Size of the variable.
byte is 8 bit variable
int is 16 bit and goes all the way up to double, which is 64bit variable.
Posted: Mon Mar 11, 2013 12:55 pm
by dazza1304
Ok, that makes sense. So why use double when the resolution even from the adc is only 12 bit, wouldn't integer be better to use?
Not picking just trying to understand the code better so I can be self sufficient - ish!
Posted: Mon Mar 11, 2013 1:11 pm
Anything that is not a whole number needs to be either float or double.
0.001925 - this is definitely not a whole number.
That's why we use 751 for temperature instead of 75.1.
751 fits in an integer, but 75.1 requires float.
Posted: Mon Mar 11, 2013 1:18 pm
by dazza1304
Cool- thanks, makes sense now!
Posted: Tue Mar 12, 2013 10:49 am
by dazza1304
Well, it works fine!!
I have some slightly corrected values for the compensation constants -
Celcius = 0.0022
Fahrenheit = 0.001165
I have attached a chart below showing results from uncompensated salinity reading and compensated readings over about 10 deg C.
I have changed my salinity ATO to use temp compensated salinity and expect to it work fine!!
I have also attached my code if anyone is interested!!
#include <Globals.h>
#include <RA_Wifi.h>
#include <Wire.h>
#include <OneWire.h>
#include <Time.h>
#include <DS1307RTC.h>
#include <InternalEEPROM.h>
#include <RA_NokiaLCD.h>
#include <RA_ATO.h>
#include <RA_Joystick.h>
#include <LED.h>
#include <RA_TempSensor.h>
#include <Relay.h>
#include <RA_PWM.h>
#include <Timer.h>
#include <Memory.h>
#include <RA_Colors.h>
#include <RA_CustomColors.h>
#include <Salinity.h>
#include <RF.h>
#include <IO.h>
#include <ORP.h>
#include <AI.h>
#include <PH.h>
#include <WaterLevel.h>
#include <ReefAngel.h>
////// Place global variable code below here
unsigned long lastLowSal=now();//salinity >35.1 timer
boolean SALduration=true;//salinity >35.1 for 2 minutes flag
boolean ATOEnabled=false;//enable ATO function for 5 seconds
boolean ATOPumping=true;//disable ATO function for 5 minutes
unsigned long ATOStart=now();//ATO 5 sec run timer
double SalCompensation;
////// Place global variable code above here
    InternalMemory.OverheatTemp_write( 260 );
    InternalMemory.SalTempComp_write( 255); // Change this to compensation temperature
    ReefAngel.Relay.On( Port4 );
    ReefAngel.Timer[1].SetInterval(1800); // 30 mins before reactivation of ATO
    ReefAngel.MHLights( Port3,0,30,23,30,5 );//skimmer off and on for dosing reef energy
    ReefAngel.StandardHeater( Port6,252,255 );
    ReefAngel.StandardFan( Port7,255,258 );
    ReefAngel.MHLights( Box1_Port5,23,30,23,31,0 );//air pump for mix reef energy prior to dosing
    ReefAngel.WaterLevelATO(Port2,180,38,40);// Salinty top up to keep water level correct
   if (ReefAngel.TempSensor.unit)
   SalCompensation=ReefAngel.Params.Salinity/(1+((ReefAngel.Params.Temp[T3_PROBE]-InternalMemory.SalTempComp_read())*0.0022));
   SalCompensation=ReefAngel.Params.Salinity/(1+((ReefAngel.Params.Temp[T3_PROBE]-InternalMemory.SalTempComp_read())*0.001165));
   SalCompensation=round(SalCompensation);
    ///// If salinity >35.1 for 120 sec set SALduration flag
    if (SalCompensation<351) lastLowSal=now();
    if (now()-lastLowSal>120) SALduration=false;
    if (SALduration && ATOPumping)//if salinity>35.1 for 2 minutes enable ATO
    {ATOStart=now();
    ATOEnabled=true;
    ATOPumping=false;
  if (now()-ATOStart<5)//ATO pump on time 5 seconds
    if (ATOEnabled) ReefAngel.Relay.On(Port1);
    ReefAngel.Timer[1].Start();//start 5 minute disable of ATO
    ReefAngel.Relay.Off(Port1);
    ATOEnabled=false;
  if (ReefAngel.Timer[1].IsTriggered())//after 30 minute disable, enable ATO
    ATOPumping=true;
    ATOStart=now();
    SALduration=true;
    ///// if skimmer cup full, turn off skimmer
    bitClear(ReefAngel.Relay.RelayMaskOff,2);
    else {
    bitSet(ReefAngel.Relay.RelayMaskOff,2);
    ReefAngel.Portal( "dazza1304" );
    int x,y;
    // Parameters
#if defined DisplayLEDPWM && ! defined RemoveAllLights
#else // defined DisplayLEDPWM && ! defined RemoveAllLights
#endif // defined DisplayLEDPWM && ! defined RemoveAllLights
    // Salinity
    ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,15,46, "SAL:" );
    ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,39,46, ReefAngel.Params.Salinity );
    ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,39,63, (int)SalCompensation );
    // ORP
    ReefAngel.LCD.DrawText( COLOR_PALEVIOLETRED,DefaultBGColor,75,46, "ORP:" );
    ReefAngel.LCD.DrawText( COLOR_PALEVIOLETRED,DefaultBGColor,99,46, ReefAngel.Params.ORP );
    // Water Level
    ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,75,63, "WL:" );
    ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,99,63, ReefAngel.WaterLevel.GetLevel() );
    // Main Relay Box
    TempRelay &= ReefAngel.Relay.RelayMaskOff;
    TempRelay |= ReefAngel.Relay.RelayMaskOn;
    ReefAngel.LCD.DrawOutletBox( 12, 79, TempRelay );
    // Relay Expansion
    TempRelay = ReefAngel.Relay.RelayDataE[0];
    TempRelay &= ReefAngel.Relay.RelayMaskOffE[0];
    TempRelay |= ReefAngel.Relay.RelayMaskOnE[0];
    ReefAngel.LCD.DrawOutletBox( 12, 98, TempRelay );
    // Date and Time
Posted: Tue Mar 12, 2013 10:52 am
Very cool!!!
I'll add this to the libraries :)
Posted: Tue Mar 12, 2013 11:32 am
Very cool!
Posted: Mon Mar 18, 2013 10:15 am
by dazza1304
SalCompensation is already a variable that you can display.
But, I think the best approach is to compensate the ADC value.
Try this:
// Apply Salinity Compensation
 SalCompensation=ReefAngel.Salinity.Read()/(1+((ReefAngel.Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.0022));
 SalCompensation=ReefAngel.Salinity.Read()//(1+((ReefAngel.Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.001925));
 ReefAngel.Params.Salinity=round(SalCompensation);
 ReefAngel.Params.Salinity=map(ReefAngel.Params.Salinity, 0, ReefAngel.SalMax, 60, 350); // apply the calibration to the sensor reading
Hi Roberto, I have a quick question for you.
Currently I have coded my controller to do the temp compensation for salinity, and currently display uncompensated salinity, compensated as per the above code, and compensated with the above code without the mapping.
Basically, it appears the mapping function makes no difference to the end value - is this what you would expect, as I am not sure quite how the map function works?
cheers..
Posted: Mon Mar 18, 2013 10:27 am
Is the SalCompensation already giving you ppt values?
If it is, there is something wrong with the calculation then.
SalCompensation was supposed to the compensated raw adc values, which would be converted to ppt with the map function. map function is simply a linear interpolation of raw adc values to ppt values.
Posted: Mon Mar 18, 2013 10:35 am
by dazza1304
No the salcompensation will display an ADC value as expected.
However, if I display salinity after this ReefAngel.Params.Salinity=round(SalCompensation);
and also after this ReefAngel.Params.Salinity=map(ReefAngel.Params.Salinity, 0, ReefAngel.SalMax, 60, 350);
Then, basically the values are the same - i.e . the mapping function does not appear to add anything?
Posted: Mon Mar 18, 2013 10:42 am
Oh, no.
You can't assign ReefAngel.Params.Salinity=something.
The next loop, the value is overwritten by the libraries own calculation and it is not compensated values.
However, you can display round(SalCompensation); and use this to convert the new compensated value:
SalCompensation=map(SalCompensation, 0, ReefAngel.SalMax, 60, 350);
This will convert it to ppt compensated values.
Posted: Mon Mar 18, 2013 10:49 am
by dazza1304
Below is the code I am using. Basically displaying salcompensation and salinity test (which uses the map function) and the map function does not seem to add anything i.e produces the same result as the displaying salcompensation?
#include <Wire.h>
#include <Time.h>
#include <RA_ATO.h>
#include <LED.h>
#include <Relay.h>
#include <RA_PWM.h>
#include <Timer.h>
#include <Memory.h>
#include <RF.h>
#include <IO.h>
#include <ORP.h>
#include <AI.h>
#include <PH.h>
double Salinitytest;
    //salinity temp compensation
   // Apply Salinity Compensation 2
   Salinitytest=ReefAngel.Salinity.Read()/(1+((ReefAngel.Params.Temp[T3_PROBE]-InternalMemory.SalTempComp_read())*0.0022));
   Salinitytest=ReefAngel.Salinity.Read()/(1+((ReefAngel.Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.001925));
   Salinitytest=round(Salinitytest);
   Salinitytest=map(Salinitytest, 0, ReefAngel.SalMax, 60, 350); // apply the calibration to the sensor reading
    {ATOStart=now();
    ATOEnabled=true;
    ATOPumping=false;
    ATOEnabled=false;
    ATOPumping=true;
    ATOStart=now();
    SALduration=true;
    else {
    int x,y;
    // Parameters
    // Salinity
    //temp comp salinity
    ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,15,63, "S/T:" );
    //map of adc temp comp salinity
    ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,15,54, "ADC:" );
    ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,39,54, (int)Salinitytest );
    // ORP
    // Water Level
    // Main Relay Box
    // Relay Expansion
    // Date and Time
Posted: Mon Mar 18, 2013 11:01 am
What are you seeing on SalCompensation and Salinitytest in the screen?
Posted: Mon Mar 18, 2013 11:03 am
by dazza1304
Temp Compensated salinity values, which are virtually identical.
Posted: Mon Mar 18, 2013 11:16 am
That's not supposed to be ppt values.... :(
It's supposed to be compensated adc values. Your formula may be converting it to ppt values and disregarding the calibration. The map function is what applies the calibration.
Posted: Mon Mar 18, 2013 11:53 am
by dazza1304
Ok, think I figured this out - I am actually using the reefangel.params.salinity to compensate, so of course will be in ppt.
And if I changed to reefangel.salinty.read, it would of course be the ADC value, then i would need the map function to convert to ppt - is this correct?
I guess I am confused as to where the salinity calibration (not temp compensation) happens - if I read the ADC value using reefangel.salinity.read, then this returns a raw uncalibrated ADC value? If I then convert to ppt using the map function, how does the salinty calibration happen?
Posted: Mon Mar 18, 2013 1:15 pm
dazza1304 wrote:Ok, think I figured this out - I am actually using the reefangel.params.salinity to compensate, so of course will be in ppt.
Correct. You should use the adc value to compensate.
dazza1304 wrote: And if I changed to reefangel.salinty.read, it would of course be the ADC value, then i would need the map function to convert to ppt - is this correct?
Yes.
dazza1304 wrote: I guess I am confused as to where the salinity calibration (not temp compensation) happens - if I read the ADC value using reefangel.salinity.read, then this returns a raw uncalibrated ADC value? If I then convert to ppt using the map function, how does the salinty calibration happen?
The calibration happens when you apply the map function. It does both at the same time. It will calibrate and convert to ppt.
Posted: Wed Mar 20, 2013 3:11 am
by dazza1304
OK, something is not happening as I would expect. When I use the code below, ReefAngel.Params.Salinty is definitely temperature compensated, but for some reason, it seems to knock my salinity ATO off. For example, my salinity is definitely over 351, but still the ATO wont trigger.
// Apply Salinity temp Compensation & salinity calibration
SalCompensation=ReefAngel.Salinity.Read()/(1+((ReefAngel.Params.Temp[T3_PROBE]-InternalMemory.SalTempComp_read())*0.0022));
SalCompensation=ReefAngel.Salinity.Read()/(1+((ReefAngel.Params.Temp[T3_PROBE]-InternalMemory.SalTempComp_read())*0.001165));
ReefAngel.Params.Salinity=map(ReefAngel.Params.Salinity, 0, ReefAngel.SalMax, 60, 350); // apply the calibration to the sensor reading//salinity temp compensation
// For displaying salinity without temp compensation
Salinitytest=ReefAngel.Salinity.Read();
if (ReefAngel.Params.Salinity<351) lastLowSal=now();
However, if I change the code around a bit and use the value SalCompensation for triggering the ATO as below, it works fine.
Salinitytest=SalCompensation;
What I don't undertand, is why the top bit of code doesnt work? I think it may have something to do with the map function, which I think should run only once, rather than be in the loop?
Any help would be appreciated!!
I can make do with things as they are, but as the portal only charts the ReefAngel.Params.Salinity parameter, I cannot get a graph of what my temp compensated salinity is which is the one I really want!!
Posted: Wed Mar 20, 2013 7:51 am
You won't. Not yet.
We need to merge this into the libraries.
The real ReefAngel.Params.Salinity is still uncompensated coming from the libraries.
Posted: Wed Mar 20, 2013 9:00 am
by dazza1304
So is there 2 ReefAngel.Params.Salinty??
When I ran the first bit of code the salinity display was def temp compensated - I proved this by holding the T3 probe, which caused the salinity value to change as you would expect when the salinity probe was in a constant salinity solution.
Posted: Wed Mar 20, 2013 9:05 am
It's the sequence of events that is tripping you.
The salinity ReefAngel.Params.Salinity value changes when the ShowInterface() function is called.
When you change the value on the DrawCustomMain() function, it is only temporarily. It gets overwritten by the libraries in the next loop.
So, you can change and display it within the DrawCustomMain(), but won't affect the controller, because it reads a new value again and overwrites whatever you placed in the variable.
Posted: Wed Mar 20, 2013 9:09 am
by dazza1304
Got it - I think - so what library do I need to modify to get this to work and what do I need to do to it, as I would like to see what my salinity graph looks like with temp compensation!! I realise if i change the library, it will be overwritten next update!!
Posted: Wed Mar 20, 2013 9:13 am
yes, it will get overwritten in the next update.
You need to change the ReefAngel.cpp in the mean time.
It starts on line 738:
https://github.com/reefangel/Libraries/ ... l.cpp#L738
Apply the compensation before the map() function is called.
Pretty sure you know what to do by looking at the code there.
Posted: Fri Apr 05, 2013 7:32 am
by ahmedess
So the only difference between the old temperature compensation code and this one is that the compensation is applied to the ADC values instead of the ppt values?
Posted: Fri Apr 05, 2013 8:46 am
Actually, there is a need to offset the temperature in which the calibration happened, or the compensated value would be wrong.
Posted: Wed Apr 10, 2013 12:51 pm
by ahmedess
I think its also better to define the constant Alpha in memory to make it easier to tune using wifi if needed cause I think it might differ a bit from a person to the other depending on the probe, salinity and Temperature. So adding it to memory would make it a lot easier than having to change the code and load several times until we get it right
Posted: Wed Apr 10, 2013 12:59 pm
Good suggestion. I've added a ticket.
https://github.com/reefangel/Libraries/issues/79
Posted: Mon Apr 22, 2013 4:15 pm
by ahmedess
I added the salinity compensation constant to the code in library below but manually changing the value of the constant in memory does not change anything in the value of salinity displayed on the screen. I m using Celsius temperature and i have set the salinity constant Alpha= 220. I changed it to several other values but no change
#if defined SALINITYEXPANSION
if (Salinity.TemperatureCompensation)
		if (TempSensor.unit)
		SalCompensation=Salinity.Read()/(1+((Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*Alpha_read()/100000));
		SalCompensation=Salinity.Read()/(1+((Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.001165));
		Params.Salinity=map(Params.Salinity, 0, SalMax, 60, 390); // apply the calibration to the sensor reading//salinity temp compensation
I have also noticed something that i think is weird and I dont know if it is related, if I just write any junk in reefangel.cpp and save the file then try to verify my code the compiler does not find errors
Posted: Mon Apr 22, 2013 4:56 pm
Make sure you are changing it in the correct place.
There are two places.
The top one is deprecated and will be removed.