Main relay port #6

Posted: Wed Jan 16, 2013 1:09 am
by romebaby
Port #6 trips my gfi breaker every time I shut off whatever is plugged into it. I've tried switching pumps & powerheads, does not matter if it is something drawing 6w or 35w it will trip. Several problems with this - I can't run the wavemaker function and I just bought some new powerheads specifically for this and I can't have them shut off on feed mode or water change mode. Do I have a faulty relay box?

Re: Main relay port #6

Posted: Wed Jan 16, 2013 9:28 am
by rimai
Port 5 and 6 have components to dampen the inductive spike generated by constant on/off of powerheads.
Maybe this is influencing on your gfci.
Does the port function accordingly if you don't use the gfci?

Re: Main relay port #6

Posted: Wed Jan 16, 2013 9:32 am
by romebaby
Haven't tried a non gfi but port 5 never trips it, and I've hammered 5 with the same gear trying to trip it.