After a very cursory look, I see you have the moon channels set to
byte MoonCh[]={0,0,0,0,1,1,0,0};
thus, channels 4 and 5 should be turning on at night... are these the channels coming on? Your intensity and flicker points all look OK- e.g. they add to <= 255 for each channel
and you have an "error" here...
boolean Wchannel[]={1,1,2,0,0,0,0,0};
I do not have any idea whats going to happen with a 2 in that array, its supposed to be filled with 0 or 1. Doubt this is the issue, but you need to edit that to either a 1 or a 0 as the program will probably just ignore the 2 and possibly neglect that channel for certain effects.
Please post a more complete description of what is and what is not working. Did the lights come on as they should have, did then dim for sunset and then at 23:18 you saw lights on, in which channels.
Without a little more information its going to be pretty hard to say why its not "working" as you expect.
abhi_123
Post by abhi_123 »
Hi Rufessor,
Nice to hear from you after long time. right now the local time here is 16:30 and lights are doing fine. will wait and see what will they it do at the time of sunset.
btw is my Latitudes and Longitudes values are fine?
rufessor
Post by rufessor »
Hi back at you Abhi-
Good to see you back at it! For those that do not know- Abhi was perhaps the first person (guinea pig) to attempt using this software- and did so well before it was really ready-
Last time you were trying this I was just finally getting the bugs out of the lat/lon and sun rise sunset time as I was treating the processor time a little bit wrong back then- its been a good while and things are much more tested and functional- I hope you find it to be enjoyable and to work well!
If you do have any issues please very carefully describe them with as much context as possible, let us know what parts seem to be working and then if you do have (or suspect you do) an issue, what exactly is not happening. Most people seem to be installing this and running with it long term with basically no issues, after perhaps a little help to get going- good luck.
rufessor
Post by rufessor »
Oh. I could not begin to tell you if you lat and lon values are ok... since I don't know where you live (or where you choose for your tank to "live"! Although I think I remember you saying it was somewhere in India! To be honest, go look at the long post I have in the tutorial section, I remember being very careful to describe the signs of the lat and lon when I wrote that because its easy to be wrong - and I admit to no longer having immediate recall of that information. But, if your lights came on at the right time you have it right... pretty hard to get the correct sunrise time using the wrong location on the globe!
Just remember, the way this calculation is done results in some error, as much perhaps as about 15-20 minutes (depending on the time of the year and your location). So you should NOT expect absolutely perfect correlation between your window and the tank lights, but it will be close and should accurately mimic seasonal variation.
abhi_123
Post by abhi_123 »
Hi,
Glad you remember me.
coming to the point i made the correction in the code as advised by you but now i can see my white channel i.e 0 and 1 are lighting up though before that only 1 was lighting and 0 was off.
don't know whats an issue and the problem though lights are dim to certain extent but not completely off which is what killing the beauty of this code.
abhi_123
Post by abhi_123 »
Hey you are right. I am from India & i live in kanpur and you can google it for my latitudes and longitudes & counter check with the values i have entered. I have some doubts with keeping negatives both the values for my tank. its 22:27 now & sun usually sets here around 18:30 during this period. so i think its too much late for light to still on.
jjdezek
Post by jjdezek »
do all lights stay on? in your code you have channel 2 offset by 600
abhi_123
Post by abhi_123 »
An Update.
The Lights comes up at approx sunrise time and channel 1 goes off at about sunset but channel 2 is still running though very dim.
Looks like there is some issue with the channel 2.
jjdezek
Post by jjdezek »
        int Choffset[]={
              0,0,0,0,600,-600,0,0,0,0,0,0,0,0,0,0};
        // NOW SET YOUR LATIDTUDE AND LONGITUDE COORDINATES as Degrees, Minutes, Seconds of Lat and Lon
If you look at this part of your code you have channel 2 offset by 600,-600 if you want them go on and off all at the same time set it to 0,0 and it should go off with the rest.
rufessor
Post by rufessor »
Unsure currently... measure the voltage on that channel
compared to the others. It really should be off. your offset is 600 seconds, so within 10 minutes of the set time both channels should be off and neither are set to be moon. There is not much chance the code is wrong here, way too many people using it- no one has ever reported this type of error. Seriously, just check the output voltage between the common ground on the dimming module and channel 1 and 2 wires. They should be the same. If they are and one lights off and the others on- well.... thats something you need to figure out. If they are different (do this well after sunset) then I will have to really look at your code. I assume you have the code posted here and not an old version... if not. Start there first and grab most recent code.
abhi_123
Post by abhi_123 »
Hi,
first of all a silly mistake of mine. the channel 1 is what is still lighting up & not the 2. Now i measure the voltage and it is zero on channel 0 and 0.7 on channel 1. the channel which is set for moon is at 3.3.
i switched of the power and again turn them on again now both 0 and 1 is lighting at same intensity. Don't know whats wrong i am doing. :(
rufessor
Post by rufessor »
I am confused as well.
Can you tell us the answers to these questions-
Does channel 2 rise and set correctly?
Does channel 1 "rise" with ch2?
- I.E. does it gain intensity during the day and peak around noon then getting dimmer throughout the day until it "sets" with this odd 0.7V low intensity light.
Does channel 1 EVER go dark?
Do the moon lights work correctly?
Have you double checked to ensure that you have these things plugged into the correct output channels on the dimming module, I know when I wired this up I had them all backwards the first time...
Reason I ask is its really hard to see how there is a code issue here. IF channel 2 rises and sets correctly then the calculation for rise and set are working. There is almost nothing else to trouble shoot- the only difference between the calculations for Ch1 and Ch2 light intensity and sunset is due to the CHoffset array. So- if your CHoffset array is correct (and it looks like it is) then I don't honestly know what to say. I can look at your code but unless you have introduced an error (and this is very hard to see by just looking) its hard to say how it would be code based. Everyone else using this would have the same issue- but no one does.
That said, I will look but please answer the questions as it will help narrow down, and seriously- double check that your wired up correctly. I had my ch 1 plugged into ch 6 out etc etc for a few days. The manual has a diagram of how the output wire channels are numbered with respect to the PWM channel-
rufessor
Post by rufessor »
Looked at code you posted-
Only thing I see thats odd is that you have a new line splitting your declaration of the Choffset array- in most cases you can split C type code into as many lines or as few as you like (but I am not absolutely certain if there is an exception for cases like this with an array designation)- so with that in mind..... I would make that the line look like this. It avoids any possible confusion or inadvertent inclusion of hidden control characters etc on a copy and paste as well as brings your code to the same lay out std as what everyone else is using.
int Choffset[]={0,0,0,0,600,-600,0,0,0,0,0,0,0,0,0,0};
Other than that, I again am left with the idea that this is not code based- in that if you have in fact a faithful copy of whats posted here and that everyone else is using, this is not an error that exists there. I will wait until you have a chance to answer the above post questions and correct this line (just to be safe, leave no spaces in the array designation and be sure your using numbers and not a capital letter "o" which again, does not appear to be the case here.
jjdezek
Post by jjdezek »
Might help if he post current code since he changed the things you originally mentioned. Maybe something he changed is incorrect.
rufessor
Post by rufessor »
I agree- Possibility exists that something is odd and was introduced/deleted.
I am sorry this is being such a pain for you, but its not terribly complicated, if you can look through the questions and see if in fact you can get a zero voltage output on that channel under any condition that would help a lot. Its just very very odd-
Don't give up, what I just thought of is that I could easily edit your code to shut off that channel... and if its still on then you have an issue with the driver not coming down to zero output with a zero PWM input signal. This seems to me to be the most likely cause at this point - because no one else has experienced this issue. Let me know what you want to do. Shutting off the channel is TRIVIAL...
in fact... just edit this line to look like the next..
for (byte a=0;a<6;a++){//using all prior mods to light intensity (Insolation-->Cloud-->Storm) lets make some light
      if (a==1){
          analogWrite(PMWports[a],0);
This will eliminate channel 1 from EVER having any intensity output on the PWM channel output. If it still lights up...
There is a problem with your hardware and how its dealing with the PWM input signal and scaling that to output current based upon the input voltage.
I would do this FIRST- It answers the question. If you have any light on ch1 with this in the code you need to leave it this way and play with your driver until it is dark under these conditions then remove that small if loop and at that point you should be good to go... if instead you get a dark channel 1- with only this mod, then we need to figure out what the heck is going on in the version of the code your operating from. Or indeed, if you are experiencing some unusual circumstance that is revealing a otherwise hidden issue.
It would be very nice to see you try this, it will directly put to rest any concerns here about what happening and further will provide a nice trouble shooting record should anyone else experience this.
dlplunkett44
Post by dlplunkett44 »
I am having trouble installing this on my new PWM expansion module. From what I understand this is installed on the PWM module, not on the main unit. I have taken the PWM module out of its case and there is nowhere to insert the USB cable that came with the main unit. The only way for me to connect it to my computer is with the mini USB cable that came with the PWM expansion module. When I do this, I get an error in Windows 7 that the USB Device not recognized. When I go to load the code, only COM1 shows up. I try it anyway with Reef Angel controller w/ optiboot selected, and I get the following error:
Using Port : \\.\COM1
Using Programmer : arduino
Overriding Baud Rate : 115200
avrdude: Send: 0 [30] [20]
avrdude: Recv:
avrdude: stk500_getsync(): not in sync: resp=0x64
avrdude done. Thank you.
Please help!
Sorry...
There was a change in hardware where the new dimming modules are not going to allow this anymore.
They are not smart modules any longer.
dlplunkett44
So I can't use this code? I want to have clouds/lightning effects. What would be the best way to do this now?
The dimming module is being reworked to allow for better and easier compatibility and in the process, it was found best to use a dedicated chip for the dimming signal instead of a mcu like the previous hardware was using.
This code would have to be ported to be used in the head unit itself.
rufessor
Post by rufessor »
Based upon what Roberto just said-
Porting to the head unit is not probably overly difficult. The code has no special "code" that would only work on the Dimming module, it is however relatively large and would be unlikely to fit on anything other than the RA+. I had spent a little time trying to create an object library that would bring this code into the distribution. I admit to being slightly over matched in my coding skills as I have no OO C++ experience and limited OO Perl experience... so I got it split into what seemed to be rational segments, and then decided I was unsure what/how exactly to take this split up code and do something with it so that it could get packaged into the libraries.
At this point, given my availability and ability I would be happy to work with a more experienced person to see this through but am uncertain I can do this on my own without dedicating way too much time to a C++ learning curve when the only place I use this language is for RA.
If someone is willing to help (and I honestly do not think its going to take much) finish this, we should talk.
If this occurs, it will simply be part of the distribution and could be enabled by adding a few lines of code and includes.
rufessor
Post by rufessor »
Lnevo? Any time or interest?
dlplunkett44
Ok, so I'm trying to port this into my code, and when compiling, its giving me this error:
Globals\Globals.cpp.o: In function `MoonPhase()':
C:\Users\DaveElise\Documents\Arduino\libraries\Globals/Globals.cpp:116: multiple definition of `MoonPhase()'
Small_Reef.cpp.o:C:\Users\DAVEEL~1\AppData\Local\Temp\build4725006818650472374.tmp/Small_Reef.cpp:746: first defined here
Here is my code:
#include <avr/wdt.h>
#include <stdlib.h>
#include <math.h>
//***********************************ARRAYS YOU MUST MODIFY TO MAKE YOUR TANK SET UP WORK*****************************
//YOU MUST READ EVERY WORD IN THIS SECTION IN ORDER TO APPROPRIATELY CONFIGURE THIS PROGERAM- READ EVERY LINE BELOW///
byte ChMax[]={200,220,200,220,225,0,0,0};//Incremental value (Max-flicker) above flicker you want as max intensity (!!!!!!! Light Set Point is ChMax PLUS Flicker !!!!!!)
byte flicker[]={31,31,31,31,40,0,0,0};//need to input actual values here for flicker point on all channels in PWM expansion box
boolean Wchannel[]={1,0,1,0,0,0,0,0}; //use 1 to designate white channel (i.e. off during storm and used for lightning).  Array corresponds to PWM channel 0-5 in order
//Array to give direction to dimming.  e.g. DimOrder[]={0,0,1,1,0,0} (cloud chase effects, just group channels you want to dim together during a cloud or storm
//(which is zero or 1 will change who dims first).  set them all to 0 if your tank has no left/right or front/back lights.
byte DimOrder[]={0,0,1,1,1,0,0,0};
//set all channel positions that you would like to use for the lightning strike effect to 1 (0-5 are PWM channels 6,7 are Main PWM outs)- and channels with a 0 are not used in strike
byte StrikeChannel[]={1,1,1,1,1,0,0,0};
byte MoonCh[]={0,0,0,0,1,0,0,0};//place a 1 in the array position of all lighting channels you would like to use a moon lighting (this does not preclude their use in other phases (day, storm etc)
//**********************************DONE CHANGING THINGS HERE BUT YOU MUST CHANGE ChOffset array IN CalcSUN function******
// arc-seconds per radian
#define _sec_rad 206264.806247096370813
// axial tilt of earth at epoch, in radians
#define _tilt 0.409092804222329
// tropical year in seconds... rounding error accumulates to 26 seconds by the year 2136
#define _tropical_year 31556925
// 'zenith' of rising (setting) sun in radians (360 - 2 * 90.833 degrees)
#define _zenith 3.11250383272322
//Unless your planning on editing the program DO NOT CHANGE ANYTHING HERE
long latitude, longitude;
byte TrueIntensity[8];//array used to place hold final write values for PWM intensity setting
long elapsedTime;//used multiple places as elapsed since midnight
long newDay;
unsigned long rise;//time in seconds from the year 2000 (GMT) for sunrise
unsigned long set;//time in seconds from the year 2000 (GMT) for sunrise
long CloudMaster[20];// Set up array to hold start and end times for clouds for the day-
long midDay;// exactly 1/2 way between rise and set, i.e. solar noon for latitudes <60 close enough for us...
byte PWMports[] ={
    3,5,6,9,10,11};
byte ChannelValue[8];// Array to store output of insolaiton which may be modified and stored in TrueIntensity which is used to write to the PWM channels
byte cmdnum=255;
byte datanum=255;
byte dow=0;//day of week
boolean InsolationAdvance;//when true we recalculate light intensity during clear sky (every 3 seconds seems more than often enough)
//END HEADER/Global Variable declaration//
    ReefAngel.FeedingModePorts = Port4Bit | Port5Bit | Port6Bit;
    ReefAngel.WaterChangePorts = Port1Bit | Port3Bit | Port4Bit | Port5Bit | Port6Bit;
    ReefAngel.OverheatShutoffPorts = Port3Bit | Port7Bit;
    ReefAngel.Relay.On( Port2 );
    ReefAngel.Relay.On( Port4 );
   Serial.begin(57600);
    Wire.begin(8);
    pinMode(3,OUTPUT);
    pinMode(5,OUTPUT);
    pinMode(6,OUTPUT);
    pinMode(9,OUTPUT);
    pinMode(10,OUTPUT);
    pinMode(11,OUTPUT);
    wdt_enable(WDTO_1S);
    unsigned long seed=0, count=32;
    while (--count){
      seed = (seed<<1) | (analogRead(5)&1);
      randomSeed(seed);//start random generator at a different point each time (not perfect but whatever its gonna be pretty damn random)
    setSyncProvider(RTC.get);   // the function to get the time from the RTC
    setSyncInterval(SECS_PER_HOUR);  // Changed to sync every hour.
//Standard PWM Functions Receive/Process
    wdt_reset();
    if (howMany==5){
        cmd1=Wire.read();
        cmd2=Wire.read();
        cmd3=Wire.read();
        cmd4=Wire.read();
        cmd5=Wire.read();
            cmdnum=cmd4;
            datanum=cmd5;
            //Serial.println(cmd4,DEC);
            //Serial.println(cmd5,DEC);
    else{
        for (int a=0;a<howMany;a++){
            Wire.read();
    wdt_reset();
//End Standard Functions
//Start of sunrise, sunset and cloud calculations- runs on reset and once a day thereafter.
void CalSun(){
        //*********************YOU NEED TO CHANGE THESE VALUES Read instructions in their ENTIRETY and CAREFULLY change to values for your tank and geographical region***************************
        int Choffset[]={
            -600,0,-1800,6000,0,600,-1200,6600,-2200,6600,0,0,0,0,0,0};
        //If Your NORTH of the equator your LONGITUDE must START with a NEGATIVE number (the rest are positive) e.g. All of North America, Europe, Russia etc are negative
        //If Your EAST of the Prime Meridian your LATITUDE must START with a NEGATIVE number (the rest are positive), e.g. Most of Europe, All of China, India, Austraila, Russia etc are negative
       latitude=dmsToSeconds(40,44,00);//United States of America- Salt Lake City, local time is -7 hours GMT
       longitude=dmsToSeconds(-111,47,00);
        //**********************ok now were done changing things IF YOU CHANGED the Top part of the GLOBAL variable decleration AND this... your FULLY configured and ready to load********************************************
    if (dow==0){//if the controller has resarted we need to find midnight
      long hours, minutes;//store current elapsed local hours as total seconds from midnight
      time_t t=now();//store current clock time to parse
      hours=hour(t);
      hours=(hours*3600);//current hour number 0-23 as seconds
      minutes=minute(t);
      minutes=(minutes*60);//minutes of current hour as seconds
      newDay=now();
      newDay-=(hours+minutes);//Convert current local unix epoch time to local unix epoch time of midnight
    else if (dow!=0){//if we did not restart but the day is new then it is midnight and were good to go..
      newDay=now();
    //#define SECS_YR_2000 (946684800) the time at the start of y2k (need to subtract from unix epoch time to bring to Y2K origin
    newDay-=946684800;//convert GMT unix Epoch to seconds elasped since 2000 for GMT midnight of today
    rise=newDay;//set value to send to SunRise as midnight GMT in seconds from Y2K
    set=newDay;//
    //Calculate rise time and set time using Epherma Library functions (see end of code)
    SunRise(&rise);//call to Epherma function
    SunSet(&set);//Call to Epherma functionunsigned long newDay;
   /*Serial.print("rise and set=  ");
   Serial.println(rise);
   Serial.println(set);
   Serial.print("newDay as seconds since 2000 to todays midnight=  ");
   Serial.println(newDay);*/
    rise=(rise-newDay);// set to elapsed seconds of day
    set=(set-newDay);
   /*Serial.print("rise and set as elapsed seconds of day=  ");
   Serial.println(set);*/
    newDay+=946684800;//Convert newDay back to unix epoch GMT midnight today (used in loop to determine how far we are into the day)
   /*Serial.print("newDay as seconds since since 1970 to todays midnight=  ");
   Serial.print("elapsed is");
   long elapsed=now()-newDay;
   Serial.println(elapsed);*/
        midDay=(((set-rise)/2)+rise);
            if (b%2==0){
                ChRiseSet[b]=rise+(Choffset[b]);
                ChSlope[b]=(deltaY/(float)(HalfDayLength-(Choffset[b])));
            else if (b%2==1){
                ChRiseSet[b]=set+(Choffset[b]);
                ChSlope[b]=(deltaY/(float)(HalfDayLength+(Choffset[b])));
        byte RainMaker=random(1,101);
        if (RainMaker<=CloudChance){
            return;
        long dayLength=0;
        for (byte a=1;a<16;a=(a+2)){//determine maximum day length given light on tank that is not moon light, this will yield night clouds and storms (and a storm after dark is severe... always
          if (a==0){
            if (((set+Choffset[a])-rise)>(set-rise)){
              dayLength=((set+Choffset[a])-rise);
            else dayLength=(set-rise);
          else if (a!=0){
            if (dayLength<((set+Choffset[a])-rise)){
        byte CloudsMax=10;//DONT INCREASE BEYOND 10 or it will DIE, or increase array size to handle it (among other things)
        byte CloudsMin=4;//use 2 as a minimum
        Overcast=(Overcast/100);
        // split the total lenght of time for clouds into equal segments and then to randomly chop or add time to the
        //segments such that cloud length is variable.  Then distribute into random parts of the day and fill array with start,duration pairs for clouds
        int CloudLength;
        float CloudFraction=0;
        float SunFraction=0;
        for (byte a=0; a<20; a++){
          CloudMaster[a]=0;
          if (a%2==0){
            if (b==0){
              if (a==0){
              else if (a<((CloudsTotal*2)-2)){
                b++;
              else if (a==((CloudsTotal*2)-2)){
                SunFraction=(2-((float)CloudMaster[0]/(float)SunSegment));
            else if (b==1){
            if (c==0){
              c++;
            else if (c==1){
        for (byte a=0;a<20;a++){
      //reframe array to generate cloud start, cloud end, cloud start, cloud end
        else {
        /*Serial.println("here is cloud master in is entirety as start and end pairs");
          if (a%2==0){
            Serial.print("Start time=");
          else {
            Serial.print("End time=");
}//END SunCalc FUNCTION
void Insolation()
         use flicker points to adjust minimum intensity to stable light.  Turn off lights after set or before rise etc.
         if (elapsedTime<=midDay){
           byte c=0;//loop counter
            for (byte b=0;b<16;b=(b+2)){
                if (elapsedTime>=ChRiseSet[b]){
                    secSoFar=(elapsedTime-ChRiseSet[b]);//just account for length of every channel 1/2 day and switch at midDay
                    ChannelValue[c]=flicker[c]+ChMax[c]*(-cos(PiHalf+(ChSlope[b]*secSoFar)));
                   if (MoonCh[c]==1){
                      byte MoonToday=MoonPhase()*0.5;//SCALE FACTOR to DIM moon setting for use with HIGH power LED as moon light
                      if (MoonToday==0) ChannelValue[c]=0;
                      else if (MoonToday<flicker[c]) ChannelValue[c]=flicker[c];
                      else ChannelValue[c]=MoonToday;
                   else if (MoonCh[c]==0){
                     ChannelValue[c]=0;//its dark and this is not a moon phase channel
              c++;//index by one so we count 0-7 as b goes 0-14 by twos
        else if (elapsedTime>midDay){
            for (byte b=1;b<16;b=b+2){
                    ChannelValue[c]=flicker[c]+ChMax[c]*(-cos(Pi+(ChSlope[b]*secSoFar)));
                   if (MoonCh[c]==1){
              c++;//index to count 0-7 as b counts 1-15 by twos.
}//END function
//WEATHER FUNCTION BEGIN
void Weather ()
    static byte loopCount;
    static float PriorCloudCover;  //used to "delay" one side of the tank from the other in cloud passing effects
    static long StormStart;
    static long StormEnd;
    static long CloudEnd;
    static byte Severity;
    static int StepSize;
    static int LastStepSize;
    if (Cloud==false){
      //Write Insolation values to TrueIntensity so the loop will pick them up and the cloud/storm will get the right data (since intensity changes during the day)
      for (byte a=0; a<8; a++){//this must be above the next loop
             //Serial.print("We started a cloud and its end is=");
             //Serial.println(CloudEnd);
             CloudCover=CloudStart(CloudMaster[a]);//CloudStart modifies TrueIntensity to get us to 50% intensity at the start of the cloud effect and also sets cloud=true to bypass this
             Counter=0;
             loopCount=1;
             LastStepSize=0;//zero out cloud random walk variables
             StepSize=0;//zero out cloud ranodm walk variables
             return;//exit having started a cloud in CLoudStart routine called above
            return;
        if (elapsedTime>=CloudEnd){
            return;
        /*Use fractional intensity to set minimum value for any channel.  Dimming is proportional to actual intensity output
         and constrained by flicker point.  Random walk uses static variable "CloudCover" constrained to 0-100 to represent fractional intensity (i.e. (1-(CloudCover/100))*Insolation SetPoint
        if (loopCount==1){
          PriorCloudCover=CloudCover; //e.g. PriorCloudCover=CloudCover with no float math to screw things up
          LastStepSize=StepSize;
          StepSize=(random(5,21));// in Percent% (0-100) This is how much light intensity will change over the loop count interval (this actual time is dependent upon the call frequency of StromAdvance as set in the loop)
          if ((random(0,2)!=1)) StepSize=-(StepSize);
          if ((CloudCover+StepSize)>=100){//cannot shut off lights more than 100% so limit here
            StepSize=(100-CloudCover);//
            Counter++;
          else if ((CloudCover+StepSize)<=0){//cannot be brighter than 100% so since were in a cloud dont "limit" it but reflect it back down
            if (Counter>=50) Counter-=random(-1,2);//since we got bright... lets further delay and randomize storm occurence
          CloudCover=CloudCover+StepSize;
        if ((Counter>=60) && ((CloudEnd-elapsedTime)>=300)) {//if Counter (indexes when cloud cover reaches 100) has accumulated and we still have time lets make a storm
           if (StormCount>=1){//if we can have storms in this cloud (random- statisticly 1/3 clouds = no storm, 1/3 = 1 possible storm, 1/3 = 2 possible storms)
             byte RandomStorm;
             RandomStorm=random(0,11);//this randomizes for longer clouds without storm, avg cloud is much longer prior to storm occuring- thus short clouds will not generally have a storm
               if (RandomStorm>=4){
                 StormCount-=1;//count down by 1 the number of storms in this cloud- this will not roll the byte since the loop requires it to be at least 1 to ever subtract here.
                 Counter=0;//reset this variable since Storm loop uses it as well.
                 Severity=StartStorm(LongestStorm, IsStorm, StormEnd);
                 loopCount=1;//reset counting loop for the storm
        else if ((Counter>=60) && ((CloudEnd-elapsedTime)<300)){
           Counter=0;//just reset the counter (does not really matter in this case but its clean)
        for (int a=0;a<8;a++){
            if (ChannelValue[a]==0) TrueIntensity[a]=0;// if were in an evening storm dont reset intensity (it would go to flicker point and possibly flicker)
            else if (DimOrder[a]==0){
                TrueIntensity[a]=(flicker[a]+(((float)(ChannelValue[a]-flicker[a]))*(1-((CloudCover-(StepSize-(StepSize/4)*loopCount))/100))));
            else if (DimOrder[a]==1){
                TrueIntensity[a]=(flicker[a]+(((float)(ChannelValue[a]-flicker[a]))*(1-((PriorCloudCover-(LastStepSize-(LastStepSize/4)*loopCount))/100))));
         loopCount++;
         if (loopCount>4) loopCount=1;
           return;
            IsStorm=false;
            Counter=0;
            return;
        if (loopCount==1){
            Counter++;
            if (Counter>=2) Counter-=random(0,2);//since we got bright... lets further delay and randomize strike occurence
          if (Counter>(Severity+2)) Counter=0;//allow if to accumulate on ocassion to train strike sequences 2-3 in a row but then dump it
        if ((Counter>=(Severity+random(-1,4))) && (StrikeNow==false)) {//this is where a storm is triggered.  Counter indexes when cloud cover reaches 100 on the random walk
          byte RandomStriker;
          RandomStriker=random(1,11);
          if (RandomStriker>4){
                if (a>=(StrikeNumber*2)){
                    StrikeMaster[a]=0;
                if (a%2==0){
                   if (a==0){
                      StrikeMaster[a]=random(300,1601);//no need for random here but I am leaving it since I wrote it that way.  This must be independent from a=2,4,6 etc...
                    else {
                       StrikeMaster[a]=(StrikeMaster[(a-2)]+random(200,1401));//position 0,2,4,6,8.. is strike delay
                 else if(a%2!=0){
                    StrikeMaster[a]=random(50,110);//position 1,3,5,7,9... is strike duration (I tried real lightning strike durations and its too short this is adjusted for visual effect
            StrikeCount=0;
          Counter=0;
        if (Severity>5){
          for (int a=0;a<8;a++) {
              else if (Wchannel[a]==1){//if were in a storm but not a severe storm constrain whites to 50% of Insolation intensity
                      TrueIntensity[a]=(flicker[a]+((((float)(ChannelValue[a]-flicker[a])/4))*(1-((CloudCover-(StepSize-(StepSize/3)*loopCount))/100))));
                      TrueIntensity[a]=(flicker[a]+((((float)(ChannelValue[a]-flicker[a])/4))*(1-((PriorCloudCover-(LastStepSize-(LastStepSize/3)*loopCount))/100))));
                      TrueIntensity[a]=(flicker[a]+(((float)((ChannelValue[a]-flicker[a])))*(1-((CloudCover-(StepSize-(StepSize/3)*loopCount))/100))));
                      TrueIntensity[a]=(flicker[a]+((((float)(ChannelValue[a]-flicker[a])))*(1-((PriorCloudCover-(LastStepSize-(LastStepSize/3)*loopCount))/100))));
        else if (Severity<=5){// severe storms occur throughout the day, but EVERY storm after sunset is severe...
              else if (Wchannel[a]==1){//if were white we need to be off in a storm
                TrueIntensity[a]=0;
              else if (ChannelValue[a]==0){//if this light channel is dark... e.g. after sunset for this channel- it produces no cloud effect
                  TrueIntensity[a]=0;
              else if (Wchannel[a]==0){//if were not shut off in a strom and not after our daylight period (this channel) then we produce storm light sequences.
                  if (DimOrder[a]==0){//if we dim first... do it
                  else if (DimOrder[a]==1){//else we dim second
              }//end of CWHchannel==0 being true
           }//end of for loop in severity <5 == true loop
        }//end severity compairson loop no more else statements
        loopCount++;
        if (loopCount>3) loopCount=1;
    }//end of storm if loop
}//End Weather function
//CloudStart drops light intensity to 50% of whatever daylight setting is to start the cloud at 50
int CloudStart(long StartTime){
    byte elapsed;
    elapsed=(elapsedTime-StartTime);//counts up since we start this at elapsedTime=StartTime and StartTime is fixed
      TrueIntensity[a]=(flicker[a]+(((float)((ChannelValue[a]-flicker[a])))*(1-(elapsed*2.5)/100)));
    if (elapsed>=20);
      Cloud=true;//start the cloud
    return 50;//set CloudCover to 50
}//end CloudStart function
//StartStorm sets up duration and severity of storm. Its currently limited to 90-600 sec in length- it will rarely be lower than 3 minutes
byte StartStorm(int MaxLength, boolean& trigger, long& EndTime){
      byte LightningIntensity;
      int StormDuration;
      MaxLength-=120;//remove 2 mins from longest storm so that we end up with 2 minutes of cloud after the storm before the sky clears to daylight
      if (MaxLength>720){
         MaxLength=720;//modify local variable
         StormDuration=random((MaxLength/3),(MaxLength+1));
         EndTime=(elapsedTime+StormDuration);//Set by reference StormEnd static variable in weather
      else {
         StormDuration=random((MaxLength/2),(MaxLength+1));
      if (elapsedTime<midDay){
         LightningIntensity=random(3,11);//morning storms are generally less severe
      else if (elapsedTime>midDay){//afternoon storms are more likely to be severe (every 10-15 sec or less) to about once in a minute or maybe less
         if (elapsedTime>(set-rise)){//Storms after sunset are always severe... it just looks too cool!
           LightningIntensity=3;
         else {
         LightningIntensity=random(3,8);
      trigger=true;
      return (LightningIntensity);
//End Storm Start Function
//Similar to Cloud start but in reverse... now ramp intensity from wherever we were at the end of the cloud to the value set by Insolation
void ClearSky(int CloudPercent, long TerminationTime)
    byte elapsed=(elapsedTime-TerminationTime);//Counts up from the scheduled end of the cloud in seconds
    float slope=(CloudPercent/30);//Just calculate how much to increment every second to go from CloudCover to clear sky (CloudCover of zero)
    float LightAdvance;
    LightAdvance=(CloudPercent-(slope*elapsed));//were reducing CloudCover from start to zero over 10 seconds.
    TrueIntensity[a]=(flicker[a]+(((float)(ChannelValue[a]-flicker[a]))*(1-(LightAdvance/100))));
    if (elapsed>=30){//at this point lights are back to full Insolation setting so cancel the cloud and start waiting for the next one
        Cloud=false;//stop the cloud we are now outside of a true condition in the if loop so it will now stay false and lights are back on
        IsStorm=false;//just to be redundant this is not called from a storm...
}//End Clear Sky function
byte MoonPhase()
   int m,d,y;
   int yy,mm;
   long K1,K2,K3,J,V;
   byte PWMvalue;
   m = month();
   d = day();
   y = year();
   yy = y-((12-m)/10);
   mm = m+9;
   if (mm>=12) mm -= 12;
   K1 = 365.25*(yy+4712);
   K2 = 30.6*mm+.5;
   J = K1+K2+d+59-K3;
   V -= int(V/100)*100;
   V = abs(V-50);
   PWMvalue = 4*abs(50-V);  // 5.12=100%    4=~80%
   //pinMode(lowATOPin,OUTPUT);
   //return (PWMvalue*100)/255; //output is 0-100
   return PWMvalue;//output is 0-255
//  A big thank you for these library functions.  Its great!
//convert degrees to seconds of arc
// decimal degrees
long ddToSeconds(float dd){
   return dd * 3600.0;
//Degrees, minutes, seconds
long dmsToSeconds(int d, unsigned char m, unsigned char s){
long ret;
   ret = labs((long)d);
   ret = ret * 3600L + 60L * m + s;
   ret = (d<0L) ? -ret : ret;
   return ret;
   'Equation of Time'
   We use the 'short form equation, which has a theoretical accuracy of about 40 seconds.
   The returned value is in seconds.
int equation_of_time(unsigned long dt){
double t;
   dt -= 192540UL; // refer to Jan 3 2000 05:29 (first periapsis)
   dt %= _tropical_year;
   t = dt;
   t /= _tropical_year;
   t *= 6.283185307179586;
   t = -459.27672 * sin(t) + 575.333472 * sin(2.0 * t + 3.588414);
   return t;
   'Solar Noon' adjusts the passed time stamp to the time (GMT) of local solar noon.
   The accuracy is about 40 seconds (set by the equation of time).
void SolarNoon(unsigned long * dt){
long r;
   // Set stamp to noon GMT
   *dt /= 86400UL;
   *dt *= 86400UL;
   *dt += 43200UL;
   // adjust for equation of time, at noon GMT
   *dt -= equation_of_time(*dt);
   // rotate to our longitude
   r = longitude / 15L;
   *dt -= r;
   'Solar Declination'
   Returns declination in radians
   Accurate to within 50 arc-seconds
double SolarDeclination(unsigned long dt){
double y;
   y = dt;
   y /= _tropical_year; // fractional year
   y *= 6.283185307179586;
   y=0.006918-0.399912*cos(y)+0.070257*sin(y)-0.006758*cos(y*2)+0.000907*sin(y*2)-0.002697*cos(y*3)+0.00148*sin(y*3);
   return y;
   Return the period between sunrise and sunset, in seconds.
   At high latitudes around the time of the solstices, this could be zero, or all day.
unsigned long daylightseconds(unsigned long dt){
float l, d, e;
long n;
   d = -SolarDeclination(dt); // will be positive in Northern winter
   l = latitude / _sec_rad; // latitude in radians
   e += 60.0 * l * tan(l + d); // latitudinal error
   d = tan(l) * tan(d); //
   if(d>1.0) return 86400UL;
   if(d < -1.0) return 0UL;
   d = acos(d);
   d /= _zenith;
   n = 86400UL * d;
   n += e;
   return n;
   Modify the passed time stamp to the time of sunrise (or sunset if 'set' is non-zero).
   Returns 0 to signal 'normal' completion. If the position is in a polar circle, 1 will be
   returned if the sun is above the horizon all day, and -1 if the sun is below the horizon
   all day.
char SunRiseSet(unsigned long * dt, char set){
unsigned long daylen;
   daylen = daylightseconds(*dt);
   if(daylen == 86400UL) return 1;   // there is no 'night' today (midnight sun)
   if(daylen == 0UL) return -1; // there is no 'day' today
   *dt /= 86400UL;
   *dt *= 86400UL;
   *dt += 43200UL; // set the time stamp to 12:00:00 GMT
   *dt -= daylen / 2; //        sunrise at the prime meridian
   if(set) *dt += daylen; //     sunset at the prime meridian
   //*dt -= longitude / 15.0; // rotate to our own meridian
   return 0;
// 'short' forms of SunRiseSet
char SunRise(unsigned long* when){
    return SunRiseSet(when, 0);
char SunSet(unsigned long* when){
    return SunRiseSet(when, 1);
    ReefAngel.StandardHeater( Port3,820,825 );
    ReefAngel.StandardLights( Port7,21,0,7,0 );
    ReefAngel.SingleATO( true,Port1,90,0 );
    ReefAngel.WavemakerRandom(Port5,15,45);
    ReefAngel.WavemakerRandom1(Port6,15,45);
static unsigned long feeding = 0;
if ((now()%SECS_PER_DAY==28800) || (now()%SECS_PER_DAY==50400) || (now()%SECS_PER_DAY==72000)) //if it is 8am or 2pm or 8 pm
ReefAngel.FeedingModeStart(); //START FEEDING MODE
 if ( feeding == 0 )
 feeding = now(); //set the time of the start of feeding to variable feeding
 if ((now()-feeding>=60) && (now()-feeding<=61)) //if between 60 and 61 seconds has past
 ReefAngel.Relay.On(Port8); //TURN FEEDER RELAY ON
 ReefAngel.Relay.Off(Port8); //TURN FEEDER RELAY OFF
} else {
if ( feeding > 0 ) {
feeding = 0;
    elapsedTime=(now()-newDay);//Elapsed time is seconds from midnight of today- local processor time.
    wdt_reset();
    if (cmdnum!=255){
        ProcessCMD(cmdnum,datanum);
        cmdnum=255;
        datanum=255;
    if (dow!=day()){ //used to see that were in a new day and need to recalculate sunrise and sunset
      CalSun();
      dow=day();
    if ((millis()-lastmillis)>=100){
        counter+=1;
        StormAdvance=true;
        if (counter==0){
          InsolationAdvance=true;//so that it runs on start up to provide light immediately
        if (counter%30==0){
        if (counter==210) counter=0;
   if (InsolationAdvance==true) Insolation();//calculate clear sky solar intensity as the day advances
   Weather();//run the weather overlay (cloud, storm)
    if (StrikeNow==true){
          byte intensity;
          intensity=random(180,256);// this little bit should generate a randomly bright flash variation between the series of flashes in StrikeMaster
              for (byte b=0; b<6; b++){
                  if (StrikeChannel[b]==1) analogWrite(PWMports[b],intensity);// set all strike channels to intensity of strike
          if (StrikeCount==(StrikeNumber-1)){
            StrikeNow=false;
            StrikeCount=0;
    ReefAngel.AddWifi();
    int x,y;
    // Parameters
    // pH Expansion
    ReefAngel.LCD.DrawText( COLOR_MEDIUMSEAGREEN,DefaultBGColor,15,66, "PHE:" );
    ReefAngel.LCD.DrawSingleMonitor( ReefAngel.Params.PHExp,COLOR_MEDIUMSEAGREEN,39,66, 100 );
    // Main Relay Box
    // Date and Time
dlplunkett44
nevermind, figured it out. Didn't need to have it in the pde as well.
dlplunkett44
After uploading this to my main unit, the screen just stays dark. What did I do wrong?
rufessor
Post by rufessor »
Its not written to run on the main....
It is doing things like hard coded write to PMW channels which will do nothing on the main since it does not have that...
I have made an effort and have said in the past that I am working on it- in working on it a bit it became obvious (after spending some hours trying) that I was not going to be able to easily get it ported to OO code and I stopped because even getting it set up to test it out was something I simply have not done before.
Since there appears to be an ongoing interest and implementation of this code, lets see if someone has time to help. If thats the case then everyone will benefit. I am happy to spend time with a more experienced person to basically work together using their skills in porting and my knowledge of how the code goes together to figure out where to split this up.
IF your knowledgable about the RA head unit and how its making calls to the dimming module to run the light intensities, I can show you pretty much where you need to edit to change the existing code so that it runs the PWM module. However, depending on which includes you have in your PDE code for the head, it may becomes somewhat complicated. Up to you... I am more interested in working with someone who can help pull this into the library distribution as this will solve the problem for everyone regardless of expertise.
No, I don't have the bandwidth at this time. I believe binder had offered to help with the OO aspect.
The SunLocation class has a lot of the SWFLTEK code in it and could probably be used as a reference. The link is in the first or second post on my INO page in my signature.
lnevo wrote:No, I don't have the bandwidth at this time. I believe binder had offered to help with the OO aspect.
yeah, I can help out with the OO part of code and getting it set up as an includable library for the controller.
I have not looked back at the current code yet. But if it's currently working in a state that you are happy with, I can start with that code and see what all i can put together making references to the sunlocation class as well.
So, if someone would either PM me the current code or point me to link for the current code and just summarize what it needs to do (sounds like just have it run off of the headunit ports or make calls to control the pwm expansion ports) and the possible things that need to be configured (duration, chance, etc), then I should be able to start hashing something out for people.
Sent from my Nexus 7
dlplunkett44
Binder, that would be awesome! I think the working code is on the first page. I would love to help with this but my coding is not up to par yet. It needs to be able to run off of the main controller and run the pwm expansion. The original code was meant to just run the pwm ports 0 - 5 of course, but it would be great to be able to control 2 or more pwm expansions. I don't believe this would require any more work, but I'm not sure....
rufessor
Post by rufessor »
Kurt-
I am sending you a PM-
dlplunkett44
Controlling more than 1 PMW dimming module is possible- but it means modifying a fair number of arrays in the code which is basically trivial. However, it also would require a beta tester to deal with trouble shooting the code. Since I wrote it with the idea that we could control only 1 dimming module, and since its working this way for now and will capture the vast majority of users- I am going to start here and PM back and forth with Kurt so he can package this up into a module. Once thats working, then its basically "Easy" to start thinking about how to do this and you, or anyone else could grab the code from the library and changes can be made locally to get it working. So long as nothing major changed in terms of how we get this packaged in (e.g. we only changed the number of addressable PMW ports) I do not see why that could not then be passed onto Kurt to basically replace the first run- single PWM module code in the library. But since I only have a single PMW module, and I do NOT have a RA+ its going to be hard for me to help test code beyond my equipment capabilities.
We will post here as we get code together thats worth testing, as I suspect that we will want a few guinea pigs to try this on the main before it gets actually put into the distribution= to avoid headaches with a bunch of people breaking stuff all at once and no one having working lights!
I got the PM. I will be reading through it over the next few days and start coming up with some ideas as to what all needs to be done.