Moonphase on custom main
Re: Moonphase on custom main
NO? lol
rimai wrote:Try this function.
Add to end of loop(). If it works, I'll make part of the libraries.
char* MoonPhaseLabel()
  int m,d,y;
  int yy,mm;
  long K1,K2,K3,J;
  double V;
  byte PWMvalue;
  m = month();
  d = day();
  y = year();
  yy = y-((12-m)/10);
  mm = m+9;
  if (mm>=12) mm -= 12;
  K1 = 365.25*(yy+4712);
  K2 = 30.6*mm+.5;
  J = K1+K2+d+59-K3;
  V = (J-2451550.1)/29.530588853;
  V -= floor(V);
  if (V<0) V++;
  if (V<0.0625) return "New Moon";
  else if (V<0.1875) return "Waxing Crescent";
  else if (V<0.3125) return "First Quarter";
  else if (V<0.4375) return "Waxing Gibbous";
  else if (V<0.5625) return "Fuul Moon";
  else if (V<0.6875) return "Waning Gibbous";
  else if (V<0.8125) return "Last Quarter";
  else if (V<0.9375) return "Waning Crescent";
  else return "New Moon";
You can draw on the screen with something like this:
ReefAngel.LCD.DrawText(0,255,10,10,MoonPhaseLabel());
I get nothing but "not in slope" errors when doing these instructions. What do I need to do to the global.h ?
"not in slope"???
There is no slope in there. Must be something else in your code generating that error.
There's nothing else that needs to be done.
Just put the whole function after the entire loop() section and call it in your custom main section.
Sorry this:
RA_060912_2037customNEW.cpp: In function 'void loop()':
RA_060912_2037customNEW:205: error: 'd' has not been declared
RA_060912_2037customNEW:205: error: 'y' has not been declared
RA_060912_2037customNEW:205: error: expected `)' before ';' token
RA_060912_2037customNEW:205: error: 'MoonPhaseLabel' declared as function returning a function
RA_060912_2037customNEW:210: error: 'm' was not declared in this scope
RA_060912_2037customNEW:211: error: 'd' was not declared in this scope
RA_060912_2037customNEW:212: error: 'y' was not declared in this scope
RA_060912_2037customNEW:223: error: return-statement with a value, in function returning 'void'
RA_060912_2037customNEW:224: error: return-statement with a value, in function returning 'void'
RA_060912_2037customNEW:225: error: return-statement with a value, in function returning 'void'
RA_060912_2037customNEW:226: error: return-statement with a value, in function returning 'void'
RA_060912_2037customNEW:227: error: return-statement with a value, in function returning 'void'
RA_060912_2037customNEW:228: error: return-statement with a value, in function returning 'void'
RA_060912_2037customNEW:229: error: return-statement with a value, in function returning 'void'
RA_060912_2037customNEW:230: error: return-statement with a value, in function returning 'void'
RA_060912_2037customNEW:231: error: return-statement with a value, in function returning 'void'
RA_060912_2037customNEW:232: error: expected primary-expression before ')' token
RA_060912_2037customNEW:232: error: expected `;' before ')' token
I'm assuming this is calling on the definition of "m" "y" etc etc...but it's not defined?
You need to place after the loop() section and not inside of it.
Oh wow. Sorry I'm still learning. What is the purpose of this? I understand the setup() and loop() but I'm still learning.
setup() is the section that gets run when the controller boots up. It only runs once.
loop() is the section that keeps running over and over again.
http://arduino.cc/en/Tutorial/BareMinimum
The testing has begun!
jsclownfish
Post by jsclownfish »
I've been using this code for a month or so in my custom main and it seems to work OK.
// moonphase------------------------------------------------------------
  YY = (year()) - floor((12 - (month())) / 10);
  MM = (month()) + 9;
  if (MM >= 12)
    MM = MM - 12;
  K1 = floor(365.25 * (YY + 4712));
  K2 = floor(30.6 * MM + 0.5);
  K3 = floor(floor((YY / 100) + 49) * 0.75) - 38;
  JD = K1 + K2 + (day()) + 59;
  if (JD > 2299160)
    JD = JD - K3;
  IP = (JD - 2451550.1) / 29.530588853;
  IP = IP - floor(IP);
  if (IP < 0)
    IP = IP + 1;
  AG = IP*29.53;
  if (AG < 1.84) ReefAngel.LCD.DrawText(DPColor,DefaultBGColor, 5, 43,"New");
  else if (AG < 5.53) ReefAngel.LCD.DrawText(DPColor,DefaultBGColor, 5, 43,"Waxing Crescent");
  else if (AG < 9.92) ReefAngel.LCD.DrawText(DPColor,DefaultBGColor, 5, 43,"First Quarter");
  else if (AG < 12.91) ReefAngel.LCD.DrawText(DPColor,DefaultBGColor, 5, 43,"Waxing Gibbous");
  else if (AG < 16.61) ReefAngel.LCD.DrawText(DPColor,DefaultBGColor, 5, 43,"Full");
  else if (AG < 20.30) ReefAngel.LCD.DrawText(DPColor,DefaultBGColor, 5, 43,"Waning gibbous");
  else if (AG < 23.99) ReefAngel.LCD.DrawText(DPColor,DefaultBGColor, 5, 43,"Last Quarter");
  else if (AG < 27.68) ReefAngel.LCD.DrawText(DPColor,DefaultBGColor, 5, 43,"Waning Crescent");
  else  ReefAngel.LCD.DrawText(DPColor,DefaultBGColor, 5, 43,"New") ;
Better than this one?
  int m,d,y;
  int yy,mm;
  long K1,K2,K3,J;
  double V;
  byte PWMvalue;
  m = month();
  d = day();
  y = year();
  yy = y-((12-m)/10);
  mm = m+9;
  K2 = 30.6*mm+.5;
  J = K1+K2+d+59-K3;
  V -= floor(V);
  if (V<0) V++;
This code is working thus far! I'll keep everyone updated.
  int m,d,y;
  int yy,mm;
  long K1,K2,K3,J;
  double V;
  byte PWMvalue;
  m = month();
  d = day();
  y = year();
  yy = y-((12-m)/10);
  mm = m+9;
  K2 = 30.6*mm+.5;
  J = K1+K2+d+59-K3;
  V -= floor(V);
  if (V<0) V++;
[/quote]
psyrob
Post by psyrob »
any update? How is it working?
Still working great! Three more phases to watch for and after that I'll post back.
Still working great. At this point. I'd say it's 100% good to go.
psyrob
Post by psyrob »
Im having trouble...in the code above, I paste it all after the loop and keep getting an error...Does the line
"char*MoonPhaseLabel" go somewhere else?
You have to make sure it is after the loop() section of the code. I did loop() {Your code here ReefAngel.ShowInterface(); } then the char*MoonPhaseLabel()
So.
ReefAngel.LCD.DrawText(0,255,20,57,MoonPhaseLabel());
Goes in your custom main...(change location depending on what you have)
Then,
    ReefAngel.StandardLights( Port1,19,0,6,30 );
    ReefAngel.StandardHeater( Port4,740,770 );
    ReefAngel.StandardLights( Port7,6,0,20,0 );
    ReefAngel.StandardLights( Port8,7,0,19,0 );
    //////// ReefAngel.Wavemaker1(Port5);
    /////// ReefAngel.Wavemaker2(Port6);
    //ReefAngel.PWM.SetActinic( MoonPhase ) Test for Meanwells
    ReefAngel.PWM.SetDaylight( PWMParabola(7,5,19,0,0,85,0) );
    ReefAngel.PWM.SetActinic( PWMParabola(6,5,21,0,0,85,0) );
    ///if ( ReefAngel.Timer[1].IsTriggered() )
          ///  ReefAngel.Timer[1].SetInterval(random(15,35));
          ///  ReefAngel.Timer[1].Start();
           /// ReefAngel.Relay.Toggle(Port5);
          ///  ReefAngel.Relay.Toggle(Port6);
    if (hour()>=6 && hour()<20)
    analogWrite(lowATOPin,0);
    analogWrite(lowATOPin,(int)MoonPhase()*2.55);
    //if ( ReefAngel.DisplayedMenu == DEFAULT_MENU ) //Dosing
   Hours between 21 and 5
   minute must be 0 (top of the hour)
   seconds less than 4 (up to 5 seconds)
   if ( ((hour()>=21) || (hour()<=5)) &&
       (minute()==0) &&
       (second()<4) )
      ReefAngel.Relay.On(Port2);
     ReefAngel.Relay.Off(Port2); //End Dosing
  int m,d,y;
  int yy,mm;
  long K1,K2,K3,J;
  double V;
  byte PWMvalue;
  m = month();
  d = day();
  y = year();
  yy = y-((12-m)/10);
  mm = m+9;
  K2 = 30.6*mm+.5;
  J = K1+K2+d+59-K3;
  V -= floor(V);
  if (V<0) V++;
  if (V<0.0625) return "New Moon Time!";
  else if (V<0.5625) return "Full Moon Time!";
  else return "New Moon Time!";
psyrob
Post by psyrob »
thanks
Good to go? It's still working great for me!
alexwbush
Post by alexwbush »
having some trouble...
here are the errors:
Globals\Globals.cpp.o: In function `MoonPhaseLabel()':
C:\Users\orbitonit\Documents\Arduino\libraries\Globals/Globals.cpp:135: multiple definition of `MoonPhaseLabel()'
sketch_nov30b.cpp.o:C:\Users\ORBITO~1\AppData\Local\Temp\build6404265574585745318.tmp/sketch_nov30b.cpp:352: first defined here
e:/program files (x86)/reef angel controller/hardware/tools/avr/bin/../lib/gcc/avr/4.3.2/../../../../avr/bin/ld.exe: Disabling relaxation: it will not work with multiple definitions
It's in the libraries now. You don't need to define it now :)
Can you post your code?
Says you have two functions with same name.
alexwbush
Post by alexwbush »
it's still a work in progress. I need to clean it up a lot
#include <WaterLevel.h> //Added for water level
byte buzzer=0;
byte overheatflag=0;
byte atoflag=0;
byte topofflevel;
byte starthr = 8; //start hour for radion cycle (0-23)
byte startmin = 0; //start minute for radion cycle (0-59)
byte endhr = 22; //end hour for radion cycle (0-23)
byte endmin = 0; //end min for radion cycle (0-59)
byte intensity = 80; //intensity of radion cycle (0-100)
  ReefAngel.FeedingModePorts = Port4Bit | Port7Bit | Port8Bit;
  ReefAngel.WaterChangePorts = Port3Bit | Port4Bit | Port5Bit | Port7Bit | Port8Bit;
  ReefAngel.WaterChangePortsE[0] = Port5Bit | Port6Bit;
  ReefAngel.LightsOnPorts = Port1Bit | Port2Bit | Port6Bit;
  ReefAngel.OverheatShutoffPorts = Port1Bit | Port2Bit | Port3Bit | Port7Bit;
  ReefAngel.Relay.On( Port1 ); //left radion
  ReefAngel.Relay.On( Port2 ); //right radion
  ReefAngel.Relay.On( Port8 ); //return
//  ReefAngel.Relay.On( Box1_Port1 ); //TBD
  ReefAngel.DosingPumpRepeat1( Box1_Port7 );
  ReefAngel.DosingPumpRepeat2( Box1_Port8 );
   /* Radion custom curve
    For testing:
    ReefAngel.RF.SetChannel( Radion_White, PWMParabola(10,0,21,0,0,75,0) );
    ReefAngel.RF.SetChannel( Radion_RoyalBlue, PWMParabola(8,0,22,0,0,100,0) );
    ReefAngel.RF.SetChannel( Radion_Red, PWMParabola(11,30,21,0,0,20,0) );
    ReefAngel.RF.SetChannel( Radion_Green, PWMParabola(12,0,19,0,0,30,0) );
    ReefAngel.RF.SetChannel( Radion_Blue, PWMParabola(9,0,21,0,0,45,0) );
    ReefAngel.RF.SetChannel( Radion_Intensity, PWMParabola(8,0,22,0,0,100,0) );
    ReefAngel.RF.SetChannel( Radion_RoyalBlue, MoonPhase() );
    ReefAngel.RF.SetChannel( Radion_White, PWMParabola(starthr+2,startmin,endhr-1,endmin,0,intensity*.75,0) );
    ReefAngel.RF.SetChannel( Radion_Red, PWMParabola(starthr+3,startmin+30,endhr-1,endmin,0,intensity*.2,0) );
    ReefAngel.RF.SetChannel( Radion_Green, PWMParabola(starthr+4,startmin,endhr-3,endmin,0,intensity*.3,0) );
    ReefAngel.RF.SetChannel( Radion_Blue, PWMParabola(starthr+1,startmin,endhr-1,endmin,0,intensity*.45,0) );
    /* Radion moon cycle
      Currently controls RoyalBlue.  If normal daylight, run defined parabola based on start and end radion cycle parameters (aka day cycle).  If after hours, run moonlight.
    if ( (hour() < starthr && (minute() < startmin || startmin == 0) ) || (hour() > endhr && minute() > endmin) ) // If time time is before or after normal daylight cycle
      ReefAngel.RF.SetChannel( Radion_RoyalBlue, 100 ); // Run moonphase on RoyalBlue
      ReefAngel.RF.SetChannel( Radion_Intensity, MoonPhase() );
    else // Or else...
      ReefAngel.RF.SetChannel( Radion_Intensity, PWMParabola(starthr,startmin,endhr,endhr,0,intensity,0) );
      ReefAngel.RF.SetChannel( Radion_RoyalBlue, PWMParabola(starthr,startmin,endhr,endmin,0,intensity,0) ); // Run day cycle parabola
      ReefAngel.Relay.On(Port4); // And turn on the Vortech
    if ( second()==0 ) ReefAngel.RF.RadionWrite();
  /* Auto feeding mode starts.
   Feeder set for 17:30, start feeding mode at 17:25. */
  if ( hour() == 17 && minute() == 25 && second() ==0 ) //if time is 17:25:00
    ReefAngel.FeedingModeStart(); //start feeding mode
  // Run Vortech during day only.  Vortech is on from 09:00-20:00.
  ReefAngel.StandardLights(Port4,9,0,20,0);
  // If in water change mode, turn on the light in the cabinet (so I can see!)
  if (ReefAngel.DisplayedMenu==WATERCHANGE_MODE) ReefAngel.Relay.On(Port6);
  /* Water level ATO
     Using memory locations:
     Location 258 (ATO Level Min Value)
     Location 259 (ATO Level Max Value)
     **NOTE: I am using the memory locations used on the PWM expansion module, so if you
     are using the PWM expansin module, I recommend you use another memory location.
     If the current water level is below the ATO Level Min Value, top off until
     you reach ATO Level Max Value, else don't.
     Also, if the current water level falls below the measureable amount (0) turn off
     the return and skimmer.
  ReefAngel.WaterLevelATO(Port5,30,InternalMemory.read(258),InternalMemory.read(259));
/* Old ATO script
  if (ReefAngel.WaterLevel.GetLevel()<topofflevel)
     topofflevel=InternalMemory.read(259);
     ReefAngel.Relay.On(Port5);
     topofflevel=InternalMemory.read(258);
     ReefAngel.Relay.Off(Port5);
  // If water level equals 0, turn off return relay; else, keep it on
  if (ReefAngel.WaterLevel.GetLevel()==0)
     ReefAngel.Relay.Off(Port7);
     ReefAngel.Relay.Off(Port8);
     ReefAngel.Relay.On(Port8);
     if (ReefAngel.WaterLevel.GetLevel()<(InternalMemory.read(259)+2) && ReefAngel.WaterLevel.GetLevel()>(InternalMemory.read(259)-10))
       ReefAngel.Relay.DelayedOn( Port7 );
  ReefAngel.Portal( "alexwbush" );
  int m,d,y;
  int yy,mm;
  long K1,K2,K3,J;
  double V;
  byte PWMvalue;
  m = month();
  d = day();
  y = year();
  yy = y-((12-m)/10);
  mm = m+9;
  K2 = 30.6*mm+.5;
  J = K1+K2+d+59-K3;
  V -= floor(V);
  if (V<0) V++;
  byte x = 6;
  byte y = 2;
  byte t;
  byte radionchannel=0;
  byte radiontext=0;
  byte radioncolor=0;
  char text[7];
  /* Drawing this:
   01/01/12 00:00:00 AM
   Disp 79.9  pH     8.00
   Sump 79.9  Sal    0.60
   Room 77.7  WL     43
   1 2 3 4 5 6 7 8
   1 2 3 4 5 6 7 8
   Moon Waning Crescent
   Intensity 88%
   Sunrise   06:15
   Sunset    18:12
  /* Colors used in this script:
     DefaultFGColor   - For basic font and line
     DefaultBGColor   - For background color
     PHColor          - For values that may change
     OutletOnBGColor  - For okay water level
     OutletOffBGColor - For low water level
     To change colors, modify these values in ReefAngel_CustomColors.h file
  ReefAngel.LCD.DrawDate(6, 2);
  ReefAngel.LCD.Clear(DefaultFGColor, 1, 11, 128, 11);
  //ReefAngel.LCD.DrawText(fcolor,bcolor,x,y,"text");
  //Line 1 - Display Temp & pH
  x = 8;
  y = 15;
  ReefAngel.LCD.DrawText(DefaultFGColor,DefaultBGColor,x,y,"Disp");
  x += 30;
  ReefAngel.LCD.DrawSingleMonitor(ReefAngel.Params.Temp[T1_PROBE], PHColor, x, y, 10);
  x = 70;
  ReefAngel.LCD.DrawText(DefaultFGColor,DefaultBGColor,x,y,"pH");
  x += 30;
  ReefAngel.LCD.DrawSingleMonitor(ReefAngel.Params.PH, PHColor, x, y, 100);
  //Line 2 - Sump & Salinity
  x = 8;
  y += 10;
  ReefAngel.LCD.DrawText(DefaultFGColor,DefaultBGColor,x,y,"Sump");
  x += 30;
  ReefAngel.LCD.DrawSingleMonitor(ReefAngel.Params.Temp[T2_PROBE], PHColor, x, y, 10);
  x = 70;
  ReefAngel.LCD.DrawText(DefaultFGColor,DefaultBGColor,x,y,"Sal");
  x += 30;
  ReefAngel.LCD.DrawSingleMonitor(ReefAngel.Params.Salinity, PHColor, x, y, 10);
  //Line 3 - Room
  x = 8;
  y += 10;
  ReefAngel.LCD.DrawText(DefaultFGColor,DefaultBGColor,x,y,"Room");
  x += 30;
  ReefAngel.LCD.DrawSingleMonitor(ReefAngel.Params.Temp[T3_PROBE], PHColor, x, y, 10);
  x = 70;
  ReefAngel.LCD.DrawText(DefaultFGColor,DefaultBGColor,x,y,"WL");
  x += 30;
  ReefAngel.LCD.DrawSingleMonitor(ReefAngel.WaterLevel.GetLevel(), PHColor, x, y, 1);
  //Lines 4 and 5 - Relays
  x = 12;
  y += 12;
  // draw main relay
//  ReefAngel.LCD.DrawOutletBox(x, y, TempRelay);
  ReefAngel.LCD.DrawCircleOutletBox(x, y, TempRelay);
  y +=12;
  // Relay Expansion
  ReefAngel.LCD.DrawOutletBox(x, y, TempRelay );
  //Line 3 - Sunrise
  x = 8;
  y += 18;
  ReefAngel.LCD.DrawText(DefaultFGColor,DefaultBGColor,x,y,"Sunrise");
  x += 50;
  ReefAngel.LCD.DrawText(PHColor,DefaultBGColor,x,y,starthr);
  if(starthr<10) x-=6;
  x += 12;
  ReefAngel.LCD.DrawText(PHColor,DefaultBGColor,x,y,":");
  x += 5;
  if(startmin<10)
    ReefAngel.LCD.DrawText(PHColor,DefaultBGColor,x,y,"0");
    x+=6;
  ReefAngel.LCD.DrawText(PHColor,DefaultBGColor,x,y,startmin);
  //Line 4 - Sunset
  x = 8;
  y += 10;
  ReefAngel.LCD.DrawText(DefaultFGColor,DefaultBGColor,x,y,"Sunset");
  x += 50;
  ReefAngel.LCD.DrawText(PHColor,DefaultBGColor,x,y,endhr);
  if(endhr<10) x-=6;
  x += 12;
  x += 5;
  if(endmin<10)
    x+=6;
  ReefAngel.LCD.DrawText(PHColor,DefaultBGColor,x,y,endmin);
  if (second()==0 || second()==30)
    //Draw Radion Coloration
    ReefAngel.LCD.Clear(COLOR_WHITE,0,100,130,130);
    x=0;
    y=120;
    while(radionchannel<=5)
      if(radionchannel==0) radioncolor=255; //white
      if(radionchannel==1) radioncolor=37; //royalblue
      if(radionchannel==2) radioncolor=224; //red
      if(radionchannel==3) radioncolor=28; //green
      if(radionchannel==4) radioncolor=3; //blue
      if(radionchannel==5) radioncolor=252; //yellow(intensity)
      y=128-(ReefAngel.RF.GetChannel(radionchannel)*.15);
      ReefAngel.LCD.Clear(radioncolor,x,y,x+21,130);
      radiontext=x+2;
      if(radionchannel==0) ReefAngel.LCD.Clear(COLOR_BLACK,x,y,x+21,y);
      if(ReefAngel.RF.GetChannel(radionchannel)<100)
        radiontext=x+6;
      if(ReefAngel.RF.GetChannel(radionchannel)<10)
        radiontext=x+8;
      ReefAngel.LCD.DrawText(DefaultFGColor,DefaultBGColor,radiontext,y-8,ReefAngel.RF.GetChannel(radionchannel));
      x+=22;
      radionchannel+=1;
You don't need the MoonPhaseLabel function. It's in the libraries now. I just checked my code and I'm using that function and do not have it defined. Try taking it out.