For awhile now, I've wanted to us the IO module to trigger a series of LEDs on the tank stand. I wanted to put 3 LEDs on the cabinet (red/yellow/green) and trigger a color change when something was out of spec. (Temp, ATO errors, water level, pH, etc) That way I can see from across the room if anything is off. I suppose I could run a series of if/then statements, but that doesn't seem very efficient. I thought I could then trigger a memory space to change at a specific location, but then everything in spec would keep correcting the change if the error triggers a change. Maybe I could use a series of memory locations and then query all of them to see if anything in that memory range has changed? Is there a better way to do this?
Thanks for the advice,
Jon
Error Log/LEDs
- jsclownfish
- Posts: 378
- Joined: Mon Oct 24, 2011 7:52 pm
- Location: Saint Louis
Re: Error Log/LEDs
So if I want to check say 10 things (water level, ATO, pH, Temps, Flows, etc), would I just have a long cascade of if, else if, else if...?
-Jon
-Jon
Re: Error Log/LEDs
Pretty much, but it also depends on which color you want to light up with what parameter.
The way I would do is probably like this:
The way I would do is probably like this:
Code: Select all
boolean RedLEDStatus=false;
if (ReefAngel.Params.Temp[T1_PROBE]>810) RedLEDStatus=true;
if (ReefAngel.Params.PH>840) RedLEDStatus=true;
if (!ReefAngel.HighATO.IsActive()) RedLEDStatus=true;
digitalWrite (RedLEDPin,RedLEDStatus);
Roberto.