Page 1 of 2
Mike's RSM 500 Code
Posted: Sun Sep 08, 2013 1:53 pm
by modulok
I have two Vortech MP40s on the way, as well as the RF Expansion and Expansion Hub. I should have everything by Tuesday.
Here are my ideas:
- Enable Center lights on for 10mins after RA feed mode
- MP40: Change modes throughout the day, night mode when lights are off, feed mode
- I would like to put both MP40s on the main relay (flow1-3, return, skimmer, MP40, MP40)
- Change Power Failure mode so that a single MP40 goes to low power mode (Main Relay Box is connected to UPS)
I was thinking to update the light schedule. I have 3 separate fixtures, and was thinking of giving each a 15 minute break every few hours. Would it work just by giving separate ReefAngel.StandardLights for a single fixture, leaving 15 min gaps when necessary?
Here is my current code.
//--------------------------------- Place global variable code below here ---------------------------------
boolean PowerOutage=false;
boolean DelayedPowerOutage=false;
// Globals for Params on Custom Main
byte x,y;
//--------------------------------- Custom Menu ---------------------------------
#include <avr/pgmspace.h>
prog_char menu0_label[] PROGMEM = "Turn Lights On";
prog_char menu1_label[] PROGMEM = "Turn Lights Off";
prog_char menu2_label[] PROGMEM = "Start Feeding";
prog_char menu3_label[] PROGMEM = "Start Water Change";
prog_char menu4_label[] PROGMEM = "Clear Overheat";
prog_char menu5_label[] PROGMEM = "Calibrate pH";
prog_char menu6_label[] PROGMEM = "Display Version";
menu0_label, menu1_label, menu2_label, menu3_label, menu4_label, menu5_label, menu6_label };
void MenuEntry1()
ReefAngel.DisplayMenuEntry("Item 1");ReefAngel.Relay.RelayMaskOn = ReefAngel.LightsOnPorts;
#ifdef RelayExp
ReefAngel.Relay.RelayMaskOnE[i] = ReefAngel.LightsOnPortsE[i];
#endif // RelayExp
ReefAngel.Relay.Write();
void MenuEntry2()
ReefAngel.DisplayMenuEntry("Item 2");ReefAngel.Relay.RelayMaskOn = 0;
#ifdef RelayExp
ReefAngel.Relay.RelayMaskOnE[i] = 0;
#endif // RelayExp
void MenuEntry3()
ReefAngel.DisplayMenuEntry("Item 3");ReefAngel.FeedingModeStart();
void MenuEntry4()
ReefAngel.DisplayMenuEntry("Item 4");ReefAngel.WaterChangeModeStart();
void MenuEntry5()
ReefAngel.DisplayMenuEntry("Item 5");ReefAngel.OverheatClear();
void MenuEntry6()
ReefAngel.DisplayMenuEntry("Item 6");ReefAngel.SetupCalibratePH();
void MenuEntry7()
ReefAngel.DisplayMenuEntry("Item 7");ReefAngel.DisplayVersion();
//--------------------------------- End Custom Menu Globals ---------------------------------
//--------------------------------- Place global variable code above here ---------------------------------
//--------------------------------- Begin Custom Main ---------------------------------
ReefAngel.LCD.DrawDate(5, 2);
// Display T1 Probe Value
ReefAngel.LCD.DrawHugeNumbers(COLOR_CRIMSON, 255, 5, 14, text);
// Display pH Text
ReefAngel.LCD.DrawText(COLOR_INDIGO,255,80,14,"pH");
// Display pH Value
ReefAngel.LCD.DrawLargeText(COLOR_INDIGO, 255, 95, 14, text, Num8x16);
// Display T3 Probe Text
ReefAngel.LCD.DrawText(COLOR_ROYALBLUE,255,80,24,"Rm");
// Display T3 Probe Value
ConvertNumToString(text, ReefAngel.Params.Temp[T3_PROBE], 10);
ReefAngel.LCD.DrawLargeText(COLOR_ROYALBLUE, 255, 95, 24, text, Num8x16);
//Moon Phase
ReefAngel.LCD.Clear(DefaultBGColor,5,88,95,95);
ReefAngel.LCD.DrawText(COLOR_CORNFLOWERBLUE,255,5,88,MoonPhaseLabel());
//Dimmable Moon LEDs
ReefAngel.LCD.DrawText(COLOR_NAVY,255,5,98, "MoonLEDs:");
ReefAngel.LCD.Clear(DefaultBGColor,59,98,75,106);
ReefAngel.LCD.DrawText(COLOR_CORNFLOWERBLUE,255,59,98, ReefAngel.PWM.GetActinicValue());
ReefAngel.LCD.DrawText(COLOR_CORNFLOWERBLUE,255,75,98, "%");
// Display Main Relay Box
ReefAngel.LCD.DrawOutletBox( 2, 107, TempRelay );
ReefAngel.LCD.DrawOutletBox( 2, 119, TempRelay );
//--------------------------------- End Custom Main ---------------------------------
//--------------------------------- Begin Setup ---------------------------------
// Initialize the menu
ReefAngel.FeedingModePorts = Port1Bit | Port2Bit | Port3Bit | Port4Bit | Port5Bit | Port7Bit; //Flow1-3,Return,Skimmer,CoolingFan
ReefAngel.FeedingModePortsE[0] = Port2Bit | Port6Bit; //FrontT5,SumpHeater
ReefAngel.WaterChangePorts = Port1Bit | Port2Bit | Port3Bit | Port4Bit | Port5Bit | Port6Bit | Port7Bit; // Flow1-3,Return,Skimmer,DispHeater,CoolingFan
ReefAngel.WaterChangePortsE[0] = Port2Bit | Port3Bit | Port6Bit; //Front+BackT5,SumpHeater
ReefAngel.LightsOnPortsE[0] = Port1Bit | Port2Bit | Port3Bit; //Center+Front+BackT5
ReefAngel.OverheatShutoffPorts = Port6Bit; //DispHeater
ReefAngel.OverheatShutoffPortsE[0] = Port2Bit | Port3Bit | Port5Bit | Port6Bit; //Front+BackT5,FugeLight,SumpHeater
//--------------------------------- Place additional initialization code below here ---------------------------------
ReefAngel.Timer[1].SetInterval(5);
//--------------------------------- Place additional initialization code above here ---------------------------------
//--------------------------------- End Setup ---------------------------------
//--------------------------------- Begin Loop ---------------------------------
ReefAngel.Relay.On( Port1 ); //Flow1
ReefAngel.Relay.On( Port2 ); //Flow2
ReefAngel.Relay.On( Port3 ); //Flow3
ReefAngel.Relay.On( Port4 ); //Return
//Delay Start
ReefAngel.Relay.DelayedOn( Port5,5 ); //Skimmer
/*Feed Mode Delay on Pump
static boolean feeding=true;
static unsigned long feedingstarted = 0;
if (!feeding)
feeding=true;
feedingstarted = now();
} else {
feeding=false;
int pumpdelay=InternalMemory.FeedingTimer_read()-240; // 4 minute delay
if (now()-feedingstarted<=pumpdelay) {
ReefAngel.Relay.Off( Port1 ); //Flow1
ReefAngel.Relay.Off( Port2 ); //Flow2
ReefAngel.Relay.Off( Port3 ); //Flow3
// Ports that are delayed on Power Cycle & Feeding & Water Change
if (PowerOutage && ReefAngel.Relay.IsRelayPresent(EXP1_RELAY))
PowerOutage=false;
LastStart=now();
// Heaters
ReefAngel.StandardHeater( Port6,770,774 ); //DispHeater
ReefAngel.StandardHeater( Box1_Port6,768,772 ); //SumpHeater
// Cooling Fan
ReefAngel.StandardFan( Port7,812,814 ); //Cooling Fan
// T5 Light Schedule
ReefAngel.StandardLights( Box1_Port1,9,0,20,0 ); //CenterT5 9a-8p
ReefAngel.StandardLights( Box1_Port2,10,0,18,0 ); //FrontT5 10a-6p
ReefAngel.StandardLights( Box1_Port3,10,30,18,45 ); //BackT5 1030a-645p
// RSMLED Moonlight Schedule
if (hour()>=6 && hour()<=8) ReefAngel.StandardLights( Box1_Port4,6,0,8,59 ); //RSMLED Morning 6a-9a
else if(hour()>=20 && hour()<=23) ReefAngel.StandardLights( Box1_Port4,20,0,23,45 ); //RSMLED Evening 8p-1145p
else if(hour()>=23 || hour()<=4) if (MoonPhase()>=90) ReefAngel.StandardLights( Box1_Port4,23,46,4,0 ); //RSMLED on for Full Moon 1146p-4a
// Fuge Light Schedule
//ReefAngel.StandardLights( Box1_Port5,0,0,8,0 ); //FugeLight 12a-8a
// PWM Dimmable Moonlights Schedule
if (hour()>=21 || hour()<4) // Turn Dimmable Moonlights on 9p & off 4a
ReefAngel.PWM.SetActinic(0);
ReefAngel.PWM.SetDaylight(0);
//--------------------------------- Place your custom code below here ---------------------------------
// Turn on Fuge light during water change mode
//if (ReefAngel.DisplayedMenu==WATERCHANGE_MODE) ReefAngel.Relay.On(Box1_Port5);
// Power Outage - Only Flow2 port on
if (!ReefAngel.Relay.IsRelayPresent(EXP1_RELAY)) PowerOutage=true; //Exp1 Relay NOT present
if (!PowerOutage)
ReefAngel.Timer[1].Start();
if (ReefAngel.Timer[1].IsTriggered())
DelayedPowerOutage=true;
if (DelayedPowerOutage)
ReefAngel.Relay.Off (Port1); //Flow1
//ReefAngel.Relay.Off (Port2); //Flow2
ReefAngel.Relay.Off (Port3); //Flow3
ReefAngel.Relay.Off (Port4); //Return
ReefAngel.Relay.Off (Port5); //Skimmer
ReefAngel.Relay.Off (Port6); //Heater
// Skimmer off when Return pump is off.
if (bitRead(ReefAngel.Relay.RelayMaskOff,3)==0) //Return
bitClear(ReefAngel.Relay.RelayMaskOff,4); //Skimmer
//////////// Place your custom code above here ////////////
ReefAngel.Portal( "modulok" );
//--------------------------------- End Loop ---------------------------------
Re: Mike's RSM 500 Code
Posted: Sun Sep 08, 2013 7:10 pm
by modulok
Here is what I am thinking for the light schedule. Giving each fixture a 15min break every 2hrs. Any reason why it would be bad for the lights/fixture?
// Center T5 Light Schedule [ 9:15am - 6:00pm ]
ReefAngel.StandardLights( CenterT5,9,15,11,15 ); //0915-1115
ReefAngel.StandardLights( CenterT5,11,30,13,30 ); //1130-1330
ReefAngel.StandardLights( CenterT5,13,45,15,45 ); //1345-1545
ReefAngel.StandardLights( CenterT5,16,00,18,00 ); //1600-1800
// Front T5 Light Schedule [ 10:00am - 6:45pm ]
ReefAngel.StandardLights( FrontT5,10,0,12,0 ); //1000-1200
ReefAngel.StandardLights( FrontT5,10,0,18,0 ); //1215-1415
ReefAngel.StandardLights( FrontT5,10,0,18,0 ); //1430-1630
ReefAngel.StandardLights( FrontT5,10,0,18,0 ); //1645-1845
// Back T5 Light Schedule [ 11:15am - 8:00pm ]
ReefAngel.StandardLights( BackT5,11,15,13,15 ); //1115-1315
ReefAngel.StandardLights( BackT5,13,30,15,30 ); //1330-1530
ReefAngel.StandardLights( BackT5,15,45,17,45 ); //1545-1745
ReefAngel.StandardLights( BackT5,18,0,20,0 ); //1800-2000
Posted: Sun Sep 08, 2013 7:42 pm
It works, but you need to do some leg work, which would make it very hard to understand.
The way I would do it is set the StandardLights for the entire period and override it off when you what them off
Something like this:
ReefAngel.StandardLights( CenterT5,9,15,18,0 ); //0915-1800
if (hour()==11 && minute()>=15 && minute()<=30) ReefAngel.Relay.Off(CenterT5);
Posted: Fri Sep 13, 2013 4:21 pm
by modulok
Something is very wrong now. After a few minutes, the red light starts blinking on the RA. On the display only a few ports shown as on, although everything that should be on is in fact on. Same ports show as on with the Android app. Can't turn on anything either.
I did a full power cycle for both relays and it did not help.
I added both MP40s to the RA (used the vortech setup code and such), and they are both white and running.
EDIT: ok, 8PM now, center T5 is still on, App and LCD show it as turned off. MoonLEDs should be on, like signature says, but they are not. I'm going to revert back to older code and see if problem is still there.
Any suggestions? I'm going to wait until 8 and see if the light goes off like it should.
// Define Relay Ports by Name
#define Flow1 1
#define Flow2 2
#define Flow3 3
#define Return 4
#define Skimmer 5
#define VortechL 6
#define VortechR 7
#define HeaterDisp 8
#define CenterT5 Box1_Port1
#define FrontT5 Box1_Port2
#define BackT5 Box1_Port3
#define MoonLED Box1_Port4
#define Unused Box1_Port5
#define Unused Box1_Port6
#define FanSump Box1_Port7
#define HeaterSump Box1_Port8
byte x,y;
void MenuEntry1()
#ifdef RelayExp
#endif // RelayExp
void MenuEntry2()
#ifdef RelayExp
#endif // RelayExp
void MenuEntry3()
void MenuEntry4()
void MenuEntry5()
void MenuEntry6()
void MenuEntry7()
// Display pH Text
// Display pH Value
//Moon Phase
ReefAngel.InitMenu(pgm_read_word(&(menu_items[0])),SIZE(menu_items)); // Initialize the menu
ReefAngel.FeedingModePorts = Port1Bit | Port2Bit | Port3Bit | Port4Bit | Port5Bit; //Flow1-3,Return,Skimmer
ReefAngel.FeedingModePortsE[0] = Port2Bit | Port7Bit | Port8Bit; //FrontT5,FanSump,SumpHeater
ReefAngel.WaterChangePorts = Port1Bit | Port2Bit | Port3Bit | Port4Bit | Port5Bit | Port8Bit; // Flow1-3,Return,Skimmer,DispHeater
ReefAngel.WaterChangePortsE[0] = Port2Bit | Port3Bit | Port7Bit | Port8Bit; //Front+BackT5,FanSump,SumpHeater
ReefAngel.OverheatShutoffPorts = Port8Bit; //DispHeater
ReefAngel.OverheatShutoffPortsE[0] = Port1Bit | Port2Bit | Port3Bit | Port8Bit; //Center+Front+BackT5,SumpHeater
ReefAngel.Relay.On( Flow1 );
ReefAngel.Relay.On( Flow2 );
ReefAngel.Relay.On( Flow3 );
ReefAngel.Relay.On( Return );
ReefAngel.Relay.On( VortechL );
ReefAngel.Relay.On( VortechR );
ReefAngel.Relay.DelayedOn( Skimmer,1 );
//Vortech
ReefAngel.RF.SetMode( ReefCrest,30,10 );
if (!feeding)
feeding=true;
} else {
feeding=false;
ReefAngel.Relay.Off( Flow1 );
ReefAngel.Relay.Off( Flow2 );
ReefAngel.Relay.Off( Flow3 );
// Temperature
ReefAngel.StandardHeater( HeaterDisp,770,774 );
ReefAngel.StandardHeater( HeaterSump,768,772 );
ReefAngel.StandardFan( FanSump,812,814 );
// Light Schedule
ReefAngel.StandardLights( CenterT5,9,0,20,0 ); //CenterT5 9a-8p
if (hour()==12 && minute()>=30 && minute()<=45) ReefAngel.Relay.Off(CenterT5);
if (hour()==16 && minute()>=30 && minute()<=45) ReefAngel.Relay.Off(CenterT5);
ReefAngel.StandardLights( FrontT5,10,0,18,0 ); //FrontT5 10a-6p
if (hour()==13 && minute()>=15 && minute()<=30) ReefAngel.Relay.Off(FrontT5);
if (hour()==16 && minute()>=15 && minute()<=30) ReefAngel.Relay.Off(FrontT5);
ReefAngel.StandardLights( BackT5,10,30,18,45 ); //BackT5 1030a-645p
if (hour()==13 && minute()>=45 && minute()<=0) ReefAngel.Relay.Off(BackT5);
if (hour()>=6 && hour()<=8) ReefAngel.StandardLights( MoonLED,6,0,8,59 ); //RSMLED Morning 6a-9a
else if(hour()>=20 && hour()<=23) ReefAngel.StandardLights( MoonLED,20,0,23,45 ); //RSMLED Evening 8p-1145p
else if(hour()>=23 || hour()<=4) if (MoonPhase()>=90) ReefAngel.StandardLights( MoonLED,23,46,4,0 ); //RSMLED on for Full Moon 1146p-4a
PowerOutage=false;
LastStart=now();
// Power Outage
if (!ReefAngel.Relay.IsRelayPresent(EXP1_RELAY)) PowerOutage=true; //Expansion Relay 1 has lost power
if (!PowerOutage)
ReefAngel.Relay.Off (Flow1);
ReefAngel.Relay.Off (Flow2);
ReefAngel.Relay.Off (Flow3);
ReefAngel.Relay.Off (Return);
ReefAngel.Relay.Off (Skimmer);
ReefAngel.Relay.Off (VortechL);
ReefAngel.Relay.Off (HeaterDisp);
// When Return pump is off shut off Skimmer & FanSump
if (!ReefAngel.Relay.Status(Return)) {
ReefAngel.Relay.Override(Skimmer,0);
ReefAngel.Relay.Override(FanSump,0);
//--------------------------------- Place your custom code above here ---------------------------------
Posted: Fri Sep 13, 2013 8:41 pm
by modulok
Went back to old code and it looks like its stable again. I got scared when I saw the heater light turn on, but the RA and app wasn't aware of that!
On the setup for both Vortech MP40s...I did the reset on each unit and hooked the BOTH to the RF unit. Each pump is either white or orange (when pressing mode).
Is this correct? Do the pumps think the RF module is the master pump, and you can set the left or right pump to sync/anti-sync?
ie: Left Vortech white driver and Right Vortech orange driver for anti-sync/opposite side as master.
EDIT: Also, why does the app show this?
Mode Reef Crest
Speed 20%
Duration 20%
Isn't the code below stating 10 duration?
ReefAngel.RF.SetMode( ReefCrest,20,10 );
Posted: Sat Sep 14, 2013 7:34 am
by modulok
I uploaded new code, still stuck with ReefCrest, 20, 10. Had the same issue with the blinking red light on controller, and no response from android app.
I commented out the RF lines and reuploaded. Now both MP40s are in Nutrient Mode, at 50% power and 10ms. I NEVER set a mode other than ReefCrest. What is going on here?
Edit: Red blinking light is back! Cannot control anything again, will need to power cycle the head unit.
Posted: Sat Sep 14, 2013 8:45 am
Yes, the pumps will think that the RF module is master and each pump can be setup as sync (white) or anti-sync(orange).
If you use ReefAngel.RF.UseMemory = true;, that's when the controller will use the settings shown in the app or portal.
If you use ReefAngel.RF.UseMemory = false;, it will ignore the memory settings and use your hard coded settings
In my case, I use memory settings (long pulse at 75% with 300s pulse) during the day. I change to UseMemory = false at night to slow down the pumps and also at 3pm through 6pm when it runs long pulse at 100% with 3s pulse.
This is the code for your reference:
if (ReefAngel.DisplayedMenu!=FEEDING_MODE || ReefAngel.DisplayedMenu!=WATERCHANGE_MODE)
if (hour()>=15 && hour()<=17)
ReefAngel.RF.UseMemory=false;
ReefAngel.RF.SetMode(LongWave,100,3);
else if (hour()>=22 || hour()<7)
ReefAngel.RF.SetMode(ReefCrest,40,0);
ReefAngel.RF.UseMemory=true;
The red blinking is being cause by noise or bad connection somewhere in the expansion bus.
Can you check your connections and see if you've got any cables going too close to any ballasts/drivers?
If that doesn't work, we can try changing the firmware of the rf module.
Posted: Sat Sep 14, 2013 9:28 am
by modulok
What do you mean by ballasts/drivers? I have both relay boxes, expansion, relay exp,and RF exp in close proximity, and the wifi exp is the only one next to the RA head unit. The two MP40 drivers are 2-3 feet from other equip right now.
I am thinking that when I commented out the RF lines the internal memory setting took over. On the portal it does say Nutrient @ 50%...
Posted: Sat Sep 14, 2013 9:39 am
I meant LED drivers/MH ballasts.
They generate quite a bit of noise and interference that can be picked up by the bus if place too close to them.
Posted: Sat Sep 14, 2013 9:51 am
by modulok
OK, only LEDs I have are the moonlights on the PWM, which have been in the same location since January.
I will replug everything and see if issue persists...if that's not it, how do I do firmware for RF exp?
Posted: Sat Sep 14, 2013 10:28 am
by modulok
OK, when I unplug the RF module the red light turns off. And I can control ports.
Posted: Sat Sep 14, 2013 11:49 am
Try this update.
You need to open the enclosure and connect the USB-TTL cable with the black wire on the GND pin.
Then, you need to edit the file update.bat to use whatever com port you are using.
Double-click the update.bat file to start updating.
Posted: Sat Sep 14, 2013 12:00 pm
by modulok
Which is the ground pin?
Posted: Sat Sep 14, 2013 12:15 pm
Sorry, I forgot to say to remove the RF module too.
- RF.png (18.62 KiB) Viewed 8756 times
Posted: Sat Sep 14, 2013 12:25 pm
by modulok
libusb0.dll is missing error when I run the bat file (avrdude.exe)
EDIT:Got the fix...Had to copy that file to c:\Windows\syswow64
RF firmware should be updated now. Going to plug it back in and see what happens.
Posted: Sat Sep 14, 2013 2:03 pm
by modulok
Same issue....after a bit red light comes on and relays don't toggle on/off. When I unplug RF module the relays toggle (even when I manually toggle when red light is blinking).
Is my RF module a dud?
Posted: Sat Sep 14, 2013 5:36 pm
Ok, are you sure you got it updated?
Did it go through the % from 0 to 100?
Posted: Sat Sep 14, 2013 6:01 pm
by modulok
OK, I didn't see any percentage...the command window closed when it was finished. I just re-ran the update by running it manually so the window didn't auto exit.
EDIT: My RA just had two power outage scenarios (code that was working fine), when power was fine (relay exp never lost power). Could the root cause be the new Expansion Hub?
avrdude -Cavrdude.conf -v -patmega328p
-carduino -P\\.\COM6 -b115200 -D -Uflash:w:RF_Update_WDT_modified.hex:i
System wide configuration file is "avrdude.conf"
Using Port : \\.\COM6
Using Programmer : arduino
Overriding Baud Rate : 115200
avrdude: stk500_getsync(): not in sync: resp=0x64
avrdude done. Thank you.
Posted: Sun Sep 15, 2013 8:56 am
No, it didn't upload.
It needs to upload just like in RA.
It will flash the red led for a few seconds and there will be a % bar.
Did you remove the Ecotech RF module?
It won't work with the RF module plugged into the board.
Posted: Sun Sep 15, 2013 9:17 am
by modulok
I don't think I understand...here is what I did.
I unplugged the RF Exp Module and removed the board from the plastic case. Hooked up the USB TTL to the RF board (pic I posted above) black wire to ground pin. Connect USB end to computer and run the command.
Sent from my Nexus 7 using Tapatalk 4
Posted: Sun Sep 15, 2013 1:06 pm
You must also remove the Ecotech RF module before you can upload or it will thing the serial data is supposed to be sent to the vortech drivers.
Posted: Thu Jun 04, 2015 4:23 pm
by modulok
It's been awhile since I have needed to update code, but the power outage function wasn't working.
Not sure why but the power outage was below "// This should always be the last line" When I moved it up I couldn't compile. What did I do wrong here?
Getting the following compile error at: void CheckPower() {
updated_code.cpp: In function 'void loop()':
updated_code:165: error: a function-definition is not allowed here before '{' token
updated_code:257: error: expected `}' at end of input
// Define Named Relay Ports
#define Flow1 1
#define Flow2 2
#define Flow3 3
#define Return 4
#define Skimmer 5
#define VortechL 6
#define VortechR 7
#define Reactor Box1_Port6
#define Fan Box1_Port7
// Custom Main
byte x,y;
////// Setup Begin
// Controlled Modes Toggled Ports
ReefAngel.FeedingModePortsE[0] = Port7Bit | Port8Bit; //Fan,HeaterSump
ReefAngel.WaterChangePorts = Port1Bit | Port2Bit | Port3Bit | Port4Bit | Port5Bit | Port8Bit; // Flow1-3,Return,Skimmer,HeaterDisp
ReefAngel.WaterChangePortsE[0] = Port2Bit | Port3Bit | Port6Bit | Port7Bit | Port8Bit; //Front+BackT5,Reactor,Fan,HeaterSump
// Water Temperature Settings & Overheat
ReefAngel.OverheatShutoffPorts = Port8Bit; //HeaterDisp
ReefAngel.OverheatShutoffPortsE[0] = Port2Bit | Port3Bit | Port8Bit; //Front+BackT5,HeaterSump
ReefAngel.Relay.On( Reactor );
// Ports that are always off
ReefAngel.Relay.Off(Unused);
//5 second timer for power outage detection
////// Setup End
////// Loop Begin
// Ports that are Delayed
ReefAngel.Relay.DelayedOn( Skimmer,2 );
// Temperature Control
ReefAngel.StandardHeater( HeaterSump,770,773 );
ReefAngel.StandardHeater( HeaterDisp,767,770 );
ReefAngel.StandardFan( Fan,810,814 );
if (hour()==14 && minute()>=0 && minute()<=59) ReefAngel.Relay.Off(CenterT5);
if (hour()==15 && minute()>=0 && minute()<=29) ReefAngel.Relay.Off(FrontT5);
ReefAngel.StandardLights( BackT5,11,0,19,0 );
if (hour()==16 && minute()>=0 && minute()<=29) ReefAngel.Relay.Off(BackT5);
// RSM MoonLED Schedule
if (hour()>=6 && hour()<=8) ReefAngel.StandardLights( MoonLED,6,0,8,59 ); //Morning
else if(hour()>=20 && hour()<=23) ReefAngel.StandardLights( MoonLED,20,0,23,45 ); //Evening
else if(hour()>=23 || hour()<=4) if (MoonPhase()>=90) ReefAngel.StandardLights( MoonLED,23,46,4,0 ); //Full Moon
// Moonphase LED Schedule
if (hour()>=20 || hour()<4)
//T5 Light Off Variable
//if (hour()==12 && minute()>=30 && minute()<=44) ReefAngel.Relay.Off(CenterT5);
//if (hour()==12 && minute()>=15 && minute()<=29) ReefAngel.Relay.Off(FrontT5);
//if (hour()==16 && minute()>=15 && minute()<=29) ReefAngel.Relay.Off(FrontT5);
//if (hour()==13 && minute()>=45 && minute()<=59) ReefAngel.Relay.Off(BackT5);
//if (hour()==16 && minute()>=45 && minute()<=59) ReefAngel.Relay.Off(BackT5);
// Vortech MP40 | Constant | Lagoon | ReefCrest | ShortWave 1=10ms | LongWave 1=1s | NutrientTransport 1=10ms | TidalSwell
if (hour()>=16 && hour()<=19)
ReefAngel.RF.SetMode(LongWave,50,30);
else if (hour()>=20 || hour()<7)
ReefAngel.RF.SetMode(Lagoon,25,0);
// When Return pump is off so is Skimmer
void CheckPower() {
static boolean PowerOutage=false;
static boolean DelayedPowerOutage=false;
// Power Outage - Leave Single Flow Pump Powered
if (!PowerOutage)
//set vortechs to low power
// Power Restored
PowerOutage=false;
LastStart=now();
ReefAngel.Portal( "*****","*****" );
////// Loop End
////// Custom Main Begin
// Display Date & Time
// Display Water Temp Value
// Display pH Text
// Display pH Value
// Display Room Temp Text
// Display Room Temp Value
// Vortech Info
//Moon Phase
////// Custom Main End
////// Custom Graph Begin
///// Custom Graph End
Posted: Thu Jun 04, 2015 6:31 pm
you cannot define a function within another function. your checkpower function is being defined inside the loop function code.
move it out and that should help.
Posted: Sun Jun 07, 2015 11:14 am
I went ahead and updated your code and moved everything around how it should be. I test compiled and everything compiles just fine. I did not upload the code to a controller though.
The formatting is updated too. You will also need to put your portal information back in since you removed it before.
Hope this helps.
#define Flow1 1
#define Flow2 2
#define Flow3 3
#define Return 4
#define Skimmer 5
#define VortechL 6
#define VortechR 7
// Custom Main
byte x, y;
////// Setup Begin
ReefAngel.Relay.Off( Unused );
ReefAngel.Timer[1].SetInterval( 5 );
////// Setup End
////// Loop Begin
ReefAngel.Relay.DelayedOn( Skimmer, 2 );
ReefAngel.StandardHeater( HeaterSump, 770, 773 );
ReefAngel.StandardHeater( HeaterDisp, 767, 770 );
ReefAngel.StandardFan( Fan, 810, 814 );
ReefAngel.StandardLights( CenterT5, 9, 0, 20, 0 );
if ( hour() == 14 && minute() >= 0 && minute() <= 59 ) {
ReefAngel.Relay.Off( CenterT5 );
ReefAngel.StandardLights( FrontT5, 10, 0, 18, 0 );
if ( hour() == 15 && minute() >= 0 && minute() <= 29 ) {
ReefAngel.Relay.Off( FrontT5 );
ReefAngel.StandardLights( BackT5, 11, 0, 19, 0 );
if ( hour() == 16 && minute() >= 0 && minute() <= 29 ) {
ReefAngel.Relay.Off( BackT5 );
if ( hour() >= 6 && hour() <= 8 ) {
ReefAngel.StandardLights( MoonLED, 6, 0, 8, 59 ); //Morning
} else if( hour() >= 20 && hour() <= 23 ) {
ReefAngel.StandardLights( MoonLED, 20, 0, 23, 45 ); //Evening
} else if( hour() >= 23 || hour() <= 4 ) if ( MoonPhase() >= 90 ) {
ReefAngel.StandardLights( MoonLED, 23, 46, 4, 0 ); //Full Moon
if ( hour() >= 20 || hour() < 4 ) {
} else {
ReefAngel.PWM.SetActinic( 0 );
ReefAngel.PWM.SetDaylight( 0 );
if ( ReefAngel.DisplayedMenu != FEEDING_MODE || ReefAngel.DisplayedMenu != WATERCHANGE_MODE ) {
if ( hour() >= 16 && hour() <= 19 ) {
ReefAngel.RF.SetMode( LongWave, 50, 30 );
} else if ( hour() >= 20 || hour() < 7 ) {
ReefAngel.RF.SetMode( Lagoon, 25, 0 );
} else {
if ( !ReefAngel.Relay.Status( Return ) ) {
ReefAngel.Relay.Override( Skimmer, 0 );
// Check the power here, the function is defined below
CheckPower();
ReefAngel.Portal( "*****", "*****" );
////// Loop End
////// Custom Function
void CheckPower()
static boolean PowerOutage = false;
static boolean DelayedPowerOutage = false;
if ( !ReefAngel.Relay.IsRelayPresent( EXP1_RELAY ) ) {
PowerOutage = true; //Expansion Relay 1 has lost power
if ( !PowerOutage ) {
if ( ReefAngel.Timer[1].IsTriggered() ) {
DelayedPowerOutage = true;
if ( DelayedPowerOutage ) {
ReefAngel.Relay.Off ( Flow1 );
ReefAngel.Relay.Off ( Flow2 );
ReefAngel.Relay.Off ( Flow3 );
ReefAngel.Relay.Off ( Return );
ReefAngel.Relay.Off ( Skimmer );
ReefAngel.Relay.Off ( HeaterDisp );
// Power Restored
if ( PowerOutage && ReefAngel.Relay.IsRelayPresent( EXP1_RELAY ) ) {
LastStart = now();
////// Custom Function End
ReefAngel.LCD.DrawDate( 5, 2 );
ReefAngel.LCD.Clear( COLOR_BLACK, 1, 11, 132, 11 );
ConvertNumToString( text, ReefAngel.Params.Temp[T1_PROBE], 10 );
ReefAngel.LCD.DrawHugeNumbers( COLOR_CRIMSON, 255, 5, 14, text );
// Display pH Text
ReefAngel.LCD.DrawText( COLOR_INDIGO, 255, 80, 14, "pH" );
// Display pH Value
ConvertNumToString( text, ReefAngel.Params.PH, 100 );
ReefAngel.LCD.DrawLargeText( COLOR_INDIGO, 255, 95, 14, text, Num8x16 );
ReefAngel.LCD.DrawText( COLOR_ROYALBLUE, 255, 80, 24, "Rm" );
ConvertNumToString( text, ReefAngel.Params.Temp[T3_PROBE], 10 );
ReefAngel.LCD.DrawLargeText( COLOR_ROYALBLUE, 255, 95, 24, text, Num8x16 );
// Vortech Info
//Moon Phase
ReefAngel.LCD.Clear( DefaultBGColor, 5, 88, 95, 95 );
ReefAngel.LCD.DrawText( COLOR_CORNFLOWERBLUE, 255, 5, 88, MoonPhaseLabel() );
ReefAngel.LCD.DrawText( COLOR_NAVY, 255, 5, 98, "MoonLEDs:" );
ReefAngel.LCD.Clear( DefaultBGColor, 59, 98, 75, 106 );
ReefAngel.LCD.DrawText( COLOR_CORNFLOWERBLUE, 255, 59, 98, ReefAngel.PWM.GetActinicValue() );
ReefAngel.LCD.DrawText( COLOR_CORNFLOWERBLUE, 255, 75, 98, "%" );
Posted: Tue Jun 23, 2015 3:32 pm
by modulok
Thanks a lot!
I uploaded the updated code and the power outage is working now.
Strange thing is that the overheat function isn't working now...I did a full power off and it temp is 82.0 and the overheat light isn't coming on and the ports aren't shutting off....any ideas?
Posted: Thu Jun 25, 2015 11:54 am
hmmm...more checking is needed. nothing is standing out to me at quick glance.
Posted: Sun Jul 05, 2015 6:57 pm
by modulok
So I recalibrated my pH probe for the first time since I set it up (Nov 2012). Before the calibration I had a pH or 8.34 and now after its at 7.75.
Could the pH be off by that much after about 2.5 years?
Posted: Mon Jul 06, 2015 9:10 am
by modulok
Forgot to mention that I moved the pH probe from the back of the display tank to the sump, could that be the difference? I'll move it back tonight and report back.
Any ideas on the overheat function not working?
Posted: Mon Jul 06, 2015 11:49 am
If you get T1 above 82F, nothing happens?
Not even the status LED?
Posted: Mon Jul 06, 2015 11:55 am
by modulok
Correct, last week t1 was at 82 and ports did not shut off and the red light did not come on. I could try and get t1 above 82.
Sent from my HTC One_M8 using Tapatalk
