Things I am needing help with
DmnYnkee
Post by DmnYnkee »
Below is my current code. A bit more clunky than it may need to be as I am definitely still early in the learning curve, but it seems to be working well.
Here is what I am wanting to do:
1) If port8 (ATO pump) is on for longer than 3 minutes, I want to turn off port8 and send an email alert. (Either my ATO float is stuck, or ATO reservoir is low) //avoid system over fill
2) If HighATO is inactive for longer than 5 minutes, I want an alert email sent. (ATO pump failure, major system leak, ato reservoir low) //avoid system low volume
3) I would like to incorporate automatic monthly temperature adjustments similar to what "hedrickms" put together. I tried his code, and it wouldn't compile.
4) I would like my actinic lights to follow actual sunrise/sunset times with daylights coming on 2 hours later, and shutting off 2 hours before. Hopefully, within a year, I will upgrade my t5's to Radions, and get even more custom in the lighting area.
Thanks in advance for any assistance.
  int avgph[10];
    unsigned long totalavgph=0;
    byte avgindex=0;
      byte x;
      byte y = 2;
      char text[7];
      // *********** CHANGE TEMP READOUT COLOR DEPENDENT ON FAN AND HEATER STATUS ***********
      int TempColor;                                    // Color for drawing temperature
      boolean FanOn = ReefAngel.Relay.Status(Port5);    // Get the status of the fan relay
      boolean HeatOn = ReefAngel.Relay.Status(Port6);   // Get the status of the heater relay
      if (HeatOn)
        TempColor = COLOR_NAVY;                         // Blue text, too cold, heater is on
      if (FanOn)
          TempColor = COLOR_RED;                        // Red text, too warm, fan is on
      if (!HeatOn && !FanOn)
          TempColor = COLOR_GREEN;                      // Green text, no fan or heater on
           int pHColor;                                 // Color for drawing pH
      boolean LowpH = (ReefAngel.Params.PH < 780) ;     // Check for Low pH Value
      boolean HighpH = (ReefAngel.Params.PH > 850);     // Check for High pH Value
      if (LowpH)
        pHColor = COLOR_NAVY;                          // Blue text, Low pH value
      if (HighpH)
        pHColor = COLOR_RED;                           // Red text, High pH value
      if (!LowpH && !HighpH)
        pHColor = COLOR_GREEN;                         // Green text, pH acceptable
      ReefAngel.LCD.DrawLargeText(COLOR_MAGENTA,DefaultBGColor, 6, 3, "Thunder Reef",Font8x8);       // Put a banner at the top
      ReefAngel.LCD.DrawDate(6, 119);        // Put the date and time at the bottom
      ReefAngel.LCD.Clear(COLOR_BLACK, 1, 12, 132, 12);                                                 // Draw a cyan line under the banner
      x = 6;
      y += MENU_START_ROW*1.4;        // MENU_START_ROW is 10, according to globals.h, so y=2+10+1=13
      ReefAngel.LCD.DrawLargeText(COLOR_BLUE, COLOR_WHITE, x, y+1, " Temp      pH");
      ConvertNumToString(text, ReefAngel.Params.Temp[T1_PROBE], 10);                                    // Get T1 temp and convert
      x = 2;
      y += MENU_START_ROW*1.6;
      ReefAngel.LCD.DrawHugeNumbers(COLOR_BLACK, TempColor, x, y, text);                                // Draw the temperature, white numbers on a colored background
      ConvertNumToString(text, ReefAngel.Params.PH, 100);                                               // Get pH reading and convert
      x = 2;
      y = MENU_START_ROW*2.6;
      ReefAngel.LCD.DrawHugeNumbers(COLOR_YELLOW, pHColor, x+65, y+6, text);                            // Put pH on the screen
      x += 6;
      y += MENU_START_ROW*3.3;
  ReefAngel.LCD.DrawLargeText(COLOR_INDIGO,DefaultBGColor,25,y,"Sump Level",Font8x8);      // Draw the Sump Float switch status
    ReefAngel.LCD.FillCircle(15,y+3,7,COLOR_GREEN);
    ReefAngel.LCD.FillCircle(15,y+3,7,COLOR_RED);
  x += 6;
  y += MENU_START_ROW*2.0;
  ReefAngel.LCD.DrawLargeText(COLOR_INDIGO,DefaultBGColor,25,y,"Skimmer Cup",Font8x8);     // Draw the Skimmer Cup Float switch status
      byte TempRelay = ReefAngel.Relay.RelayData;                                          // Code for drawing the relay box
      ReefAngel.LCD.DrawOutletBox(12, 100, TempRelay);
    ReefAngel.FeedingModePorts = Port7Bit;
    ReefAngel.WaterChangePorts = Port1Bit | Port7Bit | Port8Bit;
    ReefAngel.OverheatShutoffPorts = Port2Bit | Port3Bit | Port4Bit | Port6Bit | Port7Bit;
    ReefAngel.Relay.On( Port7 );
    ReefAngel.CustomLabels[0]="Return";
    ReefAngel.CustomLabels[1]="Daylights";
    ReefAngel.CustomLabels[2]="Actinics";
    ReefAngel.CustomLabels[3]="Fuge Light";
    ReefAngel.CustomLabels[4]="Sump Fan";
    ReefAngel.CustomLabels[5]="Heater";
    ReefAngel.CustomLabels[6]="Skimmer";
    ReefAngel.CustomLabels[7]="ATO";
    ReefAngel.StandardLights( Port2,10,0,18,0 );        //  Daytime bulbs    10:00 am -  6:00 pm
    ReefAngel.StandardLights( Port3,8,0,20,0 );         //  Actinic bulbs     8:00 am -  8:00 pm
    ReefAngel.StandardLights( Port4,17,30,10,30 );      //  Refugium light    5:30 pm - 10:30 am
    ReefAngel.StandardFan( Port5,785,787 );
    ReefAngel.StandardHeater( Port6,783,785 );
if (hour()>=9 && hour()<11)
 ReefAngel.PWM.SetDaylight( LongPulseMode(0,55,10,true) ); // Long pulse at 55% with 10s pulse on sync mode
 ReefAngel.PWM.SetActinic( LongPulseMode(0,55,10,false) ); // Long pulse at 55% with 10s pulse on Anti-sync mode
else if (hour()>=11 && hour()<12)
 ReefAngel.PWM.SetDaylight( LongPulseMode(0,60,5,true) ); // Long pulse at 60% with 5s pulse on sync mode
 ReefAngel.PWM.SetActinic( LongPulseMode(0,60,5,false) ); // Long pulse at 60% with 5s pulse on Anti-sync mode
else if (hour()>=12 && hour()<13)
 ReefAngel.PWM.SetDaylight( LongPulseMode(0,65,2,true) ); // Long pulse at 65% with 2s pulse on sync mode
 ReefAngel.PWM.SetActinic( LongPulseMode(0,65,2,false) ); // Long pulse at 65% with 2s pulse on Anti-sync mode
else if (hour()>=13 && hour()<14)
 ReefAngel.PWM.SetDaylight( ShortPulseMode(0,71,680,true) ); // Short pulse at 71% with 680ms pulse on sync mode
 ReefAngel.PWM.SetActinic( ShortPulseMode(0,71,680,false) ); // Short pulse at 71% with 680ms pulse on Anti-sync mode
else if (hour()>=14 && hour()<15)
 ReefAngel.PWM.SetDaylight( ShortPulseMode(0,78,680,true) ); // Short pulse at 78% with 680ms pulse on sync mode
 ReefAngel.PWM.SetActinic( ShortPulseMode(0,78,680,false) ); // Short pulse at 78% with 680ms pulse on Anti-sync mode
else if (hour()>=15 && hour()<16)
 ReefAngel.PWM.SetDaylight( ShortPulseMode(0,87,680,true) ); // Short pulse at 87% with 680ms pulse on sync mode
 ReefAngel.PWM.SetActinic( ShortPulseMode(0,87,680,false) ); // Short pulse at 87% with 680ms pulse on Anti-sync mode
else if (hour()>=16 && hour()<17)
else if (hour()>=17 && hour()<18)
else if (hour()>=18 && hour()<19)
else if (hour()>=19 && hour()<20)
else if (hour()>=20 && hour()<21)
 ReefAngel.PWM.SetDaylight( ReefCrestMode(40,10,true) ); // reefcrest at 40% +/- 10% on sync mode  (night mode)
 ReefAngel.PWM.SetActinic( ReefCrestMode(40,10,true) ); // reefcrest at 40% +/- 10% on sync mode  (night mode)
if( ReefAngel.DisplayedMenu==FEEDING_MODE )
 ReefAngel.PWM.SetActinic(0);
 ReefAngel.PWM.SetDaylight(0);
    if(ReefAngel.LowATO.IsActive())          //  Float switch in Skimmer Cup
    ReefAngel.Relay.On(Port7);
    ReefAngel.Relay.Off(Port7);              //  Turn off Skimmer when Cup full.
    if(ReefAngel.HighATO.IsActive())         //  Float switch in Sump
    ReefAngel.Relay.Off(Port8);
    ReefAngel.Relay.On(Port8);               //  Turn on ATO when sump level drops.
    ReefAngel.Portal( "DmnYnkee" );
Re: Things I am needing help with
1. Replace this:
With this:
ReefAngel.SingleATO(true,Port8,300,0);
Use portal for email alert on ATO timeout
2. Use the Portal for HighATO
4. I'm pretty sure your code is already like that.
These are the lines:
DmnYnkee
Post by DmnYnkee »
1.
Would using SingleATO code have any affect on the LowATO that I am using for skimmer? What would be the check value in the portal, ATO Timeout Flag >=1 ? In my mind, this was not to be flagged by the ato, but by port8, in case the port fails and gets stuck "on", as well as other possible reasons. I suppose I could also set an alert in portal for Relay port 8, but what check value could be used for "if on longer than 3 minutes"
2. What would be the check value in the portal for inactive for 5 min or more? Doing this can only get an alert once an hour, correct? Is there any way to write into the code to get notification quicker for either 1. or 2.?
4. There was a rather long thread dealing with this, but I am not exactly sure how to use the end result code for this application, and what extra files might need to be copied into my files. sunrise/sunset data
http://forum.reefangel.com/viewtopic.ph ... it=sunrise
Thanks much
The ATO timeout flag gets set if port8 is on for 300s. It will not influence low ATO.
You can get the alert quicker with the WifiAlert function, but it will require you to use the development branch of our libraries until it gets released officially.
lnevo said there is still a bug that has to be fixed before it can be released. I'll be checking on that soon.
DmnYnkee
Post by DmnYnkee »
ok, so I am trying to understand this as I continue through it.
If I Replace this:
With this:
What will be the trigger that tells Port8 to turn on?
So, this is for a single ATO switch setup where one ATO port controls both on and off. This is opposed to a dual switch setup where the low switch turns on the ATO and the high switch turns it off.
"true" means use the high port. "low" would use the low port.
Port8 is the relay the topoff pump is plugged into.
300 is the number of seconds the pump can run continuously before it times out and stops. This is for overflow protection.
The last zero is how often the pump can be switched on. For example, if you put a 1 here, the pump can only turn on once per hour (keeps the pump from switching on and off rapidly if you have a bouncy water level in your sump).
So, with this code, port 8 will turn on and off with the high ATO switch, and run up to 300 seconds continuously.
DmnYnkee
Post by DmnYnkee »
Makes sense, but does it use the high ATO active to run the pump using this code? In my code, inactive is the flag to run, and active means sump lvl is good.
In this case, the true/false works for High/Low, like calling Sync/Anti-Sync on dimming. Correct?
DmnYnkee
Post by DmnYnkee »
Also, should I break the other parts I am wanting to do into separate forum threads, so as to works through 1 topic at a time?
Chris
DmnYnkee wrote:Makes sense, but does it use the high ATO active to run the pump using this code? In my code, inactive is the flag to run, and active means sump lvl is good.
I'm not exactly sure about the first part. I get them confused. Try it, and if it's opposite, pull the plastic clip off the bottom of the float swich and flip the float over. That will reverse it.
True means use the low ATO port, false means use the high ATO port. Simple as that.
DmnYnkee wrote:Also, should I break the other parts I am wanting to do into separate forum threads, so as to works through 1 topic at a time?
Chris
That would probably be easier to follow. :D
You would want to set the ATO timeout for 180 seconds (3 minutes). You can then set an alert in the portal for the timeout flag (as above). It will send out an e-mail alert and then repeat it every hour. The initial alert is not sent instantly, but fairly quickly IIRC.
There's no good way to detect a failed relay. RA can only read what the status is supposed to be, not what it actually is.
+1. The timeout is fairly reliable and will shut off the port. You'll have to manually clear the alert from one of the apps or from the screen.
DmnYnkee
Post by DmnYnkee »
I will cross #1 & #2 off my list.
I had to just add the extra code and not replace, otherwise, pump ran 180 seconds and then went into ATO alert status.
I did have to reverse my float for this to work. Based on my testing and results, True = "LowATO" and False = "HighATO" for anyone that might find this useful.
Here is the final code for that portion.
    ReefAngel.Relay.On(Port8);                //  Run ATO pump.
    ReefAngel.Relay.Off(Port8);               //  Sump level acceptable.
    ReefAngel.SingleATO(false,Port8,180,0);    //  Sump switch.  If ATO runs for 180 seconds, then shut off and send alert.
Now, is there any way to reverse the red and green indicator for HighATO in the portal? I would like HighATO inactive to show green.
Chris
I don't think I understand what you're trying to do here.
SingleATO will monitor the switch and turn the pump on and off. If it runs more than 3 minutes then it will trip the ATO flag and stop the pump until it is reset.
In fact, it appears that the SingleATO will override your if/then/else statement.
DmnYnkee
Post by DmnYnkee »
Using
buy itself, once the pump turned on, it would continue running for 3 minutes and then trip the ATO flag, no matter what position the float was in.
If pump runs over 180 seconds, I want the if/else statement to be over ridden. My ATO typically only runs 20-30 seconds every couple of hours. From bottom of float to top of float takes 150 seconds, so it should never run 180 seconds unless something needs attention.
Side note, I believe I am very close to having #4 working. Currently testing for the next couple of days.
What is the built in offset between the daylights and actinics? 90 minutes?
    ReefAngel.DayLights( Port2 );     // ATI DayLights (White+Purple)
    ReefAngel.ActinicLights( Port3 ); // ATI Actinic+ Lights (Blues)
Thanks much.
You can reverse the indicator light for high ato, but you'll also have to reverse the behavior of your if/else to match.
I believe the function is ReefAngel.ReverseHighATO(); to activate that feature. Keep in mind this can't be commented out and it can be anywhere in the code. It does not matter where.
I believe you have the wifi module. You can go to internal memory in the portal and under the first tab for standard lights it should show you the actinic offset and the timing based on what's set in memory.
DmnYnkee
Post by DmnYnkee »
ReefAngel.ReverseHighATO(); This did not work. Received the following error.
L1:174: error: 'class ReefAngelClass' has no member named 'ReverseHighATO'
I am using sunrise & sunset programming to run the lighting schedule, so would that still show in the internal memory in the portal? I have concluded there is an hour offset, but it does not appear to be inline with portal. Right now, actinics are coming on with sunrise, and off at sunset. If I change the offset in portal, it uses daylights as the fixed value and only adjusts the time for actinics. I'd like to have the actinics stay as they are (fixed by sunrise and sunset), and use a 90-120 minute offset for the daylights, if possible (come on later, and turn off earlier).
Here is my updated complete code.
nclude <ReefAngel_Features.h>
#include <SunLocation.h>
#include <Tide.h>
#include <Moon.h>
#include <WiFiAlert.h>
  SunLocation sl;
  int avgph[10];
    byte avgindex=0;
      byte x;
      byte y = 2;
      char text[7];
      if (HeatOn)
      if (FanOn)
      if (LowpH)
      if (HighpH)
      ReefAngel.LCD.DrawLargeText(COLOR_DARKSLATEBLUE,DefaultBGColor, 6, 3, " Thunder Reef",Font8x8);   // Put a banner at the top
      x = 6;
      x = 2;
      x = 2;
      x += 6;
  x += 6;
    sl.Init(35.5022, 97.7492); // In decimal numbers (i.e. -18.285833, 147.699722)
    sl.SetOffset(7,0,7,0); // rise_hour, rise_seconds, set_hour, set_seconds
    ReefAngel.DayLights( Port2 );             // ATI DayLights (White+Purple)  On 1 hr after sunrise, off 1 hr before sunset.
    ReefAngel.ActinicLights( Port3 );         // ATI Actinic+ Lights (Blues).   On at sunrise, off at sunset.
    ReefAngel.MoonLights( Port4 );            // Refugium light.  On 1 hr before sunset, off 1 hr after sunrise.
 ReefAngel.PWM.SetDaylight( ShortPulseMode(0,69,680,true) ); // Short pulse at 71% with 680ms pulse on sync mode
 ReefAngel.PWM.SetActinic( ShortPulseMode(0,69,680,false) ); // Short pulse at 71% with 680ms pulse on Anti-sync mode
 ReefAngel.PWM.SetDaylight( ShortPulseMode(0,73,680,true) ); // Short pulse at 78% with 680ms pulse on sync mode
 ReefAngel.PWM.SetActinic( ShortPulseMode(0,73,680,false) ); // Short pulse at 78% with 680ms pulse on Anti-sync mode
 ReefAngel.PWM.SetDaylight( ShortPulseMode(0,78,690,true) ); // Short pulse at 87% with 680ms pulse on sync mode
 ReefAngel.PWM.SetActinic( ShortPulseMode(0,78,690,false) ); // Short pulse at 87% with 680ms pulse on Anti-sync mode
 ReefAngel.PWM.SetDaylight( ReefCrestMode(40,10,true) ); // reefcrest at 40% +/- 10% on sync mode  (night Mode)
    // handle updating sunrise and sunset values
    sl.CheckAndUpdate();
Sorry, the reverse code should be ReefAngel.ReverseATOHigh();
As far as the actinics you are using internal memory based on the code you provided.
sl.CheckAndUpdate(); should be updating internal memory with the times for sunrise and sunset, but it also takes into account the actinic offset that is currently set. The problem is that if you change the offset, it doesn't take into account until the next time it updates at midnight or if you reboot.
DmnYnkee
Post by DmnYnkee »
So if I change offset in portal to 90, or 120, once it updates, it should be what I am looking for? Still keeping actinics as the constant (based on sunrise/sunset), and pushing back the daylights?
I am using local lat/long for testing, and the offset in the code is 7, which I believe is GMT +6 (for us central time zone) then +1 daylight saving time. Am I correct on this?
I'm not sure the timezone offset thing is wierd because of the way the arduino works. If you change the actinic offset and reset the controller you should see the daylight time shift to accommodate the changed actinic offset.
I think i can add a patch so if the offset changes, the time change can reflect immediately.
DmnYnkee
Post by DmnYnkee »
No patch necessary. It updated over night, and worked as expected.
Will try the revised code to reverse ATO float later today. Thanks much for all you help.
I think all I am wanting to do now is add the automatic temp changes according to month. This chunk of code code is borrowed from hedricksms. I will tinker with it some more and see if I can figure it out.
 void SeasonalTemps ()
  ReefAngel.CustomVar[0]=month();
  static int heatArray[][2] = { {792,796},// default in case of error in month=0 (June)
                    {770,774},//January (winter)
                    {774,778},//February (winter)
                    {775,779},//March (early spring)
                    {779,783},//April (spring)
                    {785,789},//May (spring)
                    {792,796},//June (early summer)
                    {799,803},//July (summer)
                    {806,810},//August (summer)
                    {796,801},//September (early fall)
                    {787,791},//October (fall)
                    {780,784},//November (fall)
                    {775,779} };//December (early winter)
  static int coolArray[][2] = { {794,799},// default in case of error in month=0 (June)
                    {772,776},//January (winter)
                    {776,780},//February (winter)
                    {777,781},//March (early spring)
                    {781,785},//April (spring)
                    {787,791},//May (spring)
                    {794,798},//June (early summer)
                    {801,805},//July (summer)
                    {808,812},//August (summer)
                    {798,803},//September (early fall)
                    {789,793},//October (fall)
                    {782,786},//November (fall)
                    {777,781} };//December (early winter)
  ReefAngel.StandardHeater( Heater,heatArray[month()][0],heatArray[month()][1]);
  ReefAngel.StandardFan(Cooling,coolArray[month()][0],coolArray[month()][1]);
 }//end seasonalTemps
You could post the error you're getting when you compile that will help immensely.
I'll still do the patch at some point because it annoys me :)
DmnYnkee
Post by DmnYnkee »
Trying with this code.
Getting the error:
L1.cpp: In function 'void SeasonalTemps()':
L1:325: error: 'Heater' was not declared in this scope
L1:326: error: 'Cooling' was not declared in this scope
#include <Tide.h>
#include <Moon.h>
  SunLocation sl;
  int avgph[10];
    byte avgindex=0;
      byte x;
      byte y = 2;
      char text[7];
      if (HeatOn)
      if (FanOn)
      if (LowpH)
      if (HighpH)
      x = 6;
      x = 2;
      x = 2;
      x += 6;
  x += 6;
    randomSeed(now()%SECS_PER_DAY);
      //Custom Variable [0] =  Month/Season
    // seasonal temperatures
    SeasonalTemps();
  static int coolArray[][2] = { {794,797},// default in case of error in month=0 (June)
                    {772,775},//January (winter)
                    {776,779},//February (winter)
                    {777,780},//March (early spring)
                    {781,784},//April (spring)
                    {787,790},//May (spring)
                    {794,797},//June (early summer)
                    {801,804},//July (summer)
                    {808,811},//August (summer)
                    {798,802},//September (early fall)
                    {789,792},//October (fall)
                    {782,785},//November (fall)
                    {777,780} };//December (early winter)
See easy peazy... Heater and and Cooling were defined by the previous author as his ports for his heater and fan. Simply change those to be the ports you want to use or you can define them like this
#define Heater Port7
DmnYnkee
Post by DmnYnkee »
That was too easy, lol. I should have been able to figure that out. Thanks again!
No problem, sometimes the easy things are hardest to figure out. You've out together quite a few things so far! Quite impressive