Time for a beer, my head is throbbing... If only I had known the difference between float and byte earlier.
Roberto, thanks for answering that question so quick...
ReEfnWrX
That is good to know..lnevo wrote:Usually you dont want to do that because floats take up 4-8 times as much mem as a byte...so if you do try and keep it to the variables that need it...
so would you use (float) before the entire formula that ends with a decimal result you want to keep for further formulas?
or would you only designate (float) before a variable in a formula that you want to use its decimal value instead of its byte like this
byte acclFactorWhite=(acclDay*(float)acclPercentPerDayWhite);
Try it in front of the variable that isn't a float in the equation you wrote earlier where you were losing the precision.
AcclFactor needs to be a float since we want to store a decimal there..just saw that in your example.
ReEfnWrX
So I have something very interesting happening....
float Test=43/30;
is being computed to 1.00 and not 1.43
any idea???
float Test=43/30;
any idea???
Use the (float) in front of one of the numbers. You can also change one to 43.0 and/or 30.0. Floating point math in C is annoying sometimes..
ReEfnWrX
I am trying to reduce my formulas to only have one float variable for each channel to save memory... but I keep running into situation where its not giving the decimals like mentioned above
Will (float)only affect the number directly in front of it?
or can I do (float)(43.0/30.0)
to have it affect that part of the formula instead of just one number?
From http://arduino.cc/en/Reference/Float
That page may have more information to help you figure this part out..it's confusing for sure. But here's a relevant excerpt.
Example Code
int x;
int y;
float z;
x = 1;
y = x / 2; // y now contains 0, ints can't hold fractions
z = (float)x / 2.0; // z now contains .5 (you have to use 2.0, not 2)
89delta
Great work ReEfnWrX. Am completely lost though on the coding for this and how to implement it within the Weather Simulation for PWM ModuleSketch i'm using currently. I have it modified though to allow for changing of the settings via bluetooth and serial monitor if needed.
Would it be possible for you to kick me in the right direction on how to merge your coding into this one i'm using.
Martin
Martin
ReEfnWrX
I've never looked at the weather sim coding...It shouldn't be difficult. all my coding does is create a formula to calculate your max% for each channel.
so you should be able to merge them together, by adding my formulas where they need to go. Then just make sure in your ReefAngel.PWM.SetChannel code, where you input your start% and End % values, just change that to my variables startPercet and endPercentWhite endPercentBlue
I believe in the latest code that rufessor added a time limit so that the photoperiod could be constrained to a number of hours. Technically you can modify the percents or you could modify this field and change the range to whatever you want.
89delta
One thing I can't do is use ReefAngel.PWM.SetActinic(ActinicPWMValue);ReefAngel.PWM.SetDaylight(DaylightPWMValue) or ReefAngel.PWM.SetChannel( 0, PWMSlope(13,0,21,0,startPercent,endPercentWhite,90,20) ); within my current code as there isn't anything in there like that.
Here's what I have:
Here's what I have:
//By Matthew Hockin 2012.
//SWFLTEK library functions, #includes, and #define were copied directly from the Epherma library
//Epherma (SWFLTEK.com) was written by Michael Rice- thanks Michael it works great.
//If you copy from this (its all open source) please
//acknowledge Michael for SWFLTEK library code (obviously labeled) or Matthew Hockin (for the rest).
#include <avr/wdt.h>
#include <stdlib.h>
#include <math.h>
//***********************************ARRAYS YOU MUST MODIFY TO MAKE YOUR TANK SET UP WORK*****************************
//YOU MUST READ EVERY WORD IN THIS SECTION IN ORDER TO APPROPRIATELY CONFIGURE THIS PROGERAM- READ EVERY LINE BELOW///
byte ChMax[]={200,220,200,220,225,0,0,0};//Incremental value (Max-flicker) above flicker you want as max intensity (!!!!!!! Light Set Point is ChMax PLUS Flicker !!!!!!)
byte flicker[]={31,31,31,31,40,0,0,0};//need to input actual values here for flicker point on all channels in PWM expansion box
boolean Wchannel[]={1,0,1,0,0,0,0,0}; //use 1 to designate white channel (i.e. off during storm and used for lightning). Array corresponds to PWM channel 0-5 in order
//Array to give direction to dimming. e.g. DimOrder[]={0,0,1,1,0,0} (cloud chase effects, just group channels you want to dim together during a cloud or storm
//(which is zero or 1 will change who dims first). set them all to 0 if your tank has no left/right or front/back lights.
byte DimOrder[]={0,0,1,1,1,0,0,0};
//set all channel positions that you would like to use for the lightning strike effect to 1 (0-5 are PWM channels 6,7 are Main PWM outs)- and channels with a 0 are not used in strike
byte StrikeChannel[]={1,1,1,1,1,0,0,0};
byte MoonCh[]={0,0,0,0,1,0,0,0};//place a 1 in the array position of all lighting channels you would like to use a moon lighting (this does not preclude their use in other phases (day, storm etc)
//**********************************DONE CHANGING THINGS HERE BUT YOU MUST CHANGE ChOffset array IN CalcSUN function******
// arc-seconds per radian
#define _sec_rad 206264.806247096370813
// axial tilt of earth at epoch, in radians
#define _tilt 0.409092804222329
// tropical year in seconds... rounding error accumulates to 26 seconds by the year 2136
#define _tropical_year 31556925
// 'zenith' of rising (setting) sun in radians (360 - 2 * 90.833 degrees)
#define _zenith 3.11250383272322
//Unless your planning on editing the program DO NOT CHANGE ANYTHING HERE
long latitude, longitude;
byte TrueIntensity[8];//array used to place hold final write values for PWM intensity setting
long elapsedTime;//used multiple places as elapsed since midnight
long newDay;
unsigned long rise;//time in seconds from the year 2000 (GMT) for sunrise
unsigned long set;//time in seconds from the year 2000 (GMT) for sunrise
long CloudMaster[20];// Set up array to hold start and end times for clouds for the day-
long midDay;// exactly 1/2 way between rise and set, i.e. solar noon for latitudes <60 close enough for us...
byte PWMports[] ={
3,5,6,9,10,11};
byte ChannelValue[8];// Array to store output of insolaiton which may be modified and stored in TrueIntensity which is used to write to the PWM channels
byte cmdnum=255;
byte datanum=255;
byte dow=0;//day of week
boolean InsolationAdvance;//when true we recalculate light intensity during clear sky (every 3 seconds seems more than often enough)
//END HEADER/Global Variable declaration//
//Setup
void setup(){
Serial.begin(57600);
Wire.begin(8);
pinMode(3,OUTPUT);
pinMode(5,OUTPUT);
pinMode(6,OUTPUT);
pinMode(9,OUTPUT);
pinMode(10,OUTPUT);
pinMode(11,OUTPUT);
wdt_enable(WDTO_1S);
unsigned long seed=0, count=32;
while (--count){
seed = (seed<<1) | (analogRead(5)&1);
randomSeed(seed);//start random generator at a different point each time (not perfect but whatever its gonna be pretty damn random)
//End Setup
//Loop
void loop(){
elapsedTime=(now()-newDay);//Elapsed time is seconds from midnight of today- local processor time.
wdt_reset();
if (cmdnum!=255){
ProcessCMD(cmdnum,datanum);
cmdnum=255;
datanum=255;
if (dow!=day()){ //used to see that were in a new day and need to recalculate sunrise and sunset
CalSun();
dow=day();
if ((millis()-lastmillis)>=100){
counter+=1;
StormAdvance=true;
if (counter==0){
InsolationAdvance=true;//so that it runs on start up to provide light immediately
if (counter%30==0){
if (counter==210) counter=0;
if (InsolationAdvance==true) Insolation();//calculate clear sky solar intensity as the day advances
Weather();//run the weather overlay (cloud, storm)
if (StrikeNow==true){
byte intensity;
intensity=random(180,256);// this little bit should generate a randomly bright flash variation between the series of flashes in StrikeMaster
for (byte b=0; b<6; b++){
if (StrikeChannel[b]==1) analogWrite(PWMports[b],intensity);// set all strike channels to intensity of strike
if (StrikeCount==(StrikeNumber-1)){
StrikeNow=false;
StrikeCount=0;
for (byte a=0;a<6;a++){//using all prior mods to light intensity (Insolation-->Cloud-->Storm) lets make some light
//End Loop
//Standard PWM Functions Receive/Process
wdt_reset();
if (howMany==5){
cmd1=Wire.read();
cmd2=Wire.read();
cmd3=Wire.read();
cmd4=Wire.read();
cmd5=Wire.read();
cmdnum=cmd4;
datanum=cmd5;
//Serial.println(cmd4,DEC);
//Serial.println(cmd5,DEC);
else{
for (int a=0;a<howMany;a++){
Wire.read();
wdt_reset();
//End Standard Functions
//Start of sunrise, sunset and cloud calculations- runs on reset and once a day thereafter.
void CalSun(){
//*********************YOU NEED TO CHANGE THESE VALUES Read instructions in their ENTIRETY and CAREFULLY change to values for your tank and geographical region***************************
int Choffset[]={
-600,0,-1800,6000,0,600,-1200,6600,-2200,6600,0,0,0,0,0,0};
// NOW SET YOUR LATIDTUDE AND LONGITUDE COORDINATES as Degrees, Minutes, Seconds of Lat and Lon
//If Your NORTH of the equator your LONGITUDE must START with a NEGATIVE number (the rest are positive) e.g. All of North America, Europe, Russia etc are negative
//If Your EAST of the Prime Meridian your LATITUDE must START with a NEGATIVE number (the rest are positive), e.g. Most of Europe, All of China, India, Austraila, Russia etc are negative
latitude=dmsToSeconds(40,44,00);//United States of America- Salt Lake City, local time is -7 hours GMT
longitude=dmsToSeconds(-111,47,00);
//**********************ok now were done changing things IF YOU CHANGED the Top part of the GLOBAL variable decleration AND this... your FULLY configured and ready to load********************************************
if (dow==0){//if the controller has resarted we need to find midnight
long hours, minutes;//store current elapsed local hours as total seconds from midnight
time_t t=now();//store current clock time to parse
hours=hour(t);
hours=(hours*3600);//current hour number 0-23 as seconds
minutes=minute(t);
minutes=(minutes*60);//minutes of current hour as seconds
newDay=now();
newDay-=(hours+minutes);//Convert current local unix epoch time to local unix epoch time of midnight
else if (dow!=0){//if we did not restart but the day is new then it is midnight and were good to go..
newDay=now();
//#define SECS_YR_2000 (946684800) the time at the start of y2k (need to subtract from unix epoch time to bring to Y2K origin
newDay-=946684800;//convert GMT unix Epoch to seconds elasped since 2000 for GMT midnight of today
rise=newDay;//set value to send to SunRise as midnight GMT in seconds from Y2K
set=newDay;//
//Calculate rise time and set time using Epherma Library functions (see end of code)
SunRise(&rise);//call to Epherma function
SunSet(&set);//Call to Epherma functionunsigned long newDay;
/*Serial.print("rise and set= ");
Serial.println(rise);
Serial.println(set);
Serial.print("newDay as seconds since 2000 to todays midnight= ");
Serial.println(newDay);*/
rise=(rise-newDay);// set to elapsed seconds of day
set=(set-newDay);
/*Serial.print("rise and set as elapsed seconds of day= ");
Serial.println(set);*/
newDay+=946684800;//Convert newDay back to unix epoch GMT midnight today (used in loop to determine how far we are into the day)
/*Serial.print("newDay as seconds since since 1970 to todays midnight= ");
Serial.print("elapsed is");
long elapsed=now()-newDay;
Serial.println(elapsed);*/
midDay=(((set-rise)/2)+rise);
if (b%2==0){
ChRiseSet[b]=rise+(Choffset[b]);
ChSlope[b]=(deltaY/(float)(HalfDayLength-(Choffset[b])));
else if (b%2==1){
ChRiseSet[b]=set+(Choffset[b]);
ChSlope[b]=(deltaY/(float)(HalfDayLength+(Choffset[b])));
byte RainMaker=random(1,101);
if (RainMaker<=CloudChance){
return;
long dayLength=0;
for (byte a=1;a<16;a=(a+2)){//determine maximum day length given light on tank that is not moon light, this will yield night clouds and storms (and a storm after dark is severe... always
if (a==0){
if (((set+Choffset[a])-rise)>(set-rise)){
dayLength=((set+Choffset[a])-rise);
else dayLength=(set-rise);
else if (a!=0){
if (dayLength<((set+Choffset[a])-rise)){
byte CloudsMax=10;//DONT INCREASE BEYOND 10 or it will DIE, or increase array size to handle it (among other things)
byte CloudsMin=4;//use 2 as a minimum
Overcast=(Overcast/100);
// split the total lenght of time for clouds into equal segments and then to randomly chop or add time to the
//segments such that cloud length is variable. Then distribute into random parts of the day and fill array with start,duration pairs for clouds
int CloudLength;
float CloudFraction=0;
float SunFraction=0;
for (byte a=0; a<20; a++){
CloudMaster[a]=0;
if (a%2==0){
if (b==0){
if (a==0){
else if (a<((CloudsTotal*2)-2)){
b++;
else if (a==((CloudsTotal*2)-2)){
SunFraction=(2-((float)CloudMaster[0]/(float)SunSegment));
else if (b==1){
if (c==0){
c++;
else if (c==1){
for (byte a=0;a<20;a++){
//reframe array to generate cloud start, cloud end, cloud start, cloud end
else {
/*Serial.println("here is cloud master in is entirety as start and end pairs");
if (a%2==0){
Serial.print("Start time=");
else {
Serial.print("End time=");
}//END SunCalc FUNCTION
void Insolation()
use flicker points to adjust minimum intensity to stable light. Turn off lights after set or before rise etc.
if (elapsedTime<=midDay){
byte c=0;//loop counter
for (byte b=0;b<16;b=(b+2)){
if (elapsedTime>=ChRiseSet[b]){
secSoFar=(elapsedTime-ChRiseSet[b]);//just account for length of every channel 1/2 day and switch at midDay
ChannelValue[c]=flicker[c]+ChMax[c]*(-cos(PiHalf+(ChSlope[b]*secSoFar)));
if (MoonCh[c]==1){
byte MoonToday=MoonPhase()*0.5;//SCALE FACTOR to DIM moon setting for use with HIGH power LED as moon light
if (MoonToday==0) ChannelValue[c]=0;
else if (MoonToday<flicker[c]) ChannelValue[c]=flicker[c];
else ChannelValue[c]=MoonToday;
else if (MoonCh[c]==0){
ChannelValue[c]=0;//its dark and this is not a moon phase channel
c++;//index by one so we count 0-7 as b goes 0-14 by twos
else if (elapsedTime>midDay){
for (byte b=1;b<16;b=b+2){
ChannelValue[c]=flicker[c]+ChMax[c]*(-cos(Pi+(ChSlope[b]*secSoFar)));
if (MoonCh[c]==1){
c++;//index to count 0-7 as b counts 1-15 by twos.
}//END function
//WEATHER FUNCTION BEGIN
void Weather ()
static byte loopCount;
static float PriorCloudCover; //used to "delay" one side of the tank from the other in cloud passing effects
static long StormStart;
static long StormEnd;
static long CloudEnd;
static byte Severity;
static int StepSize;
static int LastStepSize;
if (Cloud==false){
//Write Insolation values to TrueIntensity so the loop will pick them up and the cloud/storm will get the right data (since intensity changes during the day)
for (byte a=0; a<8; a++){//this must be above the next loop
//Serial.print("We started a cloud and its end is=");
//Serial.println(CloudEnd);
CloudCover=CloudStart(CloudMaster[a]);//CloudStart modifies TrueIntensity to get us to 50% intensity at the start of the cloud effect and also sets cloud=true to bypass this
Counter=0;
loopCount=1;
LastStepSize=0;//zero out cloud random walk variables
StepSize=0;//zero out cloud ranodm walk variables
return;//exit having started a cloud in CLoudStart routine called above
return;
if (elapsedTime>=CloudEnd){
return;
/*Use fractional intensity to set minimum value for any channel. Dimming is proportional to actual intensity output
and constrained by flicker point. Random walk uses static variable "CloudCover" constrained to 0-100 to represent fractional intensity (i.e. (1-(CloudCover/100))*Insolation SetPoint
if (loopCount==1){
PriorCloudCover=CloudCover; //e.g. PriorCloudCover=CloudCover with no float math to screw things up
LastStepSize=StepSize;
StepSize=(random(5,21));// in Percent% (0-100) This is how much light intensity will change over the loop count interval (this actual time is dependent upon the call frequency of StromAdvance as set in the loop)
if ((random(0,2)!=1)) StepSize=-(StepSize);
if ((CloudCover+StepSize)>=100){//cannot shut off lights more than 100% so limit here
StepSize=(100-CloudCover);//
Counter++;
else if ((CloudCover+StepSize)<=0){//cannot be brighter than 100% so since were in a cloud dont "limit" it but reflect it back down
if (Counter>=50) Counter-=random(-1,2);//since we got bright... lets further delay and randomize storm occurence
CloudCover=CloudCover+StepSize;
if ((Counter>=60) && ((CloudEnd-elapsedTime)>=300)) {//if Counter (indexes when cloud cover reaches 100) has accumulated and we still have time lets make a storm
if (StormCount>=1){//if we can have storms in this cloud (random- statisticly 1/3 clouds = no storm, 1/3 = 1 possible storm, 1/3 = 2 possible storms)
byte RandomStorm;
RandomStorm=random(0,11);//this randomizes for longer clouds without storm, avg cloud is much longer prior to storm occuring- thus short clouds will not generally have a storm
if (RandomStorm>=4){
StormCount-=1;//count down by 1 the number of storms in this cloud- this will not roll the byte since the loop requires it to be at least 1 to ever subtract here.
Counter=0;//reset this variable since Storm loop uses it as well.
Severity=StartStorm(LongestStorm, IsStorm, StormEnd);
loopCount=1;//reset counting loop for the storm
else if ((Counter>=60) && ((CloudEnd-elapsedTime)<300)){
Counter=0;//just reset the counter (does not really matter in this case but its clean)
for (int a=0;a<8;a++){
if (ChannelValue[a]==0) TrueIntensity[a]=0;// if were in an evening storm dont reset intensity (it would go to flicker point and possibly flicker)
else if (DimOrder[a]==0){
TrueIntensity[a]=(flicker[a]+(((float)(ChannelValue[a]-flicker[a]))*(1-((CloudCover-(StepSize-(StepSize/4)*loopCount))/100))));
else if (DimOrder[a]==1){
TrueIntensity[a]=(flicker[a]+(((float)(ChannelValue[a]-flicker[a]))*(1-((PriorCloudCover-(LastStepSize-(LastStepSize/4)*loopCount))/100))));
loopCount++;
if (loopCount>4) loopCount=1;
return;
IsStorm=false;
Counter=0;
return;
if (loopCount==1){
Counter++;
if (Counter>=2) Counter-=random(0,2);//since we got bright... lets further delay and randomize strike occurence
if (Counter>(Severity+2)) Counter=0;//allow if to accumulate on ocassion to train strike sequences 2-3 in a row but then dump it
if ((Counter>=(Severity+random(-1,4))) && (StrikeNow==false)) {//this is where a storm is triggered. Counter indexes when cloud cover reaches 100 on the random walk
byte RandomStriker;
RandomStriker=random(1,11);
if (RandomStriker>4){
if (a>=(StrikeNumber*2)){
StrikeMaster[a]=0;
if (a%2==0){
if (a==0){
StrikeMaster[a]=random(300,1601);//no need for random here but I am leaving it since I wrote it that way. This must be independent from a=2,4,6 etc...
else {
StrikeMaster[a]=(StrikeMaster[(a-2)]+random(200,1401));//position 0,2,4,6,8.. is strike delay
else if(a%2!=0){
StrikeMaster[a]=random(50,110);//position 1,3,5,7,9... is strike duration (I tried real lightning strike durations and its too short this is adjusted for visual effect
StrikeCount=0;
Counter=0;
if (Severity>5){
for (int a=0;a<8;a++) {
else if (Wchannel[a]==1){//if were in a storm but not a severe storm constrain whites to 50% of Insolation intensity
TrueIntensity[a]=(flicker[a]+((((float)(ChannelValue[a]-flicker[a])/4))*(1-((CloudCover-(StepSize-(StepSize/3)*loopCount))/100))));
TrueIntensity[a]=(flicker[a]+((((float)(ChannelValue[a]-flicker[a])/4))*(1-((PriorCloudCover-(LastStepSize-(LastStepSize/3)*loopCount))/100))));
TrueIntensity[a]=(flicker[a]+(((float)((ChannelValue[a]-flicker[a])))*(1-((CloudCover-(StepSize-(StepSize/3)*loopCount))/100))));
TrueIntensity[a]=(flicker[a]+((((float)(ChannelValue[a]-flicker[a])))*(1-((PriorCloudCover-(LastStepSize-(LastStepSize/3)*loopCount))/100))));
else if (Severity<=5){// severe storms occur throughout the day, but EVERY storm after sunset is severe...
else if (Wchannel[a]==1){//if were white we need to be off in a storm
TrueIntensity[a]=0;
else if (ChannelValue[a]==0){//if this light channel is dark... e.g. after sunset for this channel- it produces no cloud effect
TrueIntensity[a]=0;
else if (Wchannel[a]==0){//if were not shut off in a strom and not after our daylight period (this channel) then we produce storm light sequences.
if (DimOrder[a]==0){//if we dim first... do it
else if (DimOrder[a]==1){//else we dim second
}//end of CWHchannel==0 being true
}//end of for loop in severity <5 == true loop
}//end severity compairson loop no more else statements
loopCount++;
if (loopCount>3) loopCount=1;
}//end of storm if loop
}//End Weather function
//CloudStart drops light intensity to 50% of whatever daylight setting is to start the cloud at 50
int CloudStart(long StartTime){
byte elapsed;
elapsed=(elapsedTime-StartTime);//counts up since we start this at elapsedTime=StartTime and StartTime is fixed
TrueIntensity[a]=(flicker[a]+(((float)((ChannelValue[a]-flicker[a])))*(1-(elapsed*2.5)/100)));
if (elapsed>=20);
Cloud=true;//start the cloud
return 50;//set CloudCover to 50
}//end CloudStart function
//StartStorm sets up duration and severity of storm. Its currently limited to 90-600 sec in length- it will rarely be lower than 3 minutes
byte StartStorm(int MaxLength, boolean& trigger, long& EndTime){
byte LightningIntensity;
int StormDuration;
MaxLength-=120;//remove 2 mins from longest storm so that we end up with 2 minutes of cloud after the storm before the sky clears to daylight
if (MaxLength>720){
MaxLength=720;//modify local variable
StormDuration=random((MaxLength/3),(MaxLength+1));
EndTime=(elapsedTime+StormDuration);//Set by reference StormEnd static variable in weather
else {
StormDuration=random((MaxLength/2),(MaxLength+1));
if (elapsedTime<midDay){
LightningIntensity=random(3,11);//morning storms are generally less severe
else if (elapsedTime>midDay){//afternoon storms are more likely to be severe (every 10-15 sec or less) to about once in a minute or maybe less
if (elapsedTime>(set-rise)){//Storms after sunset are always severe... it just looks too cool!
LightningIntensity=3;
else {
LightningIntensity=random(3,8);
trigger=true;
return (LightningIntensity);
//End Storm Start Function
//Similar to Cloud start but in reverse... now ramp intensity from wherever we were at the end of the cloud to the value set by Insolation
void ClearSky(int CloudPercent, long TerminationTime)
byte elapsed=(elapsedTime-TerminationTime);//Counts up from the scheduled end of the cloud in seconds
float slope=(CloudPercent/30);//Just calculate how much to increment every second to go from CloudCover to clear sky (CloudCover of zero)
float LightAdvance;
LightAdvance=(CloudPercent-(slope*elapsed));//were reducing CloudCover from start to zero over 10 seconds.
TrueIntensity[a]=(flicker[a]+(((float)(ChannelValue[a]-flicker[a]))*(1-(LightAdvance/100))));
if (elapsed>=30){//at this point lights are back to full Insolation setting so cancel the cloud and start waiting for the next one
Cloud=false;//stop the cloud we are now outside of a true condition in the if loop so it will now stay false and lights are back on
IsStorm=false;//just to be redundant this is not called from a storm...
}//End Clear Sky function
byte MoonPhase()
int m,d,y;
int yy,mm;
long K1,K2,K3,J,V;
byte PWMvalue;
m = month();
d = day();
y = year();
yy = y-((12-m)/10);
mm = m+9;
if (mm>=12) mm -= 12;
K1 = 365.25*(yy+4712);
K2 = 30.6*mm+.5;
J = K1+K2+d+59-K3;
V -= int(V/100)*100;
V = abs(V-50);
PWMvalue = 4*abs(50-V); // 5.12=100% 4=~80%
//pinMode(lowATOPin,OUTPUT);
//return (PWMvalue*100)/255; //output is 0-100
return PWMvalue;//output is 0-255
// A big thank you for these library functions. Its great!
//convert degrees to seconds of arc
// decimal degrees
long ddToSeconds(float dd){
return dd * 3600.0;
//Degrees, minutes, seconds
long dmsToSeconds(int d, unsigned char m, unsigned char s){
long ret;
ret = labs((long)d);
ret = ret * 3600L + 60L * m + s;
ret = (d<0L) ? -ret : ret;
return ret;
'Equation of Time'
We use the 'short form equation, which has a theoretical accuracy of about 40 seconds.
The returned value is in seconds.
int equation_of_time(unsigned long dt){
double t;
dt -= 192540UL; // refer to Jan 3 2000 05:29 (first periapsis)
dt %= _tropical_year;
t = dt;
t /= _tropical_year;
t *= 6.283185307179586;
t = -459.27672 * sin(t) + 575.333472 * sin(2.0 * t + 3.588414);
return t;
'Solar Noon' adjusts the passed time stamp to the time (GMT) of local solar noon.
The accuracy is about 40 seconds (set by the equation of time).
void SolarNoon(unsigned long * dt){
long r;
// Set stamp to noon GMT
*dt /= 86400UL;
*dt *= 86400UL;
*dt += 43200UL;
// adjust for equation of time, at noon GMT
*dt -= equation_of_time(*dt);
// rotate to our longitude
r = longitude / 15L;
*dt -= r;
'Solar Declination'
Returns declination in radians
Accurate to within 50 arc-seconds
double SolarDeclination(unsigned long dt){
double y;
y = dt;
y /= _tropical_year; // fractional year
y *= 6.283185307179586;
y=0.006918-0.399912*cos(y)+0.070257*sin(y)-0.006758*cos(y*2)+0.000907*sin(y*2)-0.002697*cos(y*3)+0.00148*sin(y*3);
return y;
Return the period between sunrise and sunset, in seconds.
At high latitudes around the time of the solstices, this could be zero, or all day.
unsigned long daylightseconds(unsigned long dt){
float l, d, e;
long n;
d = -SolarDeclination(dt); // will be positive in Northern winter
l = latitude / _sec_rad; // latitude in radians
e += 60.0 * l * tan(l + d); // latitudinal error
d = tan(l) * tan(d); //
if(d>1.0) return 86400UL;
if(d < -1.0) return 0UL;
d = acos(d);
d /= _zenith;
n = 86400UL * d;
n += e;
return n;
Modify the passed time stamp to the time of sunrise (or sunset if 'set' is non-zero).
Returns 0 to signal 'normal' completion. If the position is in a polar circle, 1 will be
returned if the sun is above the horizon all day, and -1 if the sun is below the horizon
all day.
char SunRiseSet(unsigned long * dt, char set){
unsigned long daylen;
daylen = daylightseconds(*dt);
if(daylen == 86400UL) return 1; // there is no 'night' today (midnight sun)
if(daylen == 0UL) return -1; // there is no 'day' today
*dt /= 86400UL;
*dt *= 86400UL;
*dt += 43200UL; // set the time stamp to 12:00:00 GMT
*dt -= daylen / 2; // sunrise at the prime meridian
if(set) *dt += daylen; // sunset at the prime meridian
//*dt -= longitude / 15.0; // rotate to our own meridian
return 0;
// 'short' forms of SunRiseSet
char SunRise(unsigned long* when){
return SunRiseSet(when, 0);
char SunSet(unsigned long* when){
return SunRiseSet(when, 1);
89delta
So I believe I have figured out how to use the acclimation code with with the dimming expansion module. Since I no longer have a working board I was hoping someone would be willing to look it over and possibly give it a try. Am planning on full-spectrum LED build but still unsure of using 5-6 channels. I will post code tomorrow.
89delta
So I used the memory locations that are available through the RA Status app in hopes I can dial in the correct color combination.
#include <WiFiAlert.h>
#include <SunLocation.h>
#define NUMBERS_8x16
// Place global variable code below here
////// Memory Locations used by all formulas
#define Mem_B_AcclDay 100
// Note - 100 represents the hard coded Memory location used for this variable
// not the value for the variable.
// This variable represents the current day in Acclimation Cycle. Set this value to the same
// number of days as your AcclDuration to begin the acclimation cycle or set it to 0 to use
// your normal dimming end% values.
#define Mem_B_AcclDuration 101
// Set this value to how many days you want your acclimation cycle to take.
#define Mem_B_SlopeStart 102
// Set this to your desired starting acclimation end%.
// Place your custom code below here
/////// LED Dimming Acclimation Cycle and your standard LED schedule
////////// Variables used for all channels
byte acclDay = InternalMemory.read(Mem_B_AcclDay);
// What day in the acclimation cycle it is
byte acclDuration = InternalMemory.read(Mem_B_AcclDuration);
// Acclimation Duration in days
byte startPercent = InternalMemory.read(Mem_B_SlopeStart);
// Normal start% being used by all 6 channels
randomSeed(now()/SECS_PER_DAY);
//if (InternalMemory.read(Mem_B_ResetMemory))
//init_memory();
////////// PWM Expansion Channel 0 Variables
byte acclStartEndCh0 = InternalMemory.read(Mem_B_PWMSlopeStart0);
// Starting End% for Acclimation cycle
float acclendPercentCh0 = InternalMemory.read(Mem_B_PWMSlopeEnd0);
// Your target Expansion Channel 0 end% once acclimation is complete
////////// PWM Expansion Channel 0 Formula
float acclPercentPerDayCh0 = (acclendPercentCh0 - acclStartEndCh0) / acclDuration;
// How much your Expansion Channel 0 end% rises per acclimation day
float acclFactorCh0 = acclDay * acclPercentPerDayCh0;
// endPercentCh0 will be offset by this much. If acclDay = 0 then this value will be 0
byte endPercentCh0 = acclendPercentCh0 - acclFactorCh0;
// Your final Expansion Channel 0 end% for the day
////////// PWM Expansion Channel 1 Variables
byte acclStartEndCh1 = InternalMemory.read(Mem_B_PWMSlopeStart1);
float acclendPercentCh1 = InternalMemory.read(Mem_B_PWMSlopeEnd1);
// Your target Blue end% once acclimation is complete
////////// PWM Expansion Channel 1 Formula
float acclPercentPerDayCh1 = (acclendPercentCh1 - acclStartEndCh1) / acclDuration;
// How much your Blue end% rises per acclimation day
float acclFactorCh1 = acclDay * acclPercentPerDayCh1;
// endPercentBlue will be offset by this much. If acclDay = 0 then this value will be 0
byte endPercentCh1 = acclendPercentCh1 - acclFactorCh1;
// Your final Blue end% for the day
////////// PWM Expansion Channel 2 Variables
byte acclStartEndCh2 = InternalMemory.read(Mem_B_PWMSlopeStart2);
float acclendPercentCh2 = InternalMemory.read(Mem_B_PWMSlopeEnd2);
////////// PWM Expansion Channel 2 Formula
float acclPercentPerDayCh2 = (acclendPercentCh2 - acclStartEndCh2) / acclDuration;
float acclFactorCh2 = acclDay * acclPercentPerDayCh2;
byte endPercentCh2 = acclendPercentCh2 - acclFactorCh2;
////////// PWM Expansion Channel 3 Variables
byte acclStartEndCh3 = InternalMemory.read(Mem_B_PWMSlopeStart3);
float acclendPercentCh3 = InternalMemory.read(Mem_B_PWMSlopeEnd3);
////////// PWM Expansion Channel 3 Formula
float acclPercentPerDayCh3 = (acclendPercentCh3 - acclStartEndCh3) / acclDuration;
float acclFactorCh3 = acclDay * acclPercentPerDayCh3;
byte endPercentCh3 = acclendPercentCh3 - acclFactorCh3;
////////// PWM Expansion Channel 4 Variables
byte acclStartEndCh4 = InternalMemory.read(Mem_B_PWMSlopeStart4);
float acclendPercentCh4 = InternalMemory.read(Mem_B_PWMSlopeEnd4);
////////// PWM Expansion Channel 4 Formula
float acclPercentPerDayCh4 = (acclendPercentCh4 - acclStartEndCh4) / acclDuration;
float acclFactorCh4 = acclDay * acclPercentPerDayCh4;
byte endPercentCh4 = acclendPercentCh4 - acclFactorCh4;
////////// PWM Expansion Channel 5 Variables
byte acclStartEndCh5 = InternalMemory.read(Mem_B_PWMSlopeStart5);
float acclEndPercentCh5 = InternalMemory.read(Mem_B_PWMSlopeEnd5);
// Your target White end% once acclimation is complete
////////// PWM Expansion Channel 5 Formula
float acclPercentPerDayCh5= (acclEndPercentCh5 - acclStartEndCh5) / acclDuration;
// How much your White end% rises per acclimation day
float acclFactorCh5 = acclDay * acclPercentPerDayCh5;
// endPercentWhite will be offset by this much. If acclDay = 0 then this value will be 0
byte endPercentCh5 = acclEndPercentCh5 - acclFactorCh5;
// Your standard PWM Dimming code using the variables above to determine start% and end%
ReefAngel.PWM.SetChannel( 0, PWMSlope(13,0,21,0,startPercent,endPercentCh0,90,20) );
ReefAngel.PWM.SetChannel( 1, PWMSlope(12,0,22,0,startPercent,endPercentCh1,90,20) );
ReefAngel.PWM.SetChannel( 2, PWMSlope(12,0,22,0,startPercent,endPercentCh2,90,20) );
ReefAngel.PWM.SetChannel( 3, PWMSlope(12,0,22,0,startPercent,endPercentCh3,90,20) );
ReefAngel.PWM.SetChannel( 4, PWMSlope(12,0,22,0,startPercent,endPercentCh4,90,20) );
ReefAngel.PWM.SetChannel( 5, PWMSlope(12,0,22,0,startPercent,endPercentCh5,90,20) );
// At the end of the day, we need to decrement the acclimation counter.
static boolean acclCounterReady=false; // We need a boolean so we only do this once per day
if (now()%SECS_PER_DAY!=0) acclCounterReady=true; // If it's not midnight we'll get the boolean ready
if (now()%SECS_PER_DAY==0 && acclCounterReady && acclDay>0) { // It's midnight, our bool is true and acclDay is more than 0
acclDay--; // Reduce the counter
acclCounterReady=false; // Reset the boolean flag
InternalMemory.write(Mem_B_AcclDay,acclDay); // Update memory
tanked_kiwi
Just wondering if it has been confirmed that this will work with the dimming expansion?
89delta
I just got my servo shield with the pca9685. Once I find free time I will test it.
tanked_kiwi
Sweet, looking forward to your results.