to seconds of arc
// decimal degrees
long ddToSeconds(float dd){
return dd * 3600.0;
//Degrees, minutes, seconds
long dmsToSeconds(int d, unsigned char m, unsigned char s){
long ret;
ret = labs((long)d);
ret = ret * 3600L + 60L * m + s;
ret = (d<0L) ? -ret : ret;
return ret;
'Equation of Time'
We use the 'short form equation, which has a theoretical accuracy of about 40 seconds.
The returned value is in seconds.
int equation_of_time(unsigned long dt){
double t;
dt -= 192540UL; // refer to Jan 3 2000 05:29 (first periapsis)
dt %= _tropical_year;
t = dt;
t /= _tropical_year;
t *= 6.283185307179586;
t = -459.27672 * sin(t) + 575.333472 * sin(2.0 * t + 3.588414);
return t;
'Solar Noon' adjusts the passed time stamp to the time (GMT) of local solar noon.
The accuracy is about 40 seconds (set by the equation of time).
void SolarNoon(unsigned long * dt){
long r;
// Set stamp to noon GMT
*dt /= 86400UL;
*dt *= 86400UL;
*dt += 43200UL;
// adjust for equation of time, at noon GMT
*dt -= equation_of_time(*dt);
// rotate to our longitude
r = longitude / 15L;
*dt -= r;
'Solar Declination'
Returns declination in radians
Accurate to within 50 arc-seconds
double SolarDeclination(unsigned long dt){
double y;
y = dt;
y /= _tropical_year; // fractional year
y *= 6.283185307179586;
y=0.006918-0.399912*cos(y)+0.070257*sin(y)-0.006758*cos(y*2)+0.000907*sin(y*2)-0.002697*cos(y*3)+0.00148*sin(y*3);
return y;
Return the period between sunrise and sunset, in seconds.
At high latitudes around the time of the solstices, this could be zero, or all day.
unsigned long daylightseconds(unsigned long dt){
float l, d, e;
long n;
d = -SolarDeclination(dt); // will be positive in Northern winter
l = latitude / _sec_rad; // latitude in radians
e += 60.0 * l * tan(l + d); // latitudinal error
d = tan(l) * tan(d); //
if(d>1.0) return 86400UL;
if(d < -1.0) return 0UL;
d = acos(d);
d /= _zenith;
n = 86400UL * d;
n += e;
return n;
Modify the passed time stamp to the time of sunrise (or sunset if 'set' is non-zero).
Returns 0 to signal 'normal' completion. If the position is in a polar circle, 1 will be
returned if the sun is above the horizon all day, and -1 if the sun is below the horizon
all day.
char SunRiseSet(unsigned long * dt, char set){
unsigned long daylen;
daylen = daylightseconds(*dt);
if(daylen == 86400UL) return 1; // there is no 'night' today (midnight sun)
if(daylen == 0UL) return -1; // there is no 'day' today
*dt /= 86400UL;
*dt *= 86400UL;
*dt += 43200UL; // set the time stamp to 12:00:00 GMT
*dt -= daylen / 2; // sunrise at the prime meridian
if(set) *dt += daylen; // sunset at the prime meridian
//*dt -= longitude / 15.0; // rotate to our own meridian
return 0;
// 'short' forms of SunRiseSet
char SunRise(unsigned long* when){
return SunRiseSet(when, 0);
char SunSet(unsigned long* when){
return SunRiseSet(when, 1);
ReefAngel.StandardHeater( Port3,820,825 );
ReefAngel.StandardLights( Port7,21,0,7,0 );
ReefAngel.SingleATO( true,Port1,90,0 );
ReefAngel.WavemakerRandom(Port5,15,45);
ReefAngel.WavemakerRandom1(Port6,15,45);
static unsigned long feeding = 0;
if ((now()%SECS_PER_DAY==28800) || (now()%SECS_PER_DAY==50400) || (now()%SECS_PER_DAY==72000)) //if it is 8am or 2pm or 8 pm
if ( feeding == 0 )
feeding = now(); //set the time of the start of feeding to variable feeding
if ((now()-feeding>=60) && (now()-feeding<=61)) //if between 60 and 61 seconds has past
ReefAngel.Relay.On(Port8); //TURN FEEDER RELAY ON
ReefAngel.Relay.Off(Port8); //TURN FEEDER RELAY OFF
if ( feeding > 0 ) {
feeding = 0;
elapsedTime=(now()-newDay);//Elapsed time is seconds from midnight of today- local processor time.
wdt_reset();
if (cmdnum!=255){
ProcessCMD(cmdnum,datanum);
cmdnum=255;
datanum=255;
if (dow!=day()){ //used to see that were in a new day and need to recalculate sunrise and sunset
CalSun();
dow=day();
//Use millis to enable tracking of time interval
if ((millis()-lastmillis)>=100){
counter+=1;
StormAdvance=true;
//now a bunch of stuff that may or may not be true at the same time but that all needs to happen when its true
if (counter==0){
InsolationAdvance=true;//so that it runs on start up to provide light immediately
if (counter%30==0){
if (counter==210) counter=0;
if (InsolationAdvance==true) Insolation();//calculate clear sky solar intensity as the day advances
Weather();//run the weather overlay (cloud, storm)
//check to see if were need to have a lightning strike
if (StrikeNow==true){
if ((millis()-StrikeStart)>=StrikeMaster[(StrikeCount*2)]){//check if time has passed the delay (position 0,2,4,6,8 etc in StrikeMaster)-StrikeCount is indexed up by 1 after each strike so we see positions 0,2,4,6,etc in sequence
byte intensity;
intensity=random(180,256);// this little bit should generate a randomly bright flash variation between the series of flashes in StrikeMaster
for (byte b=0; b<6; b++){
if (StrikeChannel[b]==1) analogWrite(PWMports[b],intensity);// set all strike channels to intensity of strike
delay(StrikeMaster[((StrikeCount*2)+1)]);//index to +1 position in array from 0,2,4, etc to 1,3,5 etc
StrikeCount++;//so that the next time we look at elapsed time were looking at the right array position
if (StrikeCount==(StrikeNumber-1)){
StrikeNow=false;
StrikeCount=0;
ReefAngel.AddWifi();
int x,y;
// pH Expansion
ReefAngel.LCD.DrawSingleMonitor( ReefAngel.Params.PHExp,COLOR_MEDIUMSEAGREEN,39,66, 100 );
nevermind, figured it out. Didn't need to have it in the pde as well.
After uploading this to my main unit, the screen just stays dark. What did I do wrong?
Its not written to run on the main....
It is doing things like hard coded write to PMW channels which will do nothing on the main since it does not have that...
I have made an effort and have said in the past that I am working on it- in working on it a bit it became obvious (after spending some hours trying) that I was not going to be able to easily get it ported to OO code and I stopped because even getting it set up to test it out was something I simply have not done before.
Since there appears to be an ongoing interest and implementation of this code, lets see if someone has time to help. If thats the case then everyone will benefit. I am happy to spend time with a more experienced person to basically work together using their skills in porting and my knowledge of how the code goes together to figure out where to split this up.
IF your knowledgable about the RA head unit and how its making calls to the dimming module to run the light intensities, I can show you pretty much where you need to edit to change the existing code so that it runs the PWM module. However, depending on which includes you have in your PDE code for the head, it may becomes somewhat complicated. Up to you... I am more interested in working with someone who can help pull this into the library distribution as this will solve the problem for everyone regardless of expertise.
No, I don't have the bandwidth at this time. I believe binder had offered to help with the OO aspect.
The SunLocation class has a lot of the SWFLTEK code in it and could probably be used as a reference. The link is in the first or second post on my INO page in my signature.
yeah, I can help out with the OO part of code and getting it set up as an includable library for the controller.lnevo wrote:No, I don't have the bandwidth at this time. I believe binder had offered to help with the OO aspect.
I have not looked back at the current code yet. But if it's currently working in a state that you are happy with, I can start with that code and see what all i can put together making references to the sunlocation class as well.
So, if someone would either PM me the current code or point me to link for the current code and just summarize what it needs to do (sounds like just have it run off of the headunit ports or make calls to control the pwm expansion ports) and the possible things that need to be configured (duration, chance, etc), then I should be able to start hashing something out for people.
Sent from my Nexus 7
Binder, that would be awesome! I think the working code is on the first page. I would love to help with this but my coding is not up to par yet. It needs to be able to run off of the main controller and run the pwm expansion. The original code was meant to just run the pwm ports 0 - 5 of course, but it would be great to be able to control 2 or more pwm expansions. I don't believe this would require any more work, but I'm not sure....
Kurt-
I am sending you a PM-
dlplunkett44
Controlling more than 1 PMW dimming module is possible- but it means modifying a fair number of arrays in the code which is basically trivial. However, it also would require a beta tester to deal with trouble shooting the code. Since I wrote it with the idea that we could control only 1 dimming module, and since its working this way for now and will capture the vast majority of users- I am going to start here and PM back and forth with Kurt so he can package this up into a module. Once thats working, then its basically "Easy" to start thinking about how to do this and you, or anyone else could grab the code from the library and changes can be made locally to get it working. So long as nothing major changed in terms of how we get this packaged in (e.g. we only changed the number of addressable PMW ports) I do not see why that could not then be passed onto Kurt to basically replace the first run- single PWM module code in the library. But since I only have a single PMW module, and I do NOT have a RA+ its going to be hard for me to help test code beyond my equipment capabilities.
We will post here as we get code together thats worth testing, as I suspect that we will want a few guinea pigs to try this on the main before it gets actually put into the distribution= to avoid headaches with a bunch of people breaking stuff all at once and no one having working lights!
dlplunkett44
I got the PM. I will be reading through it over the next few days and start coming up with some ideas as to what all needs to be done.
Consider me a guinea pig! I only have one PWM expansion now, but down the road I will need more channels and will approach this at that time. Thanks!
I would be happy to be a guinea pig for this project too.
Not sure if this makes a difference or not, but I have an analog version of the dimming module so it works for my Apollo Reef LED's. I currently just run it with the parabola function for my 4 channels... although I'm able to change any parameters (start/end % and/or times) via the android app on the fly, so I think this weather sim code will work for me too.
While I'm not an expert when it comes to coding, I do have a custom code running that's a bit more complicated than most are running and I feel that I could help track down any errors.
That sounds great- I am currently the weak link in the chain moving forward. I have been to busy lately to take even a few hours and ensure that what Kurt gets is exactly what we want to see as a library code. I have revised the code that protects against photo bleaching during long summer days and ensures a user specified minimum light on period on winter days where rise and set may be too short to ensure adequate light over the tank. I want to make this optional so that those who want the rise and set times to exactly match compited can do so, and suffer the consequences if they end up bleaching or browning, or have it so that you simply instruct it what you minimum light cycle must be give. your max intensity settings are so that in the winter it adds time to get that light period. During the summer I am using a scaling routine where the percent of day lenght beyond the desired light period is used to subtly scale back max intensities so that you get correlation with rise and set to their exact calculated values, but the tank does not bleach. I have been testing this for a year now and want to adjust one thing- check the rest of the code and send it on to Kurt.
Sorry for being the weak link... it will happen soon
Trust me, being the President of the reefing club I'm in (NJ Reefers) I know what it's like to juggle time between your home life and volunteering on a community project.
This project may not even be this far along if you hadn't already done the groundwork you've done so far. A little more time won't kill us, heh.
no worries here. my schedule is hectic as well. that's just the "fun" with things.
Hi all,
I'm actually using this code with my arduino uno with great success. I was wondering if it's possible to add coding for coral acclimation for x days with the max say 65% gradually ramping up to 100% again across the x days. The acclimation part would be initialized by a push button. Thanks.
Hello, I'm new here. I tried out the sketch, I'm using a arduino uno but when I go to the serial monitor it don't show anything? Anyone else experience this?
And also is there a way to turn off the storm function - and still have the cloud function?
89delta wrote:Hi all,
I have created Dimming Acclimation code.
The first post in this thread will walk you through it.
http://forum.reefangel.com/viewtopic.php?f=12&t=4193
I have not created any menu options to begin acclimation. It is started by setting the AcclDay to the same value you have chosen for your AcclDuration(Total days in accl cycle).
Did this ever get ported to the head unit with any luck?
I'm working on getting my LED's running and would love to have a storm mode set up, but I have no idea how to dow this.