PWM inversion
NanoTrevor
PWM inversion
Post by NanoTrevor »
hey curt, how hard would it be to invert the pwm values displayed on the main? since i have buckpucks they run backwards, 0% being on, 100% being off. roberto already swapped the code so i use standard 0-100 ramp but the display shows the inverse...if actinic lights are 80% on pde code, the display shows 20%. a fix would be nice, thanks in advance.
Re: PWM inversion
NanoTrevor wrote:hey curt, how hard would it be to invert the pwm values displayed on the main? since i have buckpucks they run backwards, 0% being on, 100% being off. roberto already swapped the code so i use standard 0-100 ramp but the display shows the inverse...if actinic lights are 80% on pde code, the display shows 20%. a fix would be nice, thanks in advance.
inverting the displayed values would be pretty simple to do. if you make the changes, remember that you did because every time you update the libraries you will have to change this back:
Inside ReefAngel_NokiaLCD.cpp, look for this function:
void ReefAngel_NokiaLCD::DrawMonitor(byte x, byte y, ParamsStruct Params, byte DaylightPWMValue, byte ActnicPWMValue)
#else  // defined DisplayLEDPWM && ! defined RemoveAllLights
void ReefAngel_NokiaLCD::DrawMonitor(byte x, byte y, ParamsStruct Params)
#endif  // defined DisplayLEDPWM && ! defined RemoveAllLights
    DrawText(T1TempColor,DefaultBGColor,x,y,"T1:");
    DrawSingleMonitor(Params.Temp1, T1TempColor, x+18, y,10);
    DrawText(T2TempColor,DefaultBGColor,x,y+10,"T2:");
    DrawSingleMonitor(Params.Temp2, T2TempColor, x+18, y+10,10);
    DrawText(T3TempColor,DefaultBGColor,x,y+20,"T3:");
    DrawSingleMonitor(Params.Temp3, T3TempColor, x+18, y+20,10);
    DrawText(PHColor,DefaultBGColor,x+60,y,"PH:");
    DrawSingleMonitor(Params.PH, PHColor, x+78, y,100);
    DrawText(DPColor,DefaultBGColor,x+60,y+10,"DP:");
    // Code should be     100 - DaylightPWMValue
    DrawSingleMonitor(DaylightPWMValue, DPColor, x+78, y+10,1); // Change this line
    DrawText(APColor,DefaultBGColor,x+60,y+20,"AP:");
    // Code should be     100 - ActinicPWMValue
    DrawSingleMonitor(ActnicPWMValue, APColor, x+78, y+20,1);  // Change this line
The lines are marked // Change this line. The changes are above the line. You will just need to subract the PWM values from 100 to get your inverted values.
NanoTrevor
Re: PWM inversion
thanks curt
NanoTrevor
Re: PWM inversion
hey curt, i added the 100-dp and 100-ap and still get the old inverted values...?
Re: PWM inversion
NanoTrevor wrote:hey curt, i added the 100-dp and 100-ap and still get the old inverted values...?
Are you using the CUSTOM_MAIN for the custom main screen?
Did you save the file after you made those changes?
Did you reupload the PDE to the controller?
I know some of those sound like silly questions, but I have to ask them to make sure. A lot of times the problem is a simple error that is overlooked.
NanoTrevor
Re: PWM inversion
1. No, probably the problem cause..
2. Yes
3. Yes
so the dumb question, how do i enable custom main
Re: PWM inversion
NanoTrevor wrote:1. No, probably the problem cause..
2. Yes
3. Yes
You don't have to have CUSTOM_MAIN enabled to get it to work. I was thinking you were which would make it not work.
I just tested the code on my end and it works great. Here's what I used:
    DrawSingleMonitor(100-DaylightPWMValue, DPColor, x+78, y+10,1);
    DrawSingleMonitor(100-ActnicPWMValue, APColor, x+78, y+20,1);
NanoTrevor
Re: PWM inversion
would the fact that roberto changed the code inside the pde loop to invert values there, would that affect things?
byte BuckPuckActinic=0;
byte BuckPuckDaylight=0;
    ReefAngel.FeedingModePorts = B00000001; //turns off return pump
    ReefAngel.WaterChangePorts = B10110001; //turns off return pump, heater, fan/chiller and ATO
    ReefAngel.OverheatShutoffPorts = B00100110; //turns off lights and heater
    ReefAngel.LightsOnPorts = B00001110; //turns on lights
    ReefAngel.Relay.On(Port1);
    ReefAngel.Relay.On(Port7);
    ReefAngel.Relay.On(Port4);
    BuckPuckActinic=PWMSlope(8,0,19,0,0,50,60,BuckPuckActinic); //actinic leds ramp up from 0% at 7:30am to 60% at 8:30am and ramp down from 6:00pm to 7:00pm back to 0%
    BuckPuckDaylight=PWMSlope(8,30,18,0,0,35,60,BuckPuckDaylight); //daylight leds ramp up from 0% at 8:30am to 50% at 9:30am and ramp down from 5:00pm to 6:0pm back to 0%
    ReefAngel.PWM.SetActinic(100-BuckPuckActinic); // invert value for buckpucks
    ReefAngel.PWM.SetDaylight(100-BuckPuckDaylight); // invert value for buckpucks
Re: PWM inversion
NanoTrevor wrote:would the fact that roberto changed the code inside the pde loop to invert values there, would that affect things?
Yes it would affect things. If he's inverting it already and we try to invert it again, we are just changing things back to normal. So you would not need the changes that I made at all. You would just leave the display code alone and use what he has done. That would be a lot simpler.
NanoTrevor
Re: PWM inversion
hey curt, the prob is though what he did works for the (7,30,18,00,0,50,60) but not the displayed values. meaning i can code 0-100 for the ramping but the display still shows the wrong inverted values, if it ramps to 70 the display reads 30.
thanks
Re: PWM inversion
If he inverts it to work properly with the code, then what we need to do is what I mentioned before with inverting it when we display it. I will test it tonight when I get home.
NanoTrevor
Re: PWM inversion
gracias
Re: PWM inversion
I just tested the code. I copied the code that Roberto posted about inverting the PWM values inside the PDE and watched it display the inverted values. I then applied my fix for the display and it worked perfectly. It showed 0% when it should be 100%.
Here's the code that I used: (it was the same as I posted before)
Make sure when you make the change you save the file before you compile and upload to the controller.
NanoTrevor
Re: PWM inversion
ill try again, thanks for testing it
no luck...sorry not sure what im missing...
#include "WProgram.h"
#include "Time.h"
#include "NokiaLCD.h"
#include <EEPROM.h>
// Define Software SPI Pin Signal
#define BL 2          // Digital 2 --> BL
#define CS 3          // Digital 3 --> #CS
#define CLK 4         // Digital 4 --> SCLK
#define SDA 5         // Digital 5 --> SDATA
#define RESET 6       // Digital 6 --> #RESET
#define actinicPWMPin       9
#define daylightPWMPin      10
// Phillips PCF8833 Command Set
#define NOP 0x00 	// nop
#define SWRESET  0x01 	// software reset
#define BSTROFF  0x02 	// booster voltage OFF
#define BSTRON   0x03 	// booster voltage ON
#define RDDIDIF  0x04 	// read display identification
#define RDDST    0x09 	// read display status
#define SLEEPIN  0x10 	// sleep in
#define SLEEPOUT 0x11 	// sleep out
#define PTLON    0x12 	// partial display mode
#define NORON    0x13 	// display normal mode
#define INVOFF   0x20 	// inversion OFF
#define INVON    0x21 	// inversion ON
#define DALO     0x22 	// all pixel OFF
#define DAL      0x23 	// all pixel ON
#define SETCON   0x25 	// write contrast
#define DISPOFF  0x28 	// display OFF
#define DISPON   0x29 	// display ON
#define CASET    0x2A 	// column address set
#define PASET    0x2B 	// page address set
#define RAMWR    0x2C 	// memory write
#define RGBSET   0x2D 	// colour set
#define PTLAR    0x30 	// partial area
#define VSCRDEF  0x33 	// vertical scrolling definition
#define TEOFF    0x34 	// test mode
#define TEON     0x35 	// test mode
#define MADCTL   0x36 	// memory access control
#define SEP      0x37 	// vertical scrolling start address
#define IDMOFF   0x38 	// idle mode OFF
#define IDMON    0x39 	// idle mode ON
#define COLMOD   0x3A 	// interface pixel format
#define SETVOP   0xB0 	// set Vop
#define BRS      0xB4 	// bottom row swap
#define TRS      0xB6 	// top row swap
#define DISCTR   0xB9 	// display control
//#define DAOR   0xBA 	// data order(DOR)
#define TCDFE    0xBD 	// enable/disable DF temperature compensation
#define TCVOPE   0xBF 	// enable/disable Vop temp comp
#define EC       0xC0 	// internal or external oscillator
#define SETMUL   0xC2 	// set multiplication factor
#define TCVOPAB  0xC3 	// set TCVOP slopes A and B
#define TCVOPCD  0xC4 	// set TCVOP slopes c and d
#define TCDF     0xC5 	// set divider frequency
#define DF8COLOR 0xC6 	// set divider frequency 8-color mode
#define SETBS    0xC7 	// set bias system
#define RDTEMP   0xC8 	// temperature read back
#define NLI      0xC9 	// n-line inversion
#define RDID1    0xDA 	// read ID1
#define RDID2    0xDB 	// read ID2
#define RDID3    0xDC 	// read ID3
//a few basic colors
#define RED			0xE0
#define GREEN			0x1C
#define BLUE			0x03
#define YELLOW			0xFC
#define MAGENTA			0xE3
#define CYAN			0x1F
#define BLACK			0x00
#define WHITE			0xFF
#define WaterTempColor      0xE0
#define LightsTempColor     0xCC
#define AmbientTempColor    0xAA
#define PHColor             0x34
#define DPColor             0x88
#define APColor             0x49
#define cbi(reg, bit) (reg&=~(1<<bit))
#define sbi(reg, bit) (reg|= (1<<bit))
#if defined(__AVR_ATmega2560__)
	#define BL0 cbi(PORTE,4);
	#define BL1 sbi(PORTE,4);
	#define CS0 cbi(PORTE,5);
	#define CS1 sbi(PORTE,5);
	#define CLK0 cbi(PORTG,5);
	#define CLK1 sbi(PORTG,5);
	#define SDA0 cbi(PORTE,3);
	#define SDA1 sbi(PORTE,3);
	#define RESET0 cbi(PORTH,3);
	#define RESET1 sbi(PORTH,3);
#else
	#define BL0 cbi(PORTD,BL);
	#define BL1 sbi(PORTD,BL);
	#define CS0 cbi(PORTD,CS);
	#define CS1 sbi(PORTD,CS);
	#define CLK0 cbi(PORTD,CLK);
	#define CLK1 sbi(PORTD,CLK);
	#define SDA0 cbi(PORTD,SDA);
	#define SDA1 sbi(PORTD,SDA);
	#define RESET0 cbi(PORTD,RESET);
	#define RESET1 sbi(PORTD,RESET);
#endif
byte const font[475] = {
0x00 , 0x00 , 0x00 , 0x00 , 0x00 ,
0x00 , 0x06 , 0x5F , 0x06 , 0x00 ,                      // !
0x07 , 0x03 , 0x00 , 0x07 , 0x03 ,                      // ,
0x24 , 0x7E , 0x24 , 0x7E , 0x24 ,                      // #
0x24 , 0x2B , 0x6A , 0x12 , 0x00 ,                      // $
0x63 , 0x13 , 0x08 , 0x64 , 0x63 ,                      // %
0x36 , 0x49 , 0x56 , 0x20 , 0x50 ,                      // &
0x00 , 0x07 , 0x03 , 0x00 , 0x00 ,                      // //
0x00 , 0x3E , 0x41 , 0x00 , 0x00 ,                      // (
0x00 , 0x41 , 0x3E , 0x00 , 0x00 ,                      // )
0x08 , 0x3E , 0x1C , 0x3E , 0x08 ,                      // *
0x08 , 0x08 , 0x3E , 0x08 , 0x08 ,                      // +
0x00 , 0xE0 , 0x60 , 0x00 , 0x00 ,                      // ,
0x08 , 0x08 , 0x08 , 0x08 , 0x08 ,                      // -
0x00 , 0x60 , 0x60 , 0x00 , 0x00 ,                      // .
0x20 , 0x10 , 0x08 , 0x04 , 0x02 ,                      // /
0x3E , 0x51 , 0x49 , 0x45 , 0x3E ,                      // 0
0x00 , 0x42 , 0x7F , 0x40 , 0x00 ,                      // 1
0x62 , 0x51 , 0x49 , 0x49 , 0x46 ,                      // 2
0x22 , 0x49 , 0x49 , 0x49 , 0x36 ,                      // 3
0x18 , 0x14 , 0x12 , 0x7F , 0x10 ,                      // 4
0x2F , 0x49 , 0x49 , 0x49 , 0x31 ,                      // 5
0x3C , 0x4A , 0x49 , 0x49 , 0x30 ,                      // 6
0x01 , 0x71 , 0x09 , 0x05 , 0x03 ,                      // 7
0x36 , 0x49 , 0x49 , 0x49 , 0x36 ,                      // 8
0x06 , 0x49 , 0x49 , 0x29 , 0x1E ,                      // 9
0x00 , 0x6C , 0x6C , 0x00 , 0x00 ,                      // :
0x00 , 0xEC , 0x6C , 0x00 , 0x00 ,                      // ;
0x08 , 0x14 , 0x22 , 0x41 , 0x00 ,                      // <
0x24 , 0x24 , 0x24 , 0x24 , 0x24 ,                      // =
0x00 , 0x41 , 0x22 , 0x14 , 0x08 ,                      // >
0x02 , 0x01 , 0x59 , 0x09 , 0x06 ,                      // ?
0x3E , 0x41 , 0x5D , 0x55 , 0x1E ,                      // @
0x7E , 0x09 , 0x09 , 0x09 , 0x7E ,                      // A
0x7F , 0x49 , 0x49 , 0x49 , 0x36 ,                      // B
0x3E , 0x41 , 0x41 , 0x41 , 0x22 ,                      // C
0x7F , 0x41 , 0x41 , 0x41 , 0x3E ,                      // D
0x7F , 0x49 , 0x49 , 0x49 , 0x41 ,                      // E
0x7F , 0x09 , 0x09 , 0x09 , 0x01 ,                      // F
0x3E , 0x41 , 0x49 , 0x49 , 0x7A ,                      // G
0x7F , 0x08 , 0x08 , 0x08 , 0x7F ,                      // H
0x00 , 0x41 , 0x7F , 0x41 , 0x00 ,                      // I
0x30 , 0x40 , 0x40 , 0x40 , 0x3F ,                      // J
0x7F , 0x08 , 0x14 , 0x22 , 0x41 ,                      // K
0x7F , 0x40 , 0x40 , 0x40 , 0x40 ,                      // L
0x7F , 0x02 , 0x04 , 0x02 , 0x7F ,                      // M
0x7F , 0x02 , 0x04 , 0x08 , 0x7F ,                      // N
0x3E , 0x41 , 0x41 , 0x41 , 0x3E ,                      // O
0x7F , 0x09 , 0x09 , 0x09 , 0x06 ,                      // P
0x3E , 0x41 , 0x51 , 0x21 , 0x5E ,                      // Q
0x7F , 0x09 , 0x09 , 0x19 , 0x66 ,                      // R
0x26 , 0x49 , 0x49 , 0x49 , 0x32 ,                      // S
0x01 , 0x01 , 0x7F , 0x01 , 0x01 ,                      // T
0x3F , 0x40 , 0x40 , 0x40 , 0x3F ,                      // U
0x1F , 0x20 , 0x40 , 0x20 , 0x1F ,                      // V
0x3F , 0x40 , 0x3C , 0x40 , 0x3F ,                      // W
0x63 , 0x14 , 0x08 , 0x14 , 0x63 ,                      // X
0x07 , 0x08 , 0x70 , 0x08 , 0x07 ,                      // Y
0x71 , 0x49 , 0x45 , 0x43 , 0x00 ,                      // Z
0x00 , 0x7F , 0x41 , 0x41 , 0x00 ,                      // [
0x02 , 0x04 , 0x08 , 0x10 , 0x20 ,                      // Back slash
0x00 , 0x41 , 0x41 , 0x7F , 0x00 ,                      // ]
0x04 , 0x02 , 0x01 , 0x02 , 0x04 ,                      // ^
0x80 , 0x80 , 0x80 , 0x80 , 0x80 ,                      // _
//0x00 , 0x03 , 0x07 , 0x00 , 0x00 ,                      // `
0x20 , 0x40 , 0x80 , 0x40 , 0x20 ,                      // `
0x20 , 0x54 , 0x54 , 0x54 , 0x78 ,                      // a
0x7F , 0x44 , 0x44 , 0x44 , 0x38 ,                      // b
0x38 , 0x44 , 0x44 , 0x44 , 0x28 ,                      // c
0x38 , 0x44 , 0x44 , 0x44 , 0x7F ,                      // d
0x38 , 0x54 , 0x54 , 0x54 , 0x18 ,                      // e
0x08 , 0x7E , 0x09 , 0x09 , 0x00 ,                      // f
0x18 , 0xA4 , 0xA4 , 0xA4 , 0x7C ,                      // g
0x7F , 0x04 , 0x04 , 0x78 , 0x00 ,                      // h
0x00 , 0x00 , 0x7D , 0x00 , 0x00 ,                      // i
0x40 , 0x80 , 0x84 , 0x7D , 0x00 ,                      // j
0x7F , 0x10 , 0x28 , 0x44 , 0x00 ,                      // k
0x00 , 0x00 , 0x7F , 0x40 , 0x00 ,                      // l
0x7C , 0x04 , 0x18 , 0x04 , 0x78 ,                      // m
0x7C , 0x04 , 0x04 , 0x78 , 0x00 ,                      // n
0x38 , 0x44 , 0x44 , 0x44 , 0x38 ,                      // o
0xFC , 0x44 , 0x44 , 0x44 , 0x38 ,                      // p
0x38 , 0x44 , 0x44 , 0x44 , 0xFC ,                      // q
0x44 , 0x78 , 0x44 , 0x04 , 0x08 ,                      // r
0x08 , 0x54 , 0x54 , 0x54 , 0x20 ,                      // s
0x04 , 0x3E , 0x44 , 0x24 , 0x00 ,                      // t
0x3C , 0x40 , 0x20 , 0x7C , 0x00 ,                      // u
0x1C , 0x20 , 0x40 , 0x20 , 0x1C ,                      // v
0x3C , 0x60 , 0x30 , 0x60 , 0x3C ,                      // w
0x6C , 0x10 , 0x10 , 0x6C , 0x00 ,                      // x
0x9C , 0xA0 , 0x60 , 0x3C , 0x00 ,                      // y
0x64 , 0x54 , 0x54 , 0x4C , 0x00 ,                      // z
//0x08 , 0x3E , 0x41 , 0x41 , 0x00 ,                      // {
0x33 , 0x66 , 0xCC , 0x66 , 0x33 ,                      // {
0x00 , 0x00 , 0x7F , 0x00 , 0x00 ,                      // |
//0x00 , 0x41 , 0x41 , 0x3E , 0x08 ,                      // }
0xCC , 0x66 , 0x33 , 0x66 , 0xCC ,                      // }
0x02 , 0x01 , 0x02 , 0x01 , 0x00                        // ~
NokiaLCD::NokiaLCD()
	pinMode(BL,OUTPUT);
	pinMode(CS,OUTPUT);
	pinMode(CLK,OUTPUT);
	pinMode(SDA,OUTPUT);
	pinMode(RESET,OUTPUT);
	digitalWrite(BL,HIGH);
	digitalWrite(CS,HIGH);
	digitalWrite(CLK,HIGH);
	digitalWrite(SDA,HIGH);
	digitalWrite(RESET,HIGH);
#else
  DDRD |= B01111100;   // Set SPI pins as output
  PORTD |= B01111000;  // Set SPI pins HIGH
#endif
void NokiaLCD::ShiftBits(byte b)
  byte Bit;
  for (Bit = 0; Bit < 8; Bit++)     // 8 Bit Write
    CLK0          // Standby SCLK
    if((b&0x80)>>7)
      SDA1
      SDA0
    CLK1          // Strobe signal bit
    b <<= 1;   // Next bit data
void NokiaLCD::SendData(byte data) {
  CLK0
  SDA1
  CLK1
  ShiftBits(data);
void NokiaLCD::SendCMD(byte data) {
  CLK0
  SDA0
  CLK1
  ShiftBits(data);
void NokiaLCD::SetBox(byte x1, byte y1, byte x2, byte y2)
  SendCMD(CASET);   // page start/end ram
  SendData(x1);     // for some reason starts at 2
  SendData(x2);
  SendCMD(PASET);   // column start/end ram
  SendData(y1);
  SendData(y2);
void NokiaLCD::Clear(byte color, byte x1, byte y1, byte x2, byte y2)
  uint16_t xmin, xmax, ymin, ymax;
  uint16_t i;
  unsigned int icolor;
  icolor = ~color;
  // best way to create a filled rectangle is to define a drawing box
  // and loop two pixels at a time
  // calculate the min and max for x and y directions
  xmin = (x1 <= x2) ? x1 : x2;
  xmax = (x1 > x2) ? x1 : x2;
  ymin = (y1 <= y2) ? y1 : y2;
  ymax = (y1 > y2) ? y1 : y2;
  // specify the controller drawing box according to those limits
  // Row address set (command 0x2B)
  SendCMD(CASET);
  SendData(xmin);
  SendData(xmax);
  // Column address set (command 0x2A)
  SendCMD(PASET);
  SendData(ymin);
  SendData(ymax);
  // WRITE MEMORY
  SendCMD(RAMWR);
  // loop on total number of pixels / 2
  for (i = 0; i < ((xmax - xmin + 1) * (ymax - ymin + 1)) ; i++)
    // use the color value to output three data bytes covering two pixels
    // For some reason, it has to send blue first then green and red
    //SendData((color << 4) | ((color & 0xF0) >> 4));
    //SendData(((color >> 4) & 0xF0) | (color & 0x0F));
    //SendData((color & 0xF0) | (color >> 8));
    SendData(icolor);
void NokiaLCD::Init()
  // Initial state
  CS1
  CS0
  // Hardware Reset LCD
  RESET0
  delay(100);
  RESET1
  delay(100);
  //Software Reset
  SendCMD(SWRESET);
  //Sleep Out
  SendCMD(SLEEPOUT);
  //Booster ON
  SendCMD(BSTRON);
  //Display On
  SendCMD(DISPON);
  //Normal display mode
  SendCMD(NORON);
  //Display inversion on
  SendCMD(INVON);
  //Data order
  //SendCMD(0xBA);
  SendCMD(SETCON);
  SendData(0x38);
  //Memory data access control
  SendCMD(MADCTL);
 //SendData(8|64);   //rgb + MirrorX
 //SendData(8|128);   //rgb + MirrorY
  SendData(0xc0);
  SendCMD(COLMOD);
  SendData(2);   //16-Bit per Pixel
  Clear(0xff,0,0,131,131);
void NokiaLCD::Sleep()
  SendCMD(DISPOFF);
  SendCMD(SLEEPIN);
  BacklightOff();
void NokiaLCD::Wake()
  BacklightOn();
  SendCMD(SLEEPOUT);
  SendCMD(DISPON);
void NokiaLCD::BacklightOn()
  BL1
void NokiaLCD::BacklightOff()
  BL0
void NokiaLCD::DrawTextLine(byte fcolor, byte bcolor,byte x, byte y,char c)
  unsigned int i;
  unsigned int ifcolor, ibcolor;
  ifcolor = ~fcolor;
  ibcolor = ~bcolor;
  SetBox(x,y,x,y+7);
  SendCMD(RAMWR);
  for(i=0;i<8;i++)
    if (1<<i & c)
      SendData(ifcolor);
      SendData(ibcolor);
void NokiaLCD::DrawText(byte fcolor, byte bcolor, byte x, byte y,char *text)
  byte c;
  byte t;
  unsigned int i;
  unsigned int j;
  while(*text != 0)
     t = *text;
     i = t - 32;
     i = i * 5;
     for(j = i; j < i+5; j++)
       c = font[j];
       DrawTextLine(fcolor, bcolor, x++, y, c);
     DrawTextLine(fcolor, bcolor, x++, y, 0);
     text++;
void NokiaLCD::DrawText(byte fcolor, byte bcolor, byte x, byte y,int text)
	char temp[6];
	itoa(text,temp,10);
	DrawText(fcolor, bcolor, x, y,temp);
void NokiaLCD::DrawText(byte fcolor, byte bcolor, byte x, byte y,byte text)
	char temp[6];
	itoa(text,temp,10);
void NokiaLCD::DrawText(byte fcolor, byte bcolor, byte x, byte y,long text)
	char temp[20];
	ltoa(text,temp,10);
void NokiaLCD::PutPixel(byte color, byte x, byte y)
  icolor = ~color;
  SendData(x);      // for some reason starts at 2
  SendData(x+1);
  SendData(y);
  SendData(y+1);
  SendCMD(RAMWR);
  SendData(icolor);
void NokiaLCD::SetContrast(byte Contrast)
  SendCMD(SETCON);
  SendData(Contrast);
void NokiaLCD::DrawDate(byte x, byte y)
  //byte iTimeHourOffset=0;
  char text[21];
  char temp[]="  ";
  strcpy(text,"");
  itoa(month(),temp,10);
  if (temp[1]==0) strcat(text,"0");
  strcat(text,temp);
  strcat(text,"/");
  itoa(day(),temp,10);
  strcat(text,temp);
  strcat(text,"/");
  itoa(year()-2000,temp,10);
  strcat(text,temp);
  strcat(text," ");
  //if (iTimeHour>12) iTimeHourOffset=12;
  itoa(hourFormat12(),temp,10);
  strcat(text,temp);
  strcat(text,":");
  itoa(minute(),temp,10);
  strcat(text,temp);
  strcat(text,":");
  itoa(second(),temp,10);
  strcat(text,temp);
  if (isAM())
  strcat(text," AM");
  strcat(text," PM");
  DrawText(RED,WHITE,x,y,text);
void NokiaLCD::DrawOutletBox(byte x, byte y,byte RelayData)
	Clear(94,x,y,x+104,y);
	Clear(94,x,y+12,x+104,y+12);
	for (int a=0;a<8;a++)
	  byte bcolor=WHITE;
	  byte fcolor=BLACK;
	  char temp[]="  ";
	  if ((RelayData&(1<<a))==1<<a)
		bcolor=13;
		fcolor=WHITE;
	  Clear(bcolor,x+1+(a*13),y+1,x+14+(a*13),y+11);
	  itoa(a+1,temp,10);
	  DrawText(fcolor,bcolor,x+5+(a*13),y+3,temp);
void NokiaLCD::DrawSingleMonitor(int Temp, byte fcolor, byte x, byte y, byte decimal)
  char text[7];
  char temptxt[3];
  if (Temp==0xFFFF) Temp=0;
  itoa(Temp/decimal,text,10);
  if (decimal>1)
	  itoa(Temp%decimal,temptxt,10);
	  strcat(text , ".");
	  if (Temp%decimal<10 && decimal==100) strcat(text , "0");
	  strcat(text , temptxt);
  Clear(WHITE,x,y,x+30,y+8);
  DrawText(fcolor,WHITE,x,y,text);
void NokiaLCD::DrawMonitor(byte x, byte y, ParamsStruct Params, byte DaylightPWMValue, byte ActnicPWMValue)
  DrawText(WaterTempColor,WHITE,x,y,"T1:");
  DrawSingleMonitor(Params.Temp1, WaterTempColor, x+18, y,10);
  DrawText(LightsTempColor,WHITE,x,y+10,"T2:");
  DrawSingleMonitor(Params.Temp2, LightsTempColor, x+18, y+10,10);
  DrawText(AmbientTempColor,WHITE,x,y+20,"T3:");
  DrawSingleMonitor(Params.Temp3, AmbientTempColor, x+18, y+20,10);
  DrawText(PHColor,WHITE,x+60,y,"PH:");
void NokiaLCD::DrawSingleGraph(byte color, byte x, byte y, int I2CAddr, int EEaddr)
	int start;
	for (int a=0;a<120;a++)
		start=EEaddr+a;
		if (start > (int(EEaddr/120)+1)*120) start=start-120;
		Wire.beginTransmission(I2CAddr);
		Wire.send((int)(start >> 8));   // MSB
		Wire.send((int)(start & 0xFF)); // LSB
		Wire.endTransmission();
		Wire.requestFrom(I2CAddr,1);
		if (Wire.available()) PutPixel(color,x+a,y+50-Wire.receive());
void NokiaLCD::DrawEEPromImage(int swidth, int sheight, byte x, byte y, int I2CAddr, int EEaddr)
  int count = 0;
  SetBox(x,y,swidth-1+x,sheight-1+y);
  SendCMD(0x2c);
  //for (int j = 0; j < sheight; j++)
  //  for (int i = 0; i < swidth; i++)
      //e.lcd_put_pixel(readEEPROM(I2CEEPROM,count+start),i+x,j+y);
  //    count++;
  //  WatchDogReset();
  do
    Wire.send((int)(EEaddr+count >> 8));   // MSB
    Wire.send((int)(EEaddr+count & 0xFF)); // LSB
    Wire.requestFrom(I2CAddr,30);
    for (int j = 0; j < 30; j++)
      count+=1;
      if ((count<swidth*sheight) && Wire.available()) SendData(~Wire.receive());
  while (count < swidth*sheight);
void NokiaLCD::DrawGraph(byte x, byte y, int I2CAddr, int pointer)
  Clear(WHITE,0,y,131,y+50);
  Clear(BLACK,x,y,x,y+50);
  for (int i=6; i<=131; i+=3){
    PutPixel(0x49, i, y+25);
  DrawSingleGraph(WaterTempColor,x,y,I2CAddr,EEPROM.read(pointer));
  DrawSingleGraph(LightsTempColor,x,y,I2CAddr,EEPROM.read(pointer)+120);
  DrawSingleGraph(AmbientTempColor,x,y,I2CAddr,EEPROM.read(pointer)+240);
  DrawSingleGraph(PHColor,x,y,I2CAddr,EEPROM.read(pointer)+360);
Re: PWM inversion
Are you using my development libraries? This is the Standard Libraries code. This is the NokiaLCD.cpp file and not the ReefAngel_NokiaLCD.cpp. If you are running the dev libraries and modify this code, then it won't work because this code isn't even used.
NanoTrevor
Re: PWM inversion
oh yup im using the dev lib...now what?
Re: PWM inversion
If you converted to dev lib, just go back in the thread and apply the changes to the file ReefAngel_Nokia.cpp :)
NanoTrevor
Re: PWM inversion
thanks roberto, ill try that. hey quick question, when i reload the pde the lights go full on, which at night can be a bit startling to the fish...anyway of stopping this?
Re: PWM inversion
That's because the pucks are inverted. 0V means full on. When the controller is being programmed, it outputs 0V.
The only way to avoid this is by hooking up the pucks where 0V means no light output.
NanoTrevor
Re: PWM inversion
oh ok, that wont happen, its working great and im gonna leave well enough alone. so since i was not observant and was trying to put the 100- changes into the wrong nokia library, no go. i just dropped the changes into the correct library and its working awesome, thanks roberto and curt.