Analog cable problem with Tunze pumps

Basic / Standard Reef Angel hardware
Post Reply
meadowsad
Posts: 53
Joined: Sat Jun 15, 2013 9:56 am

Analog cable problem with Tunze pumps

Post by meadowsad »

I ran in to a weird issue today after I unplugged everything and plugged it back in. Basically my Tunze pumps aren't working correctly with the Tunze cables plugged in. If I unplug the cable the pumps work fine. As soon as I plug them in they don't work as expected.

If I set the pump speed to 100 the pumps work. Anything under 100 and they pulse very quickly. At 50 or below the pumps don't run at all. I checked all the connectors for salt creep and they seem ok. I opened up the relay box to inspect the inside and everything looks fine. I used a multimeter on the cables and the voltage on the cable seems right and isn't pulsing, at least not that I could tell.

I ran the Reef Angel Wizard and uploaded generic code and it does the same thing. I also tried different pump modes and the same thing happens on all modes.

I am not sure what else I should be doing here. I find it odd that both pumps are doing the same exact thing Any help would be appreciated!
rimai
Posts: 12881
Joined: Fri Mar 18, 2011 6:47 pm

Re: Analog cable problem with Tunze pumps

Post by rimai »

Were they working before you unplugged everything?
Roberto.
meadowsad
Posts: 53
Joined: Sat Jun 15, 2013 9:56 am

Re: Analog cable problem with Tunze pumps

Post by meadowsad »

As far as I know. I can't say with 100% certainty but I am pretty sure they were working, I would have noticed the severe lack of flow.

When I unplugged everything I just zip tied some cables and rearranged them, I didn't change wall outlets or anything.
rimai
Posts: 12881
Joined: Fri Mar 18, 2011 6:47 pm

Re: Analog cable problem with Tunze pumps

Post by rimai »

Were they connected to the relay box or dimming module?
Roberto.
meadowsad
Posts: 53
Joined: Sat Jun 15, 2013 9:56 am

Re: Analog cable problem with Tunze pumps

Post by meadowsad »

They are connected to an analog Relay Box. Everything was put back exactly the way it was. Everything just happened to be unplugged for about 20-30 minutes.
rimai
Posts: 12881
Joined: Fri Mar 18, 2011 6:47 pm

Re: Analog cable problem with Tunze pumps

Post by rimai »

You are positive that it is an analog relay box, right?
It does look like PWM signal trying to control your pumps, which are expecting analog signal.
Roberto.
meadowsad
Posts: 53
Joined: Sat Jun 15, 2013 9:56 am

Re: Analog cable problem with Tunze pumps

Post by meadowsad »

I guess I'm not 100% sure. I assumed the app wouldn't work correctly to turn on/off the relays if I used the wrong box. Maybe I am just an idiot :lol: I will check this tonight when I get home.