Salinity temp compensation?
dazza1304
From the reading I have been doing and testing myself, I have seen and found that over a relatively small range of temperatures, the temp effect on salinity is very linear and typically in the range of 2-2.4% per deg Celsius change.
Why not have automatic temp compensation provided in the libraries to enable more accurate salinity readings?
I am sure most people with reef angel will control their temps within very tight limits, and this would improve the accuracy of salinity readings.
For example, with salinity of 35ppt, for each 0.1 deg variation, you will typically get a variation in salinity of 0.077ppt, (so almost 0.1ppt for each 0.1 deg C) which is significant.
I have for some time been using ATO based off salinity, but it is not controlled as tight as is possible (or I would like) with the reef angel for the above reason.
I found this code, and as an interim would like to use it, just not sure where to put it so to speak, also I run my tank at 25.5 deg, so would I need to change the values to 255 instead of 250 - but ultimately, could this not be incorporated as standard into reef angel code which will make the reef angel even more awesome! In fact I think that other product to do with neptune has this feature!?
Posted: 22 Mar 2012 19:27
Ok, I changed it to this:
CODE: SELECT ALL
double SalCompensation;
if (TempSensor.unit)
SalCompensation=Params.Salinity/(1+((Params.Temp[T1_PROBE]-250)*0.0024));
SalCompensation=Params.Salinity/(1+((Params.Temp[T1_PROBE]-770)*0.001333));
Params.Salinity=round(SalCompensation);
CODE: SELECT ALL
Re: Salinity temp compensation?
Actually, in order for this to work, you must save the temperature in which the calibration occurred in internal memory.
Then, you can calibrate at any temperature and also compensate it to adjust to any temperature variance along the way.
The formula you posted was contributed by a user and did not work quite well for me.
I was never able to make it work.
I did however come up with another formula that I have tested for a +/- 10F degree variance and it performed quite well.
This is what I used:
But in order for this formula to work, the temperature in which the salilnity calibration occured must be save in internal memory (SalTempComp location).
If you want to test and confirm it is working, it would be awesome.
Post your code and I can change it to apply the compensation.
if (ReefAngel.TempSensor.unit)
SalCompensation=ReefAngel.Params.Salinity/(1+((t-InternalMemory.SalTempComp_read())*0.00344123));
SalCompensation=ReefAngel.Params.Salinity/(1+((t-InternalMemory.SalTempComp_read())*0.001925));//001333
ReefAngel.Params.Salinity=round(SalCompensation);
dazza1304
more than happy to give it a try!!! Just let me know where I need to enter my cal temp etc!! Also, ultimately as said before, it would be great to have incorporated in the embedded code - for salinity cal I could see a simple change where you enter your tank temp probe, then set your compensation factor, then salinity cal.rimai wrote:Actually, in order for this to work, you must save the temperature in which the calibration occurred in internal memory.
This is what I used:But in order for this formula to work, the temperature in which the salilnity calibration occured must be save in internal memory (SalTempComp location).Code: Select all
double SalCompensation; if (ReefAngel.TempSensor.unit) SalCompensation=ReefAngel.Params.Salinity/(1+((t-InternalMemory.SalTempComp_read())*0.00344123)); else SalCompensation=ReefAngel.Params.Salinity/(1+((t-InternalMemory.SalTempComp_read())*0.001925));//001333 ReefAngel.Params.Salinity=round(SalCompensation);
Anyway, below is my code -
PS - what is it with all these idiots lately posting rubbish?
unsigned long lastLowSal=now();//salinity >35.1 timer
boolean SALduration=true;//salinity >35.1 for 2 minutes flag
boolean ATOEnabled=false;//enable ATO function for 5 seconds
boolean ATOPumping=true;//disable ATO function for 5 minutes
unsigned long ATOStart=now();//ATO 5 sec run timer
InternalMemory.OverheatTemp_write( 260 );
ReefAngel.Relay.On( Port4 );
ReefAngel.Relay.On( Port5 );
ReefAngel.Timer[1].SetInterval(1800); // 30 mins before reactivation of ATO
ReefAngel.MHLights( Port3,0,30,23,30,5 );//skimmer off and on for dosing reef energy
ReefAngel.StandardHeater( Port6,254,255 );
ReefAngel.StandardFan( Port7,255,256 );
ReefAngel.MHLights( Box1_Port5,23,30,23,31,0 );//air pump for mix reef energy prior to dosing
ReefAngel.WaterLevelATO(Port2,180,38,40);// Salinty top up to keep water level correct
///// If salinity >35.1 for 120 sec set SALduration flag
if (ReefAngel.Params.Salinity<351) lastLowSal=now();
if (now()-lastLowSal>120) SALduration=false;
if (SALduration && ATOPumping)//if salinity>35.1 for 2 minutes enable ATO
{ATOStart=now();
ATOEnabled=true;
ATOPumping=false;
if (now()-ATOStart<5)//ATO pump on time 5 seconds
if (ATOEnabled) ReefAngel.Relay.On(Port1);
ReefAngel.Timer[1].Start();//start 5 minute disable of ATO
ReefAngel.Relay.Off(Port1);
ATOEnabled=false;
if (ReefAngel.Timer[1].IsTriggered())//after 30 minute disable, enable ATO
ATOPumping=true;
ATOStart=now();
SALduration=true;
///// if skimmer cup full, turn off skimmer
bitClear(ReefAngel.Relay.RelayMaskOff,2);
else {
bitSet(ReefAngel.Relay.RelayMaskOff,2);
ReefAngel.Portal( "dazza1304" );
int x,y;
ReefAngel.LCD.DrawMonitor( 15, 10, ReefAngel.Params,
ReefAngel.LCD.DrawMonitor( 15, 10, ReefAngel.Params );
// Salinity
ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,15,46, "SAL:" );
ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,39,46, ReefAngel.Params.Salinity );
// ORP
ReefAngel.LCD.DrawText( COLOR_PALEVIOLETRED,DefaultBGColor,75,46, "ORP:" );
ReefAngel.LCD.DrawText( COLOR_PALEVIOLETRED,DefaultBGColor,99,46, ReefAngel.Params.ORP );
// Water Level
ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,75,63, "WL:" );
ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,99,63, ReefAngel.WaterLevel.GetLevel() );
ReefAngel.LCD.DrawOutletBox( 12, 79, TempRelay );
// Relay Expansion
Try this:
To be honest, I never tested it in Celsius though. Sorry...
So, I would suggest starting your tests with Fahrenheit first.
Make sure you change the value in this line:
InternalMemory.SalTempComp_write( 780); // Change this to compensation temperature
// Apply Salinity Compensation
SalCompensation=ReefAngel.Params.Salinity/(1+((ReefAngel.Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.00344123));
SalCompensation=ReefAngel.Params.Salinity/(1+((ReefAngel.Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.001925));//001333
ReefAngel.Params.Salinity=map(ReefAngel.Params.Salinity, 0, ReefAngel.SalMax, 60, 350); // apply the calibration to the sensor reading
ATOStart=now();
ATOEnabled=true;
ATOPumping=false;
ATOEnabled=false;
ATOPumping=true;
ATOStart=now();
SALduration=true;
else {
int x,y;
// Salinity
// ORP
// Water Level
// Relay Expansion
dazza1304
Hi Roberto,
Happy to try in celcius - just wanted to check with the code below:
As I always have set to Celcius, couldnt I simplify a little as below?
SalCompensation=ReefAngel.Params.Salinity/(1+((ReefAngel.Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.022));
That's what I said. Please test it in F before you move to C.
Don't change any code at this time.
I think I made the constants correct. Well, I'm sure it it for F degrees.
The problem of this compensation is to adjust the constant.
dazza1304
Hi Roberto,
Tried this code below and I am sure it is something simple, but when I run, the salinity display on the head unit is jumping all over the place - like it is been re written many times with differing values - any ideas?
I also tried the code exactly as you pasted above and changed temp unit to deg F, and still the same.
InternalMemory.SalTempComp_write( 255); // Change this to compensation temperature
ReefAngel.StandardHeater( Port6,252,255 );
ReefAngel.StandardFan( Port7,255,258 );
SalCompensation=ReefAngel.Params.Salinity/(1+((ReefAngel.Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.0022));
{ATOStart=now();
ATOEnabled=true;
ATOPumping=false;
ATOEnabled=false;
ATOPumping=true;
ATOStart=now();
SALduration=true;
else {
int x,y;
// Salinity
// ORP
// Water Level
// Relay Expansion
dazza1304
Can anybody help please??
dazza1304
Thanks ronerto
dazza1304
Thanks Roberto!
Piper
You probably need to put a clear in right before you draw the salinity. Try this:
// Salinity
ReefAngel.LCD.Clear(DefaultBGColor, 39, 46, 69, 54); // You will probably need to adjust the x,y on this a little
dazza1304
Thanks, but that doesnt fix the problem.
I have played around a bit more and I think it has something to do with the map function - with this in, the reading really jumps all over the place.
With it removed, it seems to work a bit more stable, but still the salinity value jumps around a lot - it seems that the salinity value is way too sensitive to the temp, if that makes sense?
Yeah, I don't think it will work as it is.
We'll need to come up with a different plot.
This constant was calculated and tested for another meter I have, but the resolution is different between the two.
If you want to contribute with the plot, it would be awesome!!
Here is your code with the raw adc readings in it.
What we need is to collect the adc reading at several different temperatures.
Preferably for every 1/2 C degree within the +/-5 degree range of your tank temperature where the salinity was calibrated.
So, fill up a cup of tank water and heat it up to +5C degrees and place the temp probe and salinity probe in it.
Start logging the data all the way until the temperature of the water is -5C degrees.
I'll try to plot the same for F degrees.
{ATOStart=now();
ATOEnabled=true;
ATOPumping=false;
ATOEnabled=false;
ATOPumping=true;
ATOStart=now();
SALduration=true;
else {
int x,y;
// Salinity
// ADC
ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,15,63, "ADC:" );
ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,39,63, ReefAngel.Salinity.Read() );
// ORP
// Water Level
// Relay Expansion
dazza1304
Will do Roberto,
dazza1304
Hi Roberto,
Here is the results of that - results pretty linear.
Temp Sal ADC
31.0 396 3343
30.5 393 3307
30.0 389 3271
29.5 385 3231
29.0 381 3195
28.5 377 3151
28.0 373 3111
27.5 369 3075
27.0 365 3035
26.5 362 3007
26.0 359 2975
25.5 356 2943
25.0 353 2915
24.5 350 2879
24.0 346 2843
23.5 342 2803
23.0 338 2759
22.5 333 2719
22.0 329 2675
21.5 325 2635
21.0 321 2595
20.5 316 2547
20.0 311 2499
here are the charts, if I can get them to load!!
Temp Sal ADC
31.0 396 3343
30.5 393 3307
30.0 389 3271
29.5 385 3231
29.0 381 3195
28.5 377 3151
28.0 373 3111
27.5 369 3075
27.0 365 3035
26.5 362 3007
26.0 359 2975
25.5 356 2943
25.0 353 2915
24.5 350 2879
24.0 346 2843
23.5 342 2803
23.0 338 2759
22.5 333 2719
22.0 329 2675
21.5 325 2635
21.0 321 2595
20.5 316 2547
20.0 311 2499
Awesome!!
Yes, it is supposed to be linear.
At what temperature did you calibrate?
dazza1304
Hi Roberto, yes I know it is supposed to be linear, I was just stating that my data points seem to be valid!!rimai wrote:Awesome!!
Calibration temp was 25.5 deg C.
I have done the maths on this for you, and using the formula:
Actual salinity = Measured salinity/(1+((temp sal measured at - calibration temp)* factor)))
For the Salinity reading I come out with a factor of 0.0214
For the ADC values, I come out with a factor 0.0248
I have attached the data, and also a plot of the compensated salinity and ADC using the above formula.
So, I think this brings us back to square one, in terms of getting the temp compensation working??
dazza1304
no - not yet - will do that tomorrow.
Just been playing around with the constants to get a better fit and now have a really good fit for Celcius and Fahrenheit.
Basically, Celcius constant = 0.00211 Fahrenheit constant = 0.001175 - graphs below with these contants used so you can see the correction.
dazza1304
Hi Roberto,
I think there is still problems with the code and I think I know where.
In the above code, the compensated salinity is been written to reef angel.params.salinity and each time it goes through the loop it will try to apply the compensation to the already compensated value etc.
So, if we changed the code to :
SalCompensation=round(SalCompensation);
Then we would just need to display the SalCompensation value instead (or even as well as) the salinity value.
So, how do I do that - something like this below, although somehow the SalCompensation needs to be defined and not sure how to do that?
// SalCompensated
ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,15,63, "SALC:" );
ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,39,63, SalCompensation.Read() );
// SalCompensated
ReefAngel.LCD.DrawText( COLOR_BLACK,DefaultBGColor,39,63, (int)SalCompensation );
But, I think the best approach is to compensate the ADC value.
Try this:
SalCompensation=ReefAngel.Salinity.Read()/(1+((ReefAngel.Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.0022));
SalCompensation=ReefAngel.Salinity.Read()//(1+((ReefAngel.Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.001925));
dazza1304
When compiling, the following line give an error - expected ";" before reef angel?
Oh, I just copied what you had....
There was an extra slash in there, turning the rest of the code into comment.
SalCompensation=ReefAngel.Salinity.Read()/(1+((ReefAngel.Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.001925));
dazza1304
Hi Roberto,
OK, what I would like to do, is run both uncompensated salinity and compensated, so I can check it works how I expect first, as use salinity for my ATO, and dont want to mess my tank up!!
I have the code as below, but when I compile it comes up with an error: SalCompensation was not declared in this scope
SalCompensation=ReefAngel.Params.Salinity/(1+((ReefAngel.Params.Temp[T1_PROBE]-InternalMemory.SalTempComp_read())*0.00215));
{ATOStart=now();
ATOEnabled=true;
ATOPumping=false;
ATOEnabled=false;
ATOPumping=true;
ATOStart=now();
SALduration=true;
else {
int x,y;
// Salinity
//comp salinity
// ORP
// Water Level
// Relay Expansion
You have SalCompenstation being declared within the loop function. If you want to draw it in the DrawCustomMain() function, you'll have to declare it with your globals.
dazza1304
As Roberto said, the SalCompensation is already defined in a library somewhere though? I think reefangel.cpp?lnevo wrote:You have SalCompenstation being declared within the loop function. If you want to draw it in the DrawCustomMain() function, you'll have to declare it with your globals.
If it is defined there, I shouldn't have to define it again in a global should I?
No, it's declared in your loop()
Just move it up top to globals.
dazza1304
Sorry for being so thick- now works!! BTW, what does double do - as in double SalCompensation?
Will chart it tomorrow and see how it works!!!