Re: Reversing the ATO code
Posted: Sun Jun 05, 2011 6:06 pm
by astralmind
alexwbush wrote:Initially I tried to modify the ReefAngel.cpp code to work with single ATO the way I have it build (see picture above) and I couldn't get it to work correctly. Then I was told that the code is designed such that the code was built to have the float switches upside down.
I ended up coding the way I posted above and it's worked great. I don't need the timer since I have the second float switch to catch a problem and having the timer may hurt you if you're away from home and can't reset it without doing so at the source. The only thing that could go wrong with my setup/code is if your sump were leaking or your skimmer went crazy and wet skimmed (which mine did), but even then if can only fill as much as the ATO has, which for me is 5 gal. I left my setup for a week and just recently adjusted the skimmer (big mistake) and it ended up skimming almost 5 gal out which was replaced by RO water. It lowered the salinity significantly and I was a bit worried while I was away. A salinity probe would have let me know this while I was gone (hint, hint Roberto), but it seems everything survived.
Ha yes a salinity probe will surely be a welcomed addition!
So I saw your code for the highATO which is very straight forward but how did you take care of the primary switch (low ATO) ?
What did you mean by having to reset the timer ? hmmm so the default is set to operate for 60 seconds and then stop regardless of the switch state. Do that mean that it won't restart again on its own ever ? That must have been the purpose of the Interval function, act as some kind of a reset option?.
Posted: Sun Jun 05, 2011 6:32 pm
astralmind wrote:
Wait, I'm confused. What you are describing is how all ATO system I know of behave.
Main switch:
Triggers ATO pump when the water level goes low enough for the switch to close (ie, the ring part stops floating and touches the bottom making contact).
Secondary switch:
As a safety, if the other switch remains stuck in closed position, the high switch shutsdown the ATO if the water level reaches it (ie, the ring part starts floating, cutting contact).
All in all both switches behave identically, one is just a redundant safety.
I was under the impression that SingleATO took care of that as opposit to the standardATO function ? Esle, why would there be 2 functions that serve the exact same purpose?
That being said I just generated some code using singleATO (high and low) and it does appear to completely inversed.
Interval is how long it takes before the function can be activated again and timeout is the max amount of time the function will run regardless of the switch state correct ?
There seems to be some confusion about what is considered floating or not floating and what is considered active or not active. It's not just the people commenting here, it's just in general.
IsActive - Means the float is
not touching the end with both wires coming out of it. So when the code says "ato->IsActive()" that means that the float is not touching the end with the wires.
With this being said, here is the way the StandardATO function works (it may be listed above but I'm re-listing it because of the discussion).
- High switch mounted with wires at the bottom
- Low switch mounted with the wires at the top
- When water level lowers all the way to cause the low switch to be active (float is touching the opposite end with the 2 wires coming out of it), the ATO pump is turned on.
- The ATO pump runs until the water level raises the low switch up from making contact, continues to raise the water level until the high switch is active (float touching the opposite end of the 2 wires coming out of it). The ATO pump shuts off when the high switch is active OR if the ATO Timeout value is exceeded. The timeout prevents the pump from running too long in case the reservoir runs dry or something else happens.
- Water then evaporates out of the tank and lowers until the low switch is active.
- Repeat process
The SingleATO function works with an individual switch only. So there is no failsafe built in. The only failsafe is the timeout value.
- Switch mounted with 2 wires at bottom
- Water level with the float at the top is the starting point.
- When the water level drops, the float is no longer floating or active, so the ATO pump turns on.
- It pumps in water until the float is active (touching the top end which is opposite the 2 wires) OR until the timeout value has exceeded. Then the pump shuts off.
- The hour interval just means that the ATO pump can only be activated once every X (specified) hours. This is to prevent it from activating too many times. You don't have to specify this if you don't want to. You can safely put in 0 and the ATO pump will activate as often as it needs.
- Repeat process
That should help clarify the 2 scenarios or sets of functions.
Yes, you are correct. Interval is the max time that the function can be activated again. Just pass in 0 to disable this check (like I stated above). Timeout is the max time that the pump will run during the current activation before the pump is shutoff. If this value is exceeded, then you either a) set it too short b) the reservoir is dry or c) the pump has failed/died/whatever and the switches will not tell the pump to stop. You will most likely not be triggering the activation again until the problem is fixed.
If you want to use the single ato functions and use the high switch as a failsafe, then you will have to look at the previous post by alex about how he coded is failsafe high switch into his PDE file. Here is his code:
I tweaked it to be an else statement because if it's active you do one thing and otherwise you do something else. It just looks better and there are less logical checks.
if(ReefAngel.HighATO.IsActive())
ReefAngel.Relay.Off(Port1);
ReefAngel.Relay.Off(Box1_Port6);
ReefAngel.Relay.On(Port1);
ReefAngel.Relay.On(Box1_Port6);
This implies having the wires underwater (at the bottom).
Hope this helps.
Posted: Sun Jun 05, 2011 6:45 pm
by alexwbush
Thanks for simplifying my code curt. That makes sense. I'm a little rusty on my programming.
astralmind wrote:Ha yes a salinity probe will surely be a welcomed addition!
I have my switches wired in series and plugged into the highATO receptical. That frees up my lowATO which I use to control my skimmer. My skimmer skims into a 2.5 or 5 gal bucket (depending on if I am out of town or not) and the skimmer will turn off if it fills the container... all part of my future auto water change setup and to keep my skimmer from going too crazy (which it already has one or two times).
Posted: Sun Jun 05, 2011 8:06 pm
by astralmind
Thank you Curt for your detailed and very clear explanation aswell as Alex for your piece of code.
I will be using both low and high for now, with both switches in the upright position (wires upward). Whenever a switch floats, the port should be off since it means water as reached the proper level (low) or exceeded it and reached the second safety switch (high).
So in the end, if I get this right, this simple code in my PDE would do it:
if(ReefAngel.HighATO.IsActive() && ReefAngel.LowATO.IsActive())
I've just uploaded the code and it seems to work as intended. That being said (and it could be just me who's way too tired to look be looking at this
), it would mean that the IsActive state defines a switch that is not floating. With the above piece of code I could only get Port1 to turn on when both switches were hanging from their wires in an empty bin - exactly what I wanted.
Posted: Mon Jun 06, 2011 6:14 am
One comment I have is about the redundancy. If the bottom switch fails and never activates for whatever reason, then using the Low and High IsActive together will FAIL. That logic check will only be true when BOTH switches are active and if the low switch isn't working that will never happen. So you don't want your failsafe to use both switches, you want it to ONLY use your high switch.
It sounds like you want the water level to be at the low switch with the high one as a backup. So going back to your initial request, here would be some logic for you: (This will assume both switches are wired with their wires at the top)
void ATOFailSafe(byte port)
// Check for the low switch
If the Low switch is active, meaning the float is opposite the end with the two wires,
we are empty so we should turn on the pump. Otherwise, we are full, so turn off the port.
if ( ReefAngel.LowATO.IsActive() )
ReefAngel.LowATO.StartTopping();
ReefAngel.Relay.On(port);
ReefAngel.LowATO.StopTopping();
ReefAngel.Relay.Off(port);
if ( ReefAngel.LowATO.IsTopping() && ! ReefAngel.HighATO.IsActive() )
// We have a problem
The pump is running and topping but the low switch isn't shutting off the port.
We must shutoff the port ourself.
// Trigger some sort of alert, maybe an email or text message
We did not indicate that the port is not topping anymore, we could do that manually
OR we could not do it and replace the switch and have the controller do it for us.
It's completely up to the user.
At this point, it shouldn't matter because there is a problem with the switch and that
needs to be addressed.
You can just copy and paste this function into your PDE file. Then inside your loop function, you can call it like this:
// other functions
ATOFailSafe(Port1);
This should handle your failsafe redundancy.
NOTE: This code does not use the timeouts at all and it does not use the hour interval. You would use this function instead of using the SingleATO or StandardATO functions.
Edited to indicate proper functionality with both wires at the top (coming out of the water) which is the reverse of how the SingleATO function works. SingleATO was based off of the high switch mounting/positioning from the StandardATO function.
Posted: Mon Jun 06, 2011 7:06 am
by astralmind
Once again, thank you very much for all your time and patience Curt, appreciated. I'll be sure to try your code as soon as I get home.
If both switches are mounted with their wires upward, then that code will not work properly. IsActive state defines a switch that IS floating (touching the end with the wires). So in your code you listed, when BOTH floats are up (touching the ends with the wires), you are turning on your pump and shutting it off when they are down. You have the logic backwards. It should be:
This is were things get extremely odd. Your instructions were perfectly clear in that regard but unless there is an hardware issue here my setup is indeed working backward. The IsActive state (turn port on) gets triggered when the float switch
does not float (ie hangs at the bottom of the switch). If I have both switch in this position, the port is ON:
as soon as one of the switches starts to float (even lifted a tiny bit), the current is shut off. I tested this numerous time with a lamp and it worked as described (also properly reflected on the RA screen).
Are my float switches "inversed" or am I simply insane ?
Posted: Mon Jun 06, 2011 7:12 am
as soon as one of the switches starts to float, the current is shut off. I tested this numerous time with a lamp and it worked as described (also properly reflected on the RA screen).
No, you are not insane.
I was wrong.
I emphasized this because I will be the first to admit when I'm wrong. I don't deal with the ATO code much and it's confusing.
I wrote a PDE file to test the status for me and confirm how the IsActive function works. Here is the PDE that I wrote to test it (also attached to this post):
#include <ReefAngel_Wifi.h>
#include <ReefAngel_EEPROM.h>
#include <ReefAngel_ATO.h>
#include <ReefAngel_LED.h>
#include <ReefAngel_Relay.h>
#include <ReefAngel_PWM.h>
#include <ReefAngel_Timer.h>
#include <ReefAngel_Memory.h>
ReefAngel.LCD.DrawText(DefaultFGColor, DefaultBGColor, 10, 10, "ATO Status Screen");
ReefAngel.LCD.DrawText(DefaultFGColor, DefaultBGColor, 10, 40, "Low:");
ReefAngel.LCD.DrawText(DefaultFGColor, DefaultBGColor, 10, 60, "High:");
byte lowcolor;
char lowstatus[10];
byte highcolor;
char highstatus[10];
lowcolor = COLOR_GREEN;
strcpy(lowstatus, "ACTIVE");
lowcolor = COLOR_RED;
strcpy(lowstatus, "INACTIVE");
if ( ReefAngel.HighATO.IsActive() )
highcolor = COLOR_GREEN;
strcpy(highstatus, "ACTIVE");
highcolor = COLOR_RED;
strcpy(highstatus, "INACTIVE");
ReefAngel.LCD.Clear(DefaultBGColor, 60, 40, 110, 48);
ReefAngel.LCD.Clear(DefaultBGColor, 60, 60, 110, 68);
ReefAngel.LCD.DrawText(lowcolor, DefaultBGColor, 60, 40, lowstatus);
ReefAngel.LCD.DrawText(highcolor, DefaultBGColor, 60, 60, highstatus);
delay(200);
So, based on this, you are absolutely correct with your float switches. I will be going back through and editing my post to be correct so others won't be confused when they read it. Bear with me for the time being on that.
Posted: Mon Jun 06, 2011 7:28 am
by astralmind
No worries Curt, I'm just happy that I got my sanity back
So in the end, the code I had written will be ok and will let me use timeouts, correct ?
Posted: Mon Jun 06, 2011 7:42 am
astralmind wrote:No worries Curt, I'm just happy that I got my sanity back
It makes me lose my sanity too at times. hahaha
astralmind wrote:So in the end, the code I had written will be ok and will let me use timeouts, correct ?
The code you wrote would work but it wouldn't have a redundancy check like I mentioned a few posts ago. I have updated my code in the post to be correct now. It still does not have the timeouts.
So your code and my code does not incorporate the timeouts.
I'm honestly seriously considering changing the SingleATO function to have the float switches be mounted like the low switch in the StandardATO function (with the wires at the top). This would solve a lot of the confusion with everybody (myself included).
Posted: Mon Jun 06, 2011 7:59 am
by astralmind
Your code definitly makes sens to me however, I still don't understand why mine would not work as a failsafe considering that we now know for sure that the IsActive state is when the water level drops. Since I am using and "AND" argument, the port will not be triggered ON unless both switches are in a IsActive state.
If the low switch was defective (ie stuck in an isActive state, not rising up with the water level), the water level would eventually reach the High switch and trip it, making it float and breaking the if condition, stopping the top off.
The only potential issues I see with this is having either the High or low switch broken and stuck in a floating state, that would stop the ATO from ever kicking in. However this same issue would also happen with your code as far as I understand. With both piece of codes the risks are of "never topping off" VS overflowing which is probably less of an issue.
In the end I'm asking because the memory on the RA seems to be very limited and if we can save some bytes than, lets do it
Actually this is another concern all together but with my current extremely lite PDE (only WiFi and Temp checked in RAgen) and no addtionnal functions, I'm already pushing the limit.
Posted: Tue Jun 07, 2011 11:59 pm
by alexwbush
I've been saying these switches were coded backwards for a while, but I think people thought I was that crazy old man in the village
Posted: Wed Jun 08, 2011 12:24 pm
by astralmind
alexwbush wrote:I've been saying these switches were coded backwards for a while, but I think people thought I was that crazy old man in the village
make it 2 crazy old men in the village hehe
Having a great time learning about the code structure on this controller. I must say that the challenge is well worth the effort. I read through the Apex's 150 pages manual and found the "language" to be so restrictive and unclear at times.
Reef Angel sure rocks and the community behind it is a critical contributing factor.
Posted: Fri Oct 07, 2011 9:31 am
by chase
// other functions
ATOFailSafe(Port1);
Trying to get this working but I'm getting the following error when compiling:
(#define Refugium 8 is highlighted yellow)
default_ragen_pde_all_ato_test:42: error: expected ',' or '...' before numeric constant
default_ragen_pde_all_ato_test:45: error: expected initializer before 'void'
Here's my PDE:
// Autogenerated file by RAGen (v1.0.4.92), (09/08/2011 09:54)
// default_ragen_pde_all_ato_test.pde
#define DisplayImages
#define WavemakerSetup
#define DateTimeSetup
#define VersionMenu
#define DirectTempSensor
#define DisplayLEDPWM
#define StandardLightSetup
#define Daylight 1
#define ATO 2
//#define Chiller 2
#define Heater 3
#define Return 4
#define WavemakerL 5
#define WavemakerR 6
#define LED 7
#define Refugium 8
void ATOFailSafe(byte ATO) //changed port to ATO
ReefAngel.Relay.On(ATO);
ReefAngel.Relay.Off(ATO);
randomSeed(analogRead(0)); //wm stuff
ReefAngel.FeedingModePorts = B00001000;
ReefAngel.WaterChangePorts = B00000000;
ReefAngel.OverheatShutoffPorts = B00000101;
ReefAngel.LightsOnPorts = B00000001;
ReefAngel.Relay.On(Return); //port 4
//wm stuff
ReefAngel.Timer[1].SetInterval(random(15,35));
ReefAngel.Timer[1].Start();
ReefAngel.Relay.On(WavemakerL);
ReefAngel.StandardGUI(); //web connection
// ReefAngel.StandardFan(Chiller,775,783); Removed for ATO function
ReefAngel.StandardHeater(Heater,768,771);
ReefAngel.StandardLights(Daylight,9,0,19,30); //Daylight schedule 9:00am - 7:30pm
ReefAngel.StandardLights(Refugium,21,0,9,0); //Refugium schedule 9:00pm - 9:00am
ReefAngel.StandardLights(LED,8,30,22,0); //LED schedule 8:30am - 10:00pm
ATOFailSafe(ATO); //ATO Stuff
//Wavemaker stuff
ReefAngel.Timer[1].SetInterval(random(15,30));
ReefAngel.Relay.Toggle(WavemakerL); //port 5
ReefAngel.Relay.Toggle(WavemakerR); //port 6
/* Old ATO stuff
if(ReefAngel.LowATO.IsActive())
ReefAngel.Relay.On(ATO); //port 7
Thanks!!
Posted: Fri Oct 07, 2011 9:35 am
You can't use:
It's a reserved word for a the LED Class
Sorry.
Choose a different name
Posted: Fri Oct 07, 2011 10:03 am
by chase
rimai wrote:You can't use:
Sorry.
Hmm, changed LED to Moonlight and I still get the same error(s). It compiles without the ATO code binder suggested (including the define LED reference) which is what I've been running for a while now with no issues.
Posted: Fri Oct 07, 2011 10:09 am
Ahhh...
After closer look, I had to change some stuff around.
Try this:
// ATO_TEST.pde
#define VersionMenu
#define Daylight 1
#define AutoTopOff 2
//#define Chiller 2
#define Heater 3
#define Return 4
#define LED1 7
#define Refugium 8
//wm stuff
ReefAngel.StandardLights(LED1,8,30,22,0); //LED schedule 8:30am - 10:00pm
ATOFailSafe(AutoTopOff); //ATO Stuff
//Wavemaker stuff
/* Old ATO stuff
Posted: Fri Oct 07, 2011 10:14 am
by chase
Winner- TY much!! Gonna upload it now...
