Page 1 of 2
Trouble with setting multiple times for WP40 modes
Posted: Thu May 30, 2013 9:01 pm
by markywmson
Hi there
I've done some research and found something that mostly worked for me, and tried modding it to my needs, but I'm clearly missing something, as when I try to verify I get errors. Here is my code
if (hour()>=6 && hour()<11)
ReefAngel.PWM.SetDaylight( TidalSwellMode(45,true) ); // TidalSwell at 45% on sync mode
ReefAngel.PWM.SetActinic( TidalSwellMode(45,true) ); // TidalSwell at 45% on sync mode
else if (hour()>=11 && hour()<15)
ReefAngel.PWM.SetDaylight( ReefCrestMode(70,20,true) ); // ReefCrest at 70% +/- 20% on sync mode
ReefAngel.PWM.SetActinic( ReefCrestMode(70,20,false) ); // ReefCrest at 70% +/- 20% on anti-sync mode
else if (hour()>=15 && hour()<18)
ReefAngel.PWM.SetDaylight( NutrientTransportMode(30,60,6000,true) );
ReefAngel.PWM.SetActinic( NutrientTransportMode(30,60,6000,false) );
else if (hour()>=18 && hour()<20)
else if (hour()>=20 && hour ()<23)
ReefAngel.PWM.SetDaylight(SineMode(15,40,30,true) ); //SineMode from 15% to 40% for 30 seconds on sync mode
ReefAngel.PWM.SetActinic(SineMode(15,40,30,true) ); //SineMode from 15% to 40% for 30 seconds on sync mode
So what I'm trying to do is have from 6a-11a tidal swell, 11a-3p reefcrest, 3p-6p nutrient transport, 6p-8p reefcrest, 8p-11p tidal swell, and 11p-6a sine mode.
It says in the error, else without previous if. Does that mean all those need to be if instead of else if? The code I grabbed had else if.
Also can't figure out how to add if feeding mode ReefAngel.PWM.SetDaylight (20) and ReefAngel.PWM.SetActinic (20)
Thanks for any help!
-mark
Re: Trouble with setting multiple times for WP40 modes
Posted: Thu May 30, 2013 9:35 pm
They need curly braces around each block...you can only leave off the curly braces if there is only one line after the if else...
if (condition) {
action1();
action2();
} else if (condition) {
action1();
action2();
What you have works only without action2();
Also you seem to have a dangling } doing nothing...
Posted: Thu May 30, 2013 9:43 pm
by markywmson
So I would want it to look like this?
if (hour()>=6 && hour()<11) {
} else if (hour()>=11 && hour()<15) {
} else if (hour()>=15 && hour()<18) {
} else if (hour()>=18 && hour()<20) {
} else if (hour()>=20 && hour ()<23) {
} else {
It compiled so I assume it would be good. What (and where) would I put the if feedmode?
Posted: Thu May 30, 2013 10:10 pm
As the first condition at the beginning or a separate check afterwards.
Posted: Fri May 31, 2013 5:03 am
by jjdezek
Not trying to hijack your thread but I was wondering if those modes can be made to where you can manually switch between them? Like right before a water change switch it to nutrient export?
Posted: Fri May 31, 2013 5:16 am
Sure. I have a post in the long jaebo thread on using the vortech memory locations to switch the wave patterns. I use mp40s but you can look at my INO file. I have a custom menu and one of the items cycles through the modes with a button press.
Posted: Fri May 31, 2013 7:56 am
by markywmson
So adding it above would look something like this? Do I need to change the second if to "else if"?
if display=feeding mode etc... {
ReefAngel.
PWM.
SetDaylight(
TidalSwellMode(45,
true) );
ReefAngel.
PWM.
SetActinic(
TidalSwellMode(45,
true) );
ReefAngel.
PWM.
SetDaylight(
true) );
ReefAngel.
PWM.
SetActinic(
false) );
ReefAngel.
PWM.
SetDaylight(
true) );
ReefAngel.
PWM.
SetActinic(
false) );
ReefAngel.
PWM.
SetDaylight(
true) );
ReefAngel.
PWM.
SetActinic(
false) );
ReefAngel.
PWM.
SetDaylight(
TidalSwellMode(45,
true) );
ReefAngel.
PWM.
SetActinic(
TidalSwellMode(45,
true) );
else {
ReefAngel.
PWM.
SetDaylight(
SineMode(15,40,30,
true) );
ReefAngel.
PWM.
SetActinic(
SineMode(15,40,30,
true) );
Posted: Fri May 31, 2013 8:19 am
Yes. exactly!
Posted: Fri May 31, 2013 12:35 pm
by markywmson
Thanks Lee
I will try it tonight (after the boys go to bed) and report back.
Posted: Tue Jun 04, 2013 5:31 pm
by markywmson
So here is my full code. So far seems to work well. Haven't gotten around to implementing ATO, but that will need to be done in the next week, as I'll be out of town for 5 days at the end of June.
The Feeding Mode add worked as expected and something that I've found very awesome is being able to control relay 5 manually via my iphone app, thus negating the need for 3 hands while holding the hose from a pump to do water changes, plug it in, and not spray everything! (continuing after code)
ReefAngel.FeedingModePorts = Port3Bit | Port7Bit;
ReefAngel.WaterChangePorts = Port3Bit | Port6Bit | Port7Bit;
ReefAngel.OverheatShutoffPorts = Port1Bit | Port4Bit | Port5Bit | Port8Bit;
ReefAngel.Relay.On( Port2 );
ReefAngel.Relay.On( Port4 );
ReefAngel.StandardHeater( Port1,790,800 );
ReefAngel.Relay.DelayedOn( Port3,4 );
ReefAngel.StandardATO( Port7,250 );
ReefAngel.StandardHeater( Port8,770,790 );
if (ReefAngel.DisplayedMenu==FEEDING_MODE) {
ReefAngel.PWM.SetDaylight(30);
ReefAngel.PWM.SetActinic(30);
else if (hour()>=6 && hour()<11) {
} else {
ReefAngel.Portal( "markywmson" );
// Change the 30 to adjust the horizontal position of the text on the screen, max 20-21 chars
ReefAngel.LCD.DrawText(DefaultFGColor, DefaultBGColor, 30, 2, "Mark's Reef");
ReefAngel.LCD.DrawDate(6, 118);
ReefAngel.LCD.DrawMonitor(15, 68, ReefAngel.Params,
ReefAngel.PWM.GetDaylightValue(),
ReefAngel.PWM.GetActinicValue());
ReefAngel.LCD.DrawOutletBox(12, 101, TempRelay);
ReefAngel.LCD.DrawGraph(5, 11);
So my next quest on the powerhead portion of this would be 2 things. 1) since I have all those modes 'timelined' to happen at different times, is there a way to display that on the RA controller? (I'm sure the iphone app isn't there yet... I can see the different modes in the graph though). 2) is there a way to make it follow this logic...
-Sine mode overnight
-Tidal Swell in AM
-Reefcrest in early afternoon
-NTM in mid afternoon
-Reefcrest in late afternoon
-Tidal swell in PM
--> FEEDING MODE interrupts this timeline and sets power at 30 constant. //up to here my code is fine
--> Following FEEDING MODE interrupt the timeline with NTM for 3 hours, then resume timeline.
-->caveat... if this happens before NTM hits in the timeline (3p-6p), could the RA skip that NTM and
continue Reefcrest?
Thanks for any help! I'm actually starting to (kinda, sorta) understand this. Still can't write the code, but can steal and modify
-mark
Posted: Tue Jun 04, 2013 5:51 pm
In your if blocks set a variable to represent the "mode" you are in. Then use the variable to display it on the screen, I do the same thing for my mp40s. Take a look at my ino in the sig and search for vtMode
Posted: Tue Jun 04, 2013 6:40 pm
by markywmson
Hi Lee
Just when I was thinking I kind of understood... hahaha
So looking at your ino, I think the section you are talking about is this
void NextRFMode() {
vtMode++;
if (vtMode > 12) {
vtMode=0;
vtSpeed=50; // Constant
} else if (vtMode == 1) {
vtSpeed=40; // Lagoon
} else if (vtMode == 2) {
vtSpeed=45; // Reef Crest
} else if (vtMode == 3) {
vtSpeed=55; vtDuration=10; // Short Pulse
} else if (vtMode == 4) {
vtSpeed=55; vtDuration=20; // Long Pulse
} else if (vtMode == 5) {
vtSpeed=InternalMemory.read(Mem_B_NTMSpeed);
vtDuration=InternalMemory.read(Mem_B_NTMDuration); // Smart_NTM
} else if (vtMode == 6) {
vtSpeed=50; vtDuration=10; // Smart_TSM
} else if (vtMode == 7) {
vtSpeed=InternalMemory.read(Mem_B_NightSpeed);
vtDuration=InternalMemory.read(Mem_B_NightDuration);
vtMode=9; // Night
} else if (vtMode == 10) {
vtSpeed=65; vtDuration=5; // Storm
} else if (vtMode == 11) {
vtSpeed=45; vtDuration=10; // Custom
but I'm not sure how to apply that to non-RF based WP-40 (just using the SetDaylight and SetActinic to define my modes). What I think I need to do (based on what you said) is during my 6-11a hours call that block (1), 11-3 call that block (2), 3-6 call that block (3), 6-8 call that block (4), 8-11 call that block (5), and 11p-6a call that block (6).
And then I can make those 'blocks' call up a certain name on my menu display? I think that's what I got from it. but not sure on how to implement it. Any chance you could help me with one so I can work off of that and do the rest? Again, I want to learn this... teach a man to fish and all... but I'm nowhere close to even a pond, let alone a lake
Also is the other part of what I'd want to do possible?
Posted: Tue Jun 04, 2013 7:02 pm
Look at the vortech mode section in the DrawStatus() function. But yes you've got the idea exactly. Don't sell yourself short, it's just learning syntax, you seem to be following the concepts perfectly. What was the other thing?
Posted: Tue Jun 04, 2013 7:30 pm
by markywmson
Having it skip the 3-6 NTM if I use feeding mode earlier, let's say at 1... it interrupts Reefcrest mode, would like when feeding mode goes off, for NTM to kick in right then. And then if NTM hasn't happened (as scheduled) Reefcrest (or other current mode) would continue.
Seems very complex and not necessarily needed. Was more just wondering if it COULD be done. Would be cool.
Posted: Tue Jun 04, 2013 8:05 pm
Let me try and find some time tomorrow to mock it up for you. Everything is doable!
Posted: Tue Jun 04, 2013 8:18 pm
by markywmson
Thanks Lee! I work at nights, so I'll be reading along with all the other threads too. Might be a bit before I could implement though
Posted: Wed Jun 05, 2013 6:35 am
by bhazard
This is very helpful. Following.
Posted: Wed Jun 05, 2013 7:49 am
Ok, try this:
What I have done is moved the FEEDING_MODE check till after the time scheedule. The time schedule will set the default mode. During feeding mode we set a timer to the current time.
The block of code after feeding mode checks when that timer starts and runs that block of code that does the Nutrient mode for 3 hours after the feeding timer stops moving.
Then in the time schedule section, in the Nutrient mode, I added a check to see if that timer is more than a day old. If it is, it runs, otherwise your if block will fall down to the last else where you have SineMode.
If you want a different mode instead, you can add another else if with the same time frame without the timer check after the current one.
byte wpMode;
time_t feeding;
// Time schedule first
wpMode=1;
wpMode=2;
} else if ( (hour()>=15 && hour()<18) && (now()-feeding > SECS_PER_DAY) ) { // We haven't fed today
wpMode=3;
wpMode=2;
wpMode=1;
} else {
wpMode=4;
// If we are feeding override the schedule
wpMode=0;
feeding=now();
// If we have finished feeding, start NTM for 3 hours
if (now()-feeding < 3*SECS_PER_HOUR) {
wpMode=3;
// WP40 Mode
int x, y;
ReefAngel.LCD.DrawText(0,255,x,y,"RF:");
ReefAngel.LCD.Clear(DefaultBGColor,x,y,128-x,y+8);
if (wpMode == 0) ReefAngel.LCD.DrawText(COLOR_GREEN,255,x,y,"Feeding");
else if (wpMode == 1) ReefAngel.LCD.DrawText(COLOR_MAGENTA,255,x,y,"Tidal Swell");
else if (wpMode == 2) ReefAngel.LCD.DrawText(COLOR_GOLD,255,x,y,"Reef Crest");
else if (wpMode == 3) ReefAngel.LCD.DrawText(COLOR_RED,255,x,y,"Nutrient");
else if (wpMode == 4) ReefAngel.LCD.DrawText(COLOR_BLUE,255,x,y,"Sine Wave");
Posted: Wed Jun 05, 2013 6:24 pm
by markywmson
Lee,
This is SO awesome! I can't wait to give it a try!! The only part of the logic I'm not currently following (mostly because I am seeing some new code I don't know the meaning of) is what I've quoted.
lnevo wrote:Then in the time schedule section, in the Nutrient mode, I added a check to see if that timer is more than a day old. If it is, it runs, otherwise your if block will fall down to the last else where you have SineMode.
What I read from this is that when Feeding mode runs, it creates a timer and a timestamp in that timer. Then when NTM runs on schedule it checks the timer to see if wpMode=3 has run today. Now here is where I get a bit hazy... if Feeding mode HAS run I don't understand what the next mode is that will go.
Example... at 10am I go into Feeding mode. What happens next? The way I read it is that Reefcrest will pick up at 1pm, and then at 3 Sine mode starts. I'm confused by the "if block falling to the last else".
Thanks so much for your work on this and helping me to understand it Lee!
Posted: Wed Jun 05, 2013 6:41 pm
You have to add another 1-3pm for what mode you want if it already did NTM...right now it will "fall down" through the if else's to the last else which is sine mode.
If you look at the current 1-3pm if statement I added an addition check that the NTM hasn't been run for 24 hours
Posted: Wed Jun 05, 2013 6:42 pm
At 10am you feed. At 10:15 you come out of it. NTM runs for 3 hours and then back to regularly scheduled program.
Posted: Wed Jun 05, 2013 8:14 pm
by markywmson
Ok, cool, I think I understand it now. So regularly scheduled program (reefcrest at 1:15-3) then what happens? Sine mode the rest of the day/night?
I may be missing something obvious here... It's been a long day at work
Posted: Wed Jun 05, 2013 8:37 pm
Whatever your time schedule is set for... except for if you already did ntm mode then the scheduled ntm time will do the sine mode at the bottom.
Posted: Wed Jun 05, 2013 9:40 pm
by markywmson
Ohhhhhhhhhhhhkay! I get it. So if NTM is done already, then Sine mode will go during the "scheduled" NTM mode (3-6p). Is there somewhere I can change that to have Reefcrest continue (instead of going to Sine)?
Posted: Thu Jun 06, 2013 1:12 am
Just put another else if right after the current one with what you want. Put the same times as the current one. Make sure it comes after the current one and it will be used instead of sine mode..
Posted: Thu Jun 06, 2013 4:38 am
I was going to make it easier for you and then I also saw I made a slight error... the time_t feeding variable needs to either be global or static in order for it to maintain the state, otherwise every loop it would get re-initialized... here's the fix for that and also I modified it to address your last issue.
Enjoy.
static time_t feeding;
wpMode=1;
wpMode=2;
wpMode=3;
wpMode=2;
wpMode=2;
wpMode=1;
} else {
wpMode=4;
wpMode=0;
feeding=now();
wpMode=3;
Posted: Thu Jun 06, 2013 1:55 pm
by markywmson
Great! Thanks so much Lee
Just to make sure I understand how this is functioning (I really appreciate you taking your time to do this and explain it!)... In the "Schedule" area, it functions as normal if Feeding mode is never activated. We added the 2nd else if from 1500-1800 (reefcrest) for when Feeding mode IS activated. This will allow the logic set by this
// If we are feeding override the schedule if (ReefAngel.DisplayedMenu==FEEDING_MODE) {
wpMode=0;
feeding=now();
wpMode=3;
and this
to skip the first line that is set for 1500-1800 (NTM scheduled).
So what happens if Feeding mode ISN'T run and there are 2 modes scheduled at the same timeframe? Does it default to the first one automatically, and disregard the 2nd one?
Do I kind of have it right? Again, thank you SOOO much for helping me understand this.
Posted: Sat Jun 08, 2013 1:00 pm
by Smotz
lnevo wrote:Yes. exactly!
Dumb question - are all off the "IF / ELSE" statements needed?
Wouldn't it check for the condition - if true, action, if not true go to the next line.
for example - my code (sorry but somewhat related to this thread..)
// WAVE PATTERNS
else {
// ReefAngel.PWM.SetDaylight( ReefCrestMode(55,20,false) ); // ReefCrest at 55% +/- 20% on sync mode (MAX)
if ( (hour() >= 5) && (hour() < 8) ) // from 5a - 8a
ReefAngel.PWM.SetDaylight( ReefCrestMode(45,16,false) );
if ( (hour() >= 8) && (hour() < 11) ) // from 8a - 11a
ReefAngel.PWM.SetDaylight( ReefCrestMode(50,17,false) );
if ( (hour() >= 11) && (hour() < 14) ) // from 11a - 2pm
ReefAngel.PWM.SetDaylight( ReefCrestMode(55,18,false) );
if ( (hour() >= 14) && (hour() < 17) ) // from 2pm - 5pm
if ( (hour() >= 17) && (hour() < 20) ) // from 5pm - 8pm
if ( (hour() >= 20) && (hour() < 23) ) // from 8pm - 11p
ReefAngel.PWM.SetDaylight( ReefCrestMode(50,18,false) );
if ( (hour() >= 23) && (hour() < 2) ) // from 11pm - 2am
ReefAngel.PWM.SetDaylight( ReefCrestMode(55,17,false) );
if ( (hour() >= 2) && (hour() < 5) ) // from 2am - 5am
// IF not in feeding mode, AND IF in night mode
//else {
////ReefAngel.PWM.SetDaylight(50);
// ReefAngel.PWM.SetDaylight( SineMode(30,40,90,false) ); // Slow wave night mode
// Only turn on UV Sterilizer between 11pm and 5am
if ( (hour() >= 5) && (hour() < 23) ) // from 5a - 11p
ReefAngel.Relay.Off(UVlight);
else {
ReefAngel.Relay.On(UVlight);
Posted: Sat Jun 08, 2013 1:33 pm
It could be written a few ways....the behavior will vary depending on how its written and where you put the override logic.
In your case if any other if statements lower down qualify they will be picked up and override any previous matches.
In an if/else once the first if matches it will break out and no more matches will be checked.
Posted: Wed Jun 12, 2013 1:10 pm
Mark,