RANet firmware update
Posted: Sat Feb 06, 2016 12:39 am
I'd like to thank GiraffeCat for working with me on troubleshooting and finding out about this issue.
All RANet relay boxes and dimming modules will need this update.
Symptom: your RANet relay box blinks white/blue very fast and causes the relay box to go into fallback.
If you would like to see the symptom, upload this code:
#include <SoftwareSerial.h>
    ReefAngel.AddRANet();  // RANet Add-On Module
    ReefAngel.Relay.On(Box1_Port2);
    ReefAngel.Relay.On(Box1_Port4);
How to perform the firmware update:
1. Open the relay box/dimming module enclosure
2. Locate the RANet module inside.
3. Remove it from the expansion module
4. Detach the Xbee radio. Be careful not to damage the pins of the radio. Be very gentle.
5. Connect the USB-TTL cable to the RANet module
6. Download the attached code and open the code on Arduino or copy and paste it from the bottom of the post
8. Change the board to "Reef Angel Controller w/ optiboot"
9. Upload the code
10. Make sure the code uploads and Arduino says "Done uploading" without errors
11. Disconnect the USB-TTL cable
12. Attach the Xbee radio
13. Place the RANet module back into the expansion module
14. Close the enclosure
15. Change the board back to "Reef Angel Plus"
16. Upload the code above to confirm that the firmware fixed the issue
This is the latest firmware code:
#include <avr/eeprom.h>
#define BLUE_LED    9
#define WHITE_LED   10
#define BLUE_INTENSITY   255
#define WHITE_INTENSITY  255
#define RANET_MAX_SIZE  68
#define DISCONNECT_TIMEOUT  10000
#define LastFallback0  100 // Memory location for fallback storage
#define RANet_Down    0
#define RANet_OK      1
#define LIGHTNING 1    // Trigger value for lightning strike
#define TRIGGER 62     // Position in payload of trigger byte
byte buffer_index;
byte buffer[128];
char buf[3];
byte bufint, bufsize;
byte RANetData[RANET_MAX_SIZE];
byte RANetCRC;
byte BlueChannel=0;
byte WhiteChannel=0;
byte RANet_Status=RANet_Down;
boolean cable_present=false;
unsigned long lastcablecheck=millis();
char lastc=0;
  pinMode(BLUE_LED,OUTPUT);
  pinMode(WHITE_LED,OUTPUT);
  Serial.begin(57600);
  Wire.onReceive(NULL);
  Wire.onRequest(NULL);
  Wire.begin();
  for (int a=0;a<RANET_MAX_SIZE; a++) // Clear array
    RANetData[a]=0;
  Wire.beginTransmission(0x68);
  Wire.write(0);
  int a=Wire.endTransmission();
  cable_present=(a==0);
  // setup PCA9685 for data receive
  // we need this to make sure it will work if connected ofter controller is booted, so we need to send it all the time.
  Wire.beginTransmission(0x40);
  Wire.write(0);
  Wire.write(0xa1);
  if (cable_present)
    BlueChannel=100;
    WhiteChannel=0;
    analogWrite(WHITE_LED,WHITE_INTENSITY*WhiteChannel/100);
    analogWrite(BLUE_LED,BLUE_INTENSITY*BlueChannel/100);
    BlueChannel=0;
    WhiteChannel=0;
    while(Serial.available())
      UpdateWhiteChannel();
      char c = Serial.read(); // Read each incoming byte
      buffer[buffer_index]=c; // store in the buffer array
      if (c==10 && lastc==13) // if line feed we analyze the payload
        if (buffer_index>25) // only need to analyse if buffer_index is greater than 25, otherwise the payload is broken or corrupt
          if (buffer_index==buffer[1]) // check if payload matches the length the controller sent
            RANetCRC=0;
            for (int a=0; a<(buffer_index-2); a++) // calculate CRC
              RANetCRC+=buffer[a];
            if (RANetCRC==buffer[buffer_index-2]) // if CRC matches
              for (int a=0; a<(buffer_index-2); a++) // Copy buffer to RANetData
                RANetData[a]=buffer[a];
  //            Serial.print(millis());
  //            Serial.print("\t");
  //            Serial.println(RANetData[2]);
              for (int a=0;a<8;a++)
                if (eeprom_read_byte((unsigned char *) LastFallback0+a)!=RANetData[10+a])
                  eeprom_write_byte((unsigned char *) LastFallback0+a, RANetData[10+a]);
                Wire.beginTransmission(0x38+a);
                Wire.write(~RANetData[2+a]);
              for (int a=0;a<12;a=a+2)    // Step through the 12 bytes of dimming data
                byte newdata=(RANetData[18+a]);    //LSB
                byte newdata1=(RANetData[18+a+1]);  //MSB
                Wire.write(0x8+(4*(a/2)));  // Channels 0 through 5
                Wire.write(newdata);    // Write LSB
                Wire.write(newdata1);   // Write MSB
              RANet_Status=RANet_OK;
        buffer_index=255; // reset buffer index
      lastc=c;
      if (buffer_index++>=128) buffer_index=0; // increment index of buffer array. reset index if >=128
    if (millis()-lastmillis>DISCONNECT_TIMEOUT)
  //    Serial.println("Disconnected");
  //    Serial.println(RANetData[10]);
        Wire.write(~eeprom_read_byte((unsigned char *) LastFallback0+a));
    if (RANet_Status==RANet_Down)
        BlueChannel=0;
        WhiteChannel=millis()%2000<1000?0:100;
  if (RANetData[TRIGGER]==LIGHTNING) Lightning();    // Look for lightning trigger
  RANetData[TRIGGER]=0;    // Clear trigger byte.
void UpdateWhiteChannel()
  WhiteChannel=sin(radians((millis()%7200)/40))*255;
  BlueChannel=255-(sin(radians((millis()%7200)/40))*255);
  analogWrite(WHITE_LED,WhiteChannel);
  analogWrite(BLUE_LED,BlueChannel);
void Lightning()
  int a=random(1,5);    // Pick a number of consecutive flashes from 1 to 4.
  for (int i=0; i<a; i++)
    // Flash on
    int newdata=4095;
    Wire.beginTransmission(0x40);      // Address of the dimming expansion module
    Wire.write(0x8+(4*1));             // 0x8 is channel 0, 0x12 is channel 1, etc.  I'm using channel 1.
    Wire.write(newdata&0xff);          // Send the data 8 bits at a time.  This sends the LSB
    Wire.write(newdata>>8);            // This sends the MSB
    int randy=random(20,80);    // Random number for a delay
    if (randy>71) randy=((randy-70)/2)*100;    // Small chance of a longer delay
    delay(randy);                // Wait from 20 to 69 ms, or 100-400 ms
    // Flash off
    Wire.beginTransmission(0x40);    // Same as above
    Wire.write(RANetData[20]);      // Return to previous value
    Wire.write(RANetData[21]);
    delay(random(30,50));                // Wait from 30 to 49 ms
Re: RANet firmware update
Posted: Sat Feb 06, 2016 6:57 am
by bencollinz
Is there a way to power up the board and test this without having to put it all back together? I have mine running off the USB cable right now and I really don't want to take it all apart just to not work again.
Posted: Sat Feb 06, 2016 3:46 pm
by Sacohen
Thanks for the update.
I did it and when I opened the relay module the wire that is connected to the RANet module was not connected to anything.
I could not see where it should be connected.
I put the whole thing back together and it all seems to be working in terms of the ports all turn on and off remotely, but the Reef Angle logo doe not light up at all now.
It worked fine before.
Posted: Sat Feb 06, 2016 4:06 pm
bencollinz wrote:Is there a way to power up the board and test this without having to put it all back together? I have mine running off the USB cable right now and I really don't want to take it all apart just to not work again.
You can power it with the power cord without putting it back together. Just be careful not to touch the socket pins.
Sacohen wrote:Thanks for the update.
The logo plugs into that connector
Posted: Sat Feb 06, 2016 4:20 pm
by Sacohen
I'll open it again, but the other end coming from that connection was not attached to anything.
Posted: Sun Feb 07, 2016 5:58 am
by bencollinz
Sacohen wrote:I'll open it again, but the other end coming from that connection was not attached to anything.
It's a very tiny LED. I thought the same thing. It's supposed to be glued/taped to the closest end of the RA logo to that connector. I used electrical tape.
Posted: Sun Feb 07, 2016 6:24 am
by bencollinz
side note; I love how upload size is limited to 2MB then you try to upload it after resizing and the limit changes to 1MB. something odd happening there.
Posted: Sun Feb 07, 2016 6:34 am
by bencollinz
rimai wrote:I'd like to thank GiraffeCat for working with me on troubleshooting and finding out about this issue.
9. Upload the code
#define BLUE_LED    9
#define RANet_OK      1
byte buffer_index;
byte buffer[128];
char buf[3];
byte RANetCRC;
byte BlueChannel=0;
char lastc=0;
  Wire.begin();
    RANetData[a]=0;
  Wire.write(0);
  Wire.write(0);
  Wire.write(0xa1);
  if (cable_present)
    BlueChannel=100;
    WhiteChannel=0;
    BlueChannel=0;
    WhiteChannel=0;
            RANetCRC=0;
      lastc=c;
        BlueChannel=0;
void Lightning()
    // Flash on
    int newdata=4095;
    // Flash off
This fixed the issue! Thank you very much. Any idea why it started?
Posted: Sun Feb 07, 2016 8:04 am
by Sacohen
Thanks. I thought it was something like that.
Posted: Sat May 14, 2016 1:14 pm
by GiraffeCat
If you would like to see the symptom, upload this.....
I would like to thank Roberto, because where else are you going to find this kind of tech support? (Check the time he posted this update thread if you don't believe me.) So, Thank You!
It has been a while since I changed the code on the boards, and haven't seen the issue return. (I waited to reply until I was sure.) I am going to start messing with stuff again soon, and I hope to not find any more bugs.
Thanks again for getting this figured out,
Dan